mick H | 23/06/2017 08:30:13 |
795 forum posts 34 photos | The small transformer (240v-12v) which powers my pond pump is reaching quite high temperatures. At an ambient temperature of 19 deg C yesterday morning the temperature of the transformer was 48degC as measured with an infra red thermometer. In the heat of a couple of days ago it was barely touchable suggesting probably about 60 deg C. I know that transformers get warm but this seems to be a bit excessive. Advice will be appreciated. Mick |
Muzzer | 23/06/2017 08:44:34 |
![]() 2904 forum posts 448 photos | Don't overthink it. The insulation system inside that transformer will be rated at something like 130C, 155C or even 180C. They are tested extensively and will almost certainly incorporate a thermal fuse if indeed there is an actual overtemperature situation. If you look carefully at the documentation, you may find details of the temperature rating - or at least where you could find out about it. For interest. To lower the temperature, if you felt that was desirable or commercially justifiable, you'd need to make everything bigger (more copper and larger surface area). You'd then struggle to sell it at a sensible margin against the smaller competition. We like to chortle about "elf and safety" and "red tape" but in a more grown up world, the regulations are designed to ensure that products are safe to use, including fire hazard, electric shock hazard and touch temperature. Murray |
Gordon Tarling | 23/06/2017 09:22:17 |
185 forum posts 4 photos | It is also entirely possible that your pump is drawing more current than it used to. This could be for many reasons, including moisture ingress. Protection for a stalled motor should be built in, though this won't necessarily work for a motor that is starting to tighten up for some reason. |
Muzzer | 23/06/2017 09:31:41 |
![]() 2904 forum posts 448 photos | Protection of the transformer is to ensure there isn't a fire or touch hazard and also to ensure that the electrical insulators are not compromised by the temperature, so it will "necessarily work". This safety stuff is not some hobby activity but actually the result of decades or more of learnings from death, injury and industrial accidents. Murray |
JasonB | 23/06/2017 09:39:42 |
![]() 25215 forum posts 3105 photos 1 articles | Any restrictions in the pipework like a build up of blanket weed on the pump strainer, dirty filter, you also get a lot of insect growth inside the pipes and even around the impellor this time of year. All will make the pump work harder and draw more current |
mick H | 23/06/2017 11:21:29 |
795 forum posts 34 photos | I can give a little more background. The pump system is less than a year old. The first transformer failed after about 6 months and this too seemed to reach excessive temperature. It was replaced free of charge but the replacement is still reaching the temperatures outlined above. The transformer is an IP68 . The pump is 12V 10watts and the UV lamp 5 watts. I have just Googled IP68 and it appears to have a working temperature of 0-25 deg C Mick |
Muzzer | 23/06/2017 11:28:08 |
![]() 2904 forum posts 448 photos | IP68 (ingress protection) is a test to check for ingress of dust and water. It has nothing to do with temperature. I wonder how you have determined that it has reached "excessive temperature"? On what basis do you make this judgement? |
mick H | 23/06/2017 12:02:37 |
795 forum posts 34 photos | Muzzer.......I got the specification IP68 from the user manual technical specifications....obviously not much use. My feelings about the excessive temperature (48 degC) are I suppose quite subjective but this is only a small transformer, say 50 x 50 x75 mm and the pump/uv demand is only 15 watts. I would be perfectly happy to be assured that there is no problem but the warranty runs out next month. Mick |
John Rudd | 23/06/2017 12:13:46 |
1479 forum posts 1 photos | Mick, Did you purchase both pump and transformer as a package? If yes, then I'd take it up with the supplier on the basis that the first transformer had failed and the second replacement is getting hot. Suggest there may be a problem with the pump and ask how they will resolve this?
