Hacksaw | 24/07/2016 00:25:49 |
474 forum posts 202 photos | I had a 180 amp oil cooled welder sat in my workshop , fitted with a blue round pin plug (32a?) ,only the underground armoured cable feeding my workshop ring , is a piddly 2.5mm ..from a fusebox 50ft away . This is feeding a consumer unit in my workshop to which i fitted a ring and light circuit....The largest load is a 2hp motor on a lathe and a SIP 140amp buzz box welder. I was a little reluctant to use the oxford welder ,I thought it might be too much for the wiring although i did try it out at low power with a fly lead plugged in to a 3 pin metalclad socket .. no bang or fire !! A friend now has the welder .. and wants to use it in his outbuilding that has a consumer unit , that is fed with a 16mm underground cable 200 meters from the house supply .. The cable was run for lighting , and a couple of sockets for horse clippers / kettle .. I suggested having a dedicated blue socket fitted a so it can be plugged in . Will it be safe ? Volt drop issues ? Was i wise not to use it in my workshop on the 2.5mm? At idle ,does a transformer welder use the same amount of juice as when its pushing a 4mm rod ? Edited By Hacksaw on 24/07/2016 00:27:42 Edited By Hacksaw on 24/07/2016 00:35:40 |
not done it yet | 24/07/2016 06:33:52 |
7517 forum posts 20 photos | At idle, the current used will be only transformer losses -although these welders were not designed for maximum efficiency at idle! Think here of the different amounts of heat produced when welding! If the welder had to dissipate the arcing current when idle it would soon melt!
There will be tables on the net giving maximum power and maximum distances for the cable run. I assume you really mean 16mm^2 conductors. That is a large cable, easily able to transmit a few kW over that distance. The tails on your meter are likely that size - good for 100A in that use.
Look at the rating plate on the welder. I doubt it will be more than 6kW and likely only 4 1/2. And that would be flat out. Voltage drop for the welder would only mean a slightly reduced welding current/voltage requiring a higher setting on the machine. Look at the consumer unit rating - that will have a supply rating and will likely include a 45A cooker breaker.
Common sense should prevail with only the welder in use as a high current userat the time, of course.
|
Bob Brown 1 | 24/07/2016 08:44:31 |
![]() 1022 forum posts 127 photos | Cable size calculator **LINK** |
Neil Wyatt | 24/07/2016 09:11:48 |
![]() 19226 forum posts 749 photos 86 articles | Sorry, much as I understand the rationale, if anyone with slightly dodgy wiring tries to follow that tip they could end up with a house fire, so I have had to delete it. FWIW its the switch on surge that is the biggest problem. I use an extension lead for my arc welder or it pops the breaker half the time. The MIG is better behaved. Neil |
Bob Brown 1 | 24/07/2016 09:28:45 |
![]() 1022 forum posts 127 photos | Cable sizes are quite critical to get right and we (UK) are not allowed or supposed to do alterations to home wiring outside small jobs like change a socket outlet unless you are qualified to do so. The garage/workshop is on a 16mm2 supply, sub 10m cable run, to consumer unit which may seem a bit of over kill but did not want to be find the cable was too small at a later date. I've seen some really dodgy supplies to workshops and I have been guilty in the past, twin and earth is not really the cable to use outside, bigger is better.
