Using a vfd for two machines

All Topics | Latest Posts

Search for:  in Thread Title in  
terry callaghan20/02/2021 15:18:26
237 forum posts
10 photos

Hi chaps. For some reason single to three phase inverters or vfd. Are thin on the ground. I have a mitsubishi vfd in my workshop that’s rated to 1.5kw which is running the lathe. However I had to replace the motor on my milling machine to three phase and this motor is also rated at 1.5kw. So question is there a way that I can run both machines ( not at the same time ) from the single vfd. I don’t however wish to connect and disconnect cables each time. Would some sort of electrical switch work. What are your views.

Harry Wilkes20/02/2021 15:28:54
avatar
1613 forum posts
72 photos

A pair of electrically/mechanically interlocked contactors comes to mind other ways could be a rotorary switch, vfd feeds a 4pin socket into which you could plug machines into as and when. If it was me I would go with the contactors and interlock these with the vfd to make sure the load could not be disconnected whilst running.

H

Tony Ray20/02/2021 15:35:44
238 forum posts
47 photos

Hi Terry,

It could be done but I would challenge your statement regarding the availability of 230V input VFD’s unless you are talking about secondhand units. I buy mine from inverterdrive.com no connection just a satisfied customer they are showing over 130 models currently.

terry callaghan20/02/2021 15:49:04
237 forum posts
10 photos

Hi Tony, I would like to use a mitsubishi brand as I have had one for years and never let me down. Apart from the expensive ones they are all on back order. I just don’t want to go through the nightmare of the Chinese ones again with no back up.

Emgee20/02/2021 15:59:52
2610 forum posts
312 photos

A suitably rated 3 pole + aux contacts changeover switch with centre off would do what you want but you must always isolate the power to the VFD before changing the switch to the 2nd machine.
I would suggest you wire the units direct without using  plugs and sockets.
The aux contacts in the switch would have to suit the STOP circuit requirements (NO or NC) of the VFD so with the switch in an OFF position the stop is activated.

It is not recommended to fit any switching device between the VFD and motor because of possible damage to the VFD if switched off with a running motor but