I.M. OUTAHERE | 23/06/2017 12:29:58 |
1468 forum posts 3 photos | You may be forcing the pump to push too much head or lift so it is under full load all the time , restricting the outlet pipewirk diameter will do the same . Disconnect the outlet on the pump then let it run and see if the temps on the transformer drop . The uv lamp may be shorted causing more current draw than usual ? If all else fails upgrade he power supply to somehing that can put out more power . Have a look at your transformer it should have a rating of at least 1.5 amps preferably 2 amps or more . V X A = W (12x1.25 =15 w ) you state your pump is 10w and the light 5 w = 15w but one really never knows exactly how much power a pump will pull under full load ( unless you tested it ) a factor of X1.5 of the expected maximum is what i use as a minimum. I'm sure there will be an electronics / electrical engineer who will come along shortly that will want to correct me for things like RMS or delve into power factors and electrical losses in cables etc etc etc . Ian
not done it yet | 23/06/2017 12:49:05 |
7517 forum posts 20 photos | I would be checking output voltage and current to find the wattage of the load as a first step. I might then be looking at input power v. output power to check for efficiency, if not overloaded. It cannot be good if the case temperature is near 50C (in the shade) as the internal wiring temp may be considerably higher.
A decent one should only be losing about 3-4W as heat. Do check your IR thermometer as some are notoriously inaccurate, but the power supply should not get to untouchable temperatures from internal heat generation, that is for certain!
I would not think that an impellor pump (non postive displacement) would be affected by blockage in pipework, only if the impellor is rubbing. Is it direct drive or magnetically coupled? If the latter, is it driving continuously or is the motor decoupling continually? |
mick H | 23/06/2017 13:21:05 |
795 forum posts 34 photos | Quite a few things to investigate there. Firstly I think I shall do an easy bit and de-restrict the pump out flow .....less pretty but more flow. Back soon. Mick |
I.M. OUTAHERE | 23/06/2017 14:15:02 |
1468 forum posts 3 photos | Posted by not done it yet on 23/06/2017 12:49:05:
I would be checking output voltage and current to find the wattage of the load as a first step. I might then be looking at input power v. output power to check for efficiency, if not overloaded. It cannot be good if the case temperature is near 50C (in the shade) as the internal wiring temp may be considerably higher. * Efficiency is irrelevant as the output power vs pump requirement is all that matters. A decent one should only be losing about 3-4W as heat. Do check your IR thermometer as some are notoriously inaccurate, but the power supply should not get to untouchable temperatures from internal heat generation, that is for certain! * Agreed. I would not think that an impellor pump (non postive displacement) would be affected by blockage in pipework, only if the impellor is rubbing. Is it direct drive or magnetically coupled? If the latter, is it driving continuously or is the motor decoupling continually? The load on an impellor pump increases until cavitation occurs , if power is so low that cavitation cannot occur the vortex inside the pump can collapse causing flooding of the impeller and it will stall or load up or become a propellor instead of an impellor and this gives the same sort of current draw a pump would have on start up but it is continuos . Ian Edited By XD 351 on 23/06/2017 14:31:28 |
mick H | 23/06/2017 17:01:36 |
795 forum posts 34 photos | I have now de-restricted the flow from the pump and after a few hours the temperature of the transformer remains much the same, if not a little higher at 49degC. Ambient temperature 22degC. The unit has a maximum pumping head of 1.25 metres but is only about 30cm below the surface. I will attempt to measure the current output (12v AC) from the transformer tomorrow. Would I be correct in saying that I can do this by connecting a multimeter in series with one of the two output leads? The transformer output is listed as 1670mA. Mick |
Samsaranda | 23/06/2017 17:43:42 |
![]() 1688 forum posts 16 photos | I have "messed about" with ponds of all sizes for at least forty years and my past experiences tell me that Mick's problem with the transformer will be the load experienced by the pump. At this time of year all ponds will be loaded with small pieces of vegetable matter free floating in the water, when this vegetable matter passes through the pump it will gradually clog the impeller and therefore increase the consumption from the transformer and hence cause the temperature to rise. As well as the vegetable matter accumulating in the pump housing, at this time of year there will be minute water snails that have hatched and probably lodged in the impeller housing, the only way to guarantee reducing the loading on the pump is to regularly dismantle the impeller housing and clean it out, unfortunately at this time of year with a small pump which it appears Mick's is, this may need to be done daily to keep the pump free flowing, and the temperature at an acceptable level. There are pumps that will give better performance with accumulated solids but without knowing which pump we are discussing difficult to comment further. Dave