|
Mike Lightfoot | 24/07/2016 10:58:06 |
76 forum posts 24 photos | Hi, not withstanding the common sense approach ref wiring sizes, I have an Oxford oil cooled and in my old shop it tripped the breaker every time if I forgot to turn the welding current down first it's called inrush current, a transformer can be considered similar to a big capacitor as in it needs ' filling' with lots of little wigglies as you turn it on, once on I never had any trouble welding. |
Mark C | 24/07/2016 12:13:07 |
707 forum posts 1 photos | Bob, although this will seem a tad picky, you do not need to be qualified as the common misconception is peddaled. You do need to be competent though (and commonly you get competent by achieving a standard of training)and that definition reads allong the lines of understanding when to take advice/consult the regulations. It is a very wooly description. It may be worded that wY to make it easier to prosecute rather than have to proove reckless intent? Surprissingly, this technically applies to plumbing and gas but I would caution against working on gas...... Mark |
Nick_G | 24/07/2016 12:30:12 |
![]() 1808 forum posts 744 photos | Posted by Neil Wyatt on 24/07/2016 09:11:48:
FWIW its the switch on surge that is the biggest problem. I use an extension lead for my arc welder or it pops the breaker half the time. Neil . Look up the differences between B, C and D type breakers. - The correct selection is designed to overcome this problem of initial inrush. But first the supply to the workshop has to be adequate. No easy fix for that one other than to put ones hand into thy pocket and dig deep for correct sized copper. Nick
|
Bob Brown 1 | 24/07/2016 13:29:04 |
![]() 1022 forum posts 127 photos | Mark C just so its clear some work on the electrics fall under part P of building regulations see **LINK**
|
Mark C | 24/07/2016 13:54:06 |
707 forum posts 1 photos | Yes i know. However, pat p is often misunderstood as requiring a 'qualifed electrician'. You only have to be competent and the two things are not the same. Further to this, any testing costs for building control must be born by them and not passed on to the house holder. If you want to be bothered reading up on it you need to research 'competent persons scheme' Mark |
Mark C | 24/07/2016 13:56:57 |
707 forum posts 1 photos | An interesting point to note is that the electricians are self certification and building control will often say you must have work done or checked by an electrician. Clearly you cant self certify somone else's work..... |
Neil Wyatt | 24/07/2016 15:46:36 |
![]() 19226 forum posts 749 photos 86 articles | Posted by Nick_G on 24/07/2016 12:30:12:
Posted by Neil Wyatt on 24/07/2016 09:11:48:
FWIW its the switch on surge that is the biggest problem. I use an extension lead for my arc welder or it pops the breaker half the time. Neil . Look up the differences between B, C and D type breakers. - The correct selection is designed to overcome this problem of initial inrush. But first the supply to the workshop has to be adequate. No easy fix for that one other than to put ones hand into thy pocket and dig deep for correct sized copper. Nick The wire won't reach to my workshop I use one or other of two RCD domestic sockets at front and back of house, each is on a normal ring main (small welder suitable for 13A plug - it's never blown a 13A fuse) and I don't want to reduce the day to day protection. I have got a higher capacity 32A spur in the workshop (which in turn is on VERY hefty copper for up to 40A from the main box) (these amperages are approximate - I can't be bothered to go and check, but it was all done to the regs as of 2002) Neil Neil |
Ed Duffner | 24/07/2016 16:21:17 |
863 forum posts 104 photos | Posted by Hacksaw on 24/07/2016 00:25:49:
... A friend now has the welder .. and wants to use it in his outbuilding that has a consumer unit , that is fed with a 16mm underground cable 200 meters from the house supply .. The cable was run for lighting , and a couple of sockets for horse clippers / kettle .. I suggested having a dedicated blue socket fitted a so it can be plugged in . Will it be safe ? Volt drop issues ? Was i wise not to use it in my workshop on the 2.5mm? ...
Hi Hacksaw, My advice would be for your friend to get an Electrician with current knowledge (no punn intended) to assess the installation. There are too many unknowns for anyone here, and I mean no disrespect to anyone, to provide solid answers to your specific questions (and I include myself, electrician working to 15th edition a few years ago). Ideally any electric cable installed should have a fuse or circuit breaker rated to protect it. ie the 16mm SWA cable should have been installed with an appropriate protective device allowing for potential volts drop over the 200m that you mention. The potential volt drop is usually factored in when a circuit is designed and the cabling and equipment is chosen for the installation. If overloaded, the over current device would break the circuit before damage to the cable occurred. I'd doubt whether the 16mm cable would have any issues, a problem that seems to be posted in a number of forums relates more to not having the 32amp blue plugs installed and standard 13amp 3 pin plugs blowing fuses. It would be interesting to know how much current a welder e.g. 180amp would actually pull from the supply. Anyone know ? Ed.
