charadam16/06/2016 17:56:31
185 forum posts
6 photos

I was happily making chips on my Boxford VM30 yesterday, took a short break, came back and the mill would no longer run.

The machine has worked happily with the inverter (Nordac Compact) for about 12 years so this has come as an unwelcome surprise.

The inverter is electrically live and the parameters are accessible from the simple buttons on the panel. The parameters are unchanged from when it was running OK.

Now when I switch on, the inverter panel displays 036.8 (no "F" so not a fault code?) and the 8 flickers on and off.

I am electronically a dimwit.

Can anyone offer advice?

John Rudd16/06/2016 18:18:19
1479 forum posts
1 photos

Just in case you dont have the manual...

https://www.nord.com/cms/media/documents/bw/BU330X_GB_1096.pdf

Having had a quick flick through it, I cant see anything that relates to the characters being displayed...

charadam16/06/2016 18:26:12
185 forum posts
6 photos

Thank you John.

My inverter seems to be an earlier variant. There are only 3 buttons on the panel,  P, + and -.

I have the manual and can work through the parameters but that's about my limit.

The motor is 3 phase and a large capacitor is included in the wiring.

Edited By charadam on 16/06/2016 18:26:44

Gray6216/06/2016 18:30:40
1058 forum posts
16 photos

Are you using the controls on the inverter for run stop or a pendant. May be a broken connection between pendant and inverter if the latter. If you are using a pendant try changing the parameter P007 to change to panel control and see if it then fires up (you may also have to alter P121 - 124)

Edited By Graeme W on 16/06/2016 18:31:43

charadam16/06/2016 19:05:01
185 forum posts
6 photos

Graeme, the inverter gets switched on at the 13A wall socket, then the motor is switched on using the original Boxford switch on the machine panel.

David Jupp16/06/2016 19:29:25
978 forum posts
26 photos

Posted by charadam on 16/06/2016 18:26:12:

The motor is 3 phase and a large capacitor is included in the wiring

Not clear why there would be a capacitor in wiring for a 3-phase motor, but if it has worked for 12 years....

If switch on machine panel is after inverter, that is asking for problems - never break connection between inverter and motor, risks blowing output stage of inverter.

charadam16/06/2016 19:46:19
185 forum posts
6 photos

Oops! The capacitor is in circuit with the coolant pump.

Sorry for the red herring.

Clive Foster16/06/2016 19:51:42
3630 forum posts
128 photos
Posted by charadam on 16/06/2016 19:05:01:

Graeme, the inverter gets switched on at the 13A wall socket, then the motor is switched on using the original Boxford switch on the machine panel.

Do you let the inverter run up to 50Hz before switching the motor on?

If so odds are you are overstressing the electronics to some degree due to the large surge current when the motor starts. Hopefully its just one of the input capacitors or diodes gone which should be fairly simple for an electronics guru to sort on a relatively old design like that. If its an output device fixing may be harder and there may be deeper damage. Repair may not be economic.

Although this sort of "plug and play" operation is possible using a correctly (over)rated inverter normal use with an inverter fairly closely matched to the motor power assumes that the inverter does both switching and speed control duties. The motor run up to speed from zero and run down to stop is controlled by the inverter circuitry to avoid potentially damaging surge currents. Plug and play using the machines own switchgear with the inverter acting as a 1 box substitute for mains three phase needs an inverter whose rated capacity is at least twice the power of the largest individual motor to be run with a high overload capability probably at least 200% overload for 60 seconds. Still hard on the electronics although smoothing incutors on the output helps. Looking at the manual John linked to your inverter has a decent overload capability of 150% for 60 seconds so its a pretty tough device but I'd expect the hard starts and current surges to wear it down eventually.

Clive.

Ian P16/06/2016 20:10:45
avatar
2747 forum posts
123 photos
Posted by charadam on 16/06/2016 19:05:01:

Graeme, the inverter gets switched on at the 13A wall socket, then the motor is switched on using the original Boxford switch on the machine panel.

It not clear from the above statement whether the Boxford switch is actually switching the motor wiring or whether it has been wired to the inverter controls input (for remote pendants etc).

Without knowing how the inverter is wired I think we can only make guesses as to the cause of the fault.

Maybe someone with some relevant knowledge is local to you and could help, I certainly would but have no idea what country or where you are.

Ian P

charadam16/06/2016 20:11:40
185 forum posts
6 photos

Graeme,

Thank you - I think I understand.

Are you saying I should have been setting the motor switch "on" before firing up the inverter?

John Rudd16/06/2016 20:44:17
1479 forum posts
1 photos
Posted by charadam on 16/06/2016 20:11:40:

Graeme,

Are you saying I should have been setting the motor switch "on" before firing up the inverter?

Absolutely.....

Manufacturers usually provide a connection drawing on how to hook up an inverter...and all the time I've been repairing/selling them, I've never come across one where it shows an indirect connection...

All switching is done on the input side of the inverter....

charadam17/06/2016 14:36:19
185 forum posts
6 photos

The consensus is that I have fried the inverter over time by incorrect starting technique.