SillyOldDuffer | 23/06/2017 18:05:10 |
10668 forum posts 2415 photos | Posted by mick H on 23/06/2017 17:01:36:
... I will attempt to measure the current output (12v AC) from the transformer tomorrow. Would I be correct in saying that I can do this by connecting a multimeter in series with one of the two output leads? The transformer output is listed as 1670mA. Mick Yes, provided your multimeter has a suitable AC current scale. Quite a few are DC current only. If it does measure AC current it's likely to have a single 0-10A range only, but that's OK for what you're doing. Another way of checking if you can manage a bit of ad-hoc wiring, is to load the transformer with car indicator bulbs (a 10W and a 5W in parallel). That will replicate the transformer's 15W design load: if it overheats the transformer is faulty (shorted turns?) or inadequate. If the transformer stays cool, the problem is in the cable, or more likely, the pump &/or lamp. Dave Edited By SillyOldDuffer on 23/06/2017 18:05:36 |
Phil Whitley | 23/06/2017 19:24:59 |
![]() 1533 forum posts 147 photos | Can you post up some pics of transformer and pump? the chances are that this is chinese made and as you have already had one failure, the chances are you are well on the way to the next. The best way to slow the flow on a pond pump is to bleed off water from the pressure side back into the pond via a T peice and a valve, so you can slow the flow without choking the pump on the pressure side. 1.67A is not a lot and you could get a, say, 3 amp transformer, and see how that performed, it will make no difference to pump performance, but will run much cooler. Chinese mains dropper transformers do run stinking hot, and do pack up, as you have found out. My water feature has a mains submersible pump which has given no problems for several years now, and I don't think it was new when it went in. As I have mentioned before, there is zero product testing going on today, all "CE" marked good are supposed to conform with standards laid down by the EU, but it is up to the manufacturer to do their own testing, and to provide "proof of compliance" paperwork. It is very common for, shall we say, foreign made equipment to fail to reach its rated output and far exceed its claimed current demand by a sometimes very large margin!! Muzzers faith in the system is charming, but a little misplaced |
David Jupp | 23/06/2017 20:05:18 |
978 forum posts 26 photos | Posted by Phil Whitley on 23/06/2017 19:24:59:
The best way to slow the flow on a pond pump is to bleed off water from the pressure side back into the pond via a T peice and a valve, so you can slow the flow without choking the pump on the pressure side. That is actually likely to increase the flow through the pump (though reduce it through the visible water feature) and therefore may even increase the absorbed power. Restricting the outlet of a centrifugal pump will reduce the power consumption. Large centrifugal pumps are commonly started against an almost closed delivery valve to limit current surge (less so now that VFDs are commonplace). |
David George 1 | 23/06/2017 21:21:19 |
![]() 2110 forum posts 565 photos | Hi Mick I have a small Hoselock pond pump on a small water feature and the power supply has always run hot. When it was new I rang support and was told they do run hot but if it fails or causes any problem call back and they would replace it. That was four or five years ago. Its a 240 to 24v 1 amp model 62531-000. its very hot to the touch and always has been I think it helps to keep my tools rust free in winter. David |
Tim Stevens | 23/06/2017 21:29:03 |
![]() 1779 forum posts 1 photos | Remember, if you are using filament lamps as a load to check your system, that the bulb will only have the stated characteristics (eg 12v 6W, and therefore a working resistance of 24 ohms*) when it is getting the full 12 volts. Put it in series with something else and the voltage at the bulb will be lower, the filament will not get so hot, and its resistance will drop. A cold filament will draw several times the current of a properly hot one. This would be clear to us all if only cars still had ammeters. One factor which has not been mentioned is the ventilation of the transformer. A small amount of heat that can't get out will produce a large rise in temperature, after a time. Cheers, Tim *PS if memory serves ... Edited By Tim Stevens on 23/06/2017 21:32:06 |