|
Sam Longley 1 | 24/07/2016 16:27:02 |
965 forum posts 34 photos | If like me you had built your own house ( twice now) then you would have built the garages first so you could store tools & important gear. Then you would have had the electric meter & supply placed in the garage so you could use electricity for the works & run the house supply from there when ready. That way the workshop & garages do not have the problems others have . Called forward planning !! |
Muzzer | 24/07/2016 16:51:41 |
![]() 2904 forum posts 448 photos | It's a common misconception that transformers have an inrush surge current at first turn-on. In fact, the primary of the transformer is simply an inductive load, so the peak current resulting from energising it part way through the cycle can never exceed the normal peak magnetising current. It's just basic electrical theory as taught at school. You might argue that connecting the primary when the secondary is loaded could explain this problem but that's not normally the cause and even then it's not an "inrush surge" issue so much as a "reflected load". And that shouldn't exceed the normal rated current anyway. What DOES cause transient currents at turn-on is remanence ie residual magnetism in the cores due to the random timing of last disconnection (when the switch was opened) and random timing when the primary is next connected (switch turned on again). If the correct conditions occur, the core magnetisation is additive (volt seconds on the winding), the transformer cores can saturate and you get a very high transient current - essentially a short circuit on the primary winding. The typical saturation margin on the magnetisation current is surprisingly low. Fitting a high current type C or D MCB can help to some degree but isn't always the answer, given what is actually happening. The ideal solution is a soft start circuit - usually a phase controlled triac or a timed resistor / relay. The latter is simpler but not straightforward, as you need a low enough resistance to drive the magnetising current close to where it should be but high enough to prevent saturation. You can also control (delay) the turn-on and turn-off events so that the flux is always controlled. Murray |
Marcus Bowman | 24/07/2016 17:12:15 |
196 forum posts 2 photos | In practical terms: I have owned an Oxford welder for more than 40 years, and I can tell you that it will require a heavier-than-domestic wiring feed, and appropriate trips (see Nick_G's post). In a previous workshop, I began with a 16 amp industrial-style socket wired into its own fuse at the fusebox, but had endless trouble with the earth arrangements, so abandoned that temporarily many years ago. Using the welder via a 13A domestic plug into a good quality 13 amp socket for short welds the socket face plate soon had burn marks on it, and it got very hot if welding over a metre or so at a time. You can't really run more than about 110 amps with this setup. The 2.5mm2 wiring leading to the socket also got hot, which is a potentially serious problem. So I would caution you not to begin by using a domestic wiring arrangement with this welder, but to install a proper high capacity fuse, thicker wiring and an industrial plug. Domestic wiring is a definite fire hazard. I also have a large capacity fire extinguisher in the workshop, but that would not be much good if the wiring in the walls overheats. One other problem is that when the welder is switched on there is a significant surge which can trip a domestically-rated fuse. The more often the fuse trips, the more prone it is to tripping. It's a cycle of despair relieved only by taking note of the differences between types and ratings of breakers (see Nick_G's post). I'm hoping to add a different type of welder shortly, but it is clear that any welder capable of welding anything other than thin sheet (car body thickness) will draw more current than can safely be delivered via 13 amp domestic fuses and cables. The specs on many models make this clear, and I note that at least one manufacturer will not supply a 13A plug for their more capable welders. Having said all that, the Oxford is a robust welder capable of heavy duty. I have not had a moment's bother with mine, despite miles of welding. Marcus
|
Hacksaw | 24/07/2016 22:50:24 |
474 forum posts 202 photos | Some helpful answers here ! Thanks. My friend is wealthy.. I'll advise him to get his sparks to fit a blue plug and dedicated cable into the consumer unit . He wont be welding much anyway .. Marcus, I agree ,those old Oxfords weld lovely , and all day long without cutting out ! |
Speedy Builder5 | 25/07/2016 07:16:40 |
2878 forum posts 248 photos | Probably cheaper to sell the Oxford (unless he was going to use the single point carbon brazing setup) and buy a 120 amp MIG. So much easier to use, runs off 13 amp plug etc etc. |
frank brown | 25/07/2016 20:59:33 |
436 forum posts 5 photos |
Others are available Frank Edited By Neil Wyatt on 25/07/2016 21:46:18 |
norm norton | 26/07/2016 22:00:19 |
202 forum posts 10 photos | Posted by Marcus Bowman on 24/07/2016 17:12:15:
, but it is clear that any welder capable of welding anything other than thin sheet (car body thickness) will draw more current than can safely be delivered via 13 amp domestic fuses and cables. I respect your care and attention Marcus, but the qualification on thickness of metal is not correct. I have a 150amp commonly supplied, basic MIG welder (Clarke) that runs through a 13amp domestic plug and fuse, and I can fully weld 6mm steel that is butted, vee groove. I have even joined items onto 10mm plate by working from both sides, although probably not a fully penetrating weld. Whether it really delivers 150amps is another matter, but it's called a '150 turbo' !! Norm Edited By norm norton on 26/07/2016 22:04:15 |
Please login to post a reply.
Want the latest issue of Model Engineer or Model Engineers' Workshop? Use our magazine locator links to find your nearest stockist!
Sign up to our newsletter and get a free digital issue.
You can unsubscribe at anytime. View our privacy policy at www.mortons.co.uk/privacy
You can contact us by phone, mail or email about the magazines including becoming a contributor, submitting reader's letters or making queries about articles. You can also get in touch about this website, advertising or other general issues.
Click THIS LINK for full contact details.
For subscription issues please see THIS LINK.