A new item has been ordered.

May I thank all who offered help and advice, with special thanks to John Rudd who advised off-forum.

Onward and upward - but select the motor "on" first!

Charles

Neil Wyatt17/06/2016 14:53:39
avatar
19226 forum posts
749 photos
86 articles

It seems unlikely to me that what you have done for 12 years should suddenly cause the inverter to fry, although it certainly is possible. Switching the machine OFF  on the downstream side when the inverter is running is what the handbook for my inverter warns against. Of course you may be doing this...

Perhaps more likely is that the big electrolytic capacitors have gradually reached the end of their life and need to be replaced - this may be what your message is telling you. My inverter keeps track of usage hours and can be set to warn when the capacitors need replacing.

Neil

 

Edited By Neil Wyatt on 17/06/2016 14:55:52

charadam17/06/2016 17:59:28
185 forum posts
6 photos

Neil,

Aye, there's the rub!

Of course I switched off wrongly as well.

I am, at least, consistent.

Charles

John Stevenson17/06/2016 20:40:28
avatar
5068 forum posts
3 photos

Just smile and accept the Kama.

If you have had it 12 years chances are it's 15 to 18 year old inverter technology, possibly longer ? which puts it at about coming out of the Jurassic period, possible a few decades in front of a Myford.

Ian P17/06/2016 22:30:10
avatar
2747 forum posts
123 photos
Posted by charadam on 17/06/2016 14:36:19:

The consensus is that I have fried the inverter over time by incorrect starting technique.

A new item has been ordered.

May I thank all who offered help and advice, with special thanks to John Rudd who advised off-forum.

Onward and upward - but select the motor "on" first!

Charles

If I understand the wiring scheme you have been using with this mill and inverter for years (switching motor on and off instantly) then you have been missing out on many of the basic advantages of a VFD system. Like the ability to adjust the acceleration and deceleration rates of the drive and vary the speed (right down to zero) plus lots of other features etc.

Presumably your replacement VFD will be a more modern model which will come with a manual so fitting it should be straighforward.

Ian P

charadam17/06/2016 23:27:41
185 forum posts
6 photos

Ian,

The mill used its original controls so I had mechanical control of speed and never considered using the electronics in their place.

The inverter was inconveniently remote mounted so using functions was not ergonomic (translate: big lad, small workshop, too many belly bruises from corner of table).

The new inverter will be mounted on the belt guard so will be convenient to use.

But I will probably continue to use the mechanical controls for speed.

Charles

 

Edited By charadam on 18/06/2016 00:00:33

Ian P18/06/2016 10:00:53
avatar
2747 forum posts
123 photos

When you alter the wiring so that the motor on/off is done on the signal input side of the VFD (you can wire the existing switch to do that) then the very nature of the VFD will give the acceleration ramps.

To get the same 'feel' as your existing setup you could reduce the ramps to zero but there is no much point, far better to have say, a half second ramp, apart from putting less shock loads on the drive line it makes the machine feel smoother.

Certainly if have got used to the machine over such a long period I would not want you to have to re-learn anything so stick with the mechanical speed control. I am not conversant with your mill but one thing I find useful on mine is the VFDs ability to rotate the spindle at dial indicator sweep speeds (20-30 RPM) as its the speed I use when using my edge finder. At such low speeds the torque is laughable but as the motor is doing no work as such it would never even get warm.

Ian P


capnahab19/06/2016 17:14:39
194 forum posts
17 photos

I hope this isn't going to confuse everything (comparing apples, pears, and oranges). I have two transwave inverters (one static and one rotary). The lathe and milling machne are plugged into them. What's the recommended sequence for starting and stopping them?

frank brown19/06/2016 17:54:14
436 forum posts
5 photos

If your static converter also steps up to 440 3 phase, then you switch the motor of by turning the converter off. Else a, the start caps won't be switched in and, b the back EMF from the transformer will blow up your capacitors (guess how I know?)

Frank

All Topics | Latest Posts

Please login to post a reply.

Magazine Locator

Want the latest issue of Model Engineer or Model Engineers' Workshop? Use our magazine locator links to find your nearest stockist!

Find Model Engineer & Model Engineers' Workshop

Sign up to our Newsletter

Sign up to our newsletter and get a free digital issue.

You can unsubscribe at anytime. View our privacy policy at www.mortons.co.uk/privacy

Latest Forum Posts
Support Our Partners
cowells
Sarik
MERIDIENNE EXHIBITIONS LTD
Subscription Offer

Latest "For Sale" Ads
Latest "Wanted" Ads
Get In Touch!

Do you want to contact the Model Engineer and Model Engineers' Workshop team?

You can contact us by phone, mail or email about the magazines including becoming a contributor, submitting reader's letters or making queries about articles. You can also get in touch about this website, advertising or other general issues.

Click THIS LINK for full contact details.

For subscription issues please see THIS LINK.

Digital Back Issues

Social Media online

'Like' us on Facebook
Follow us on Facebook

Follow us on Twitter
 Twitter Logo

Pin us on Pinterest

 

Donate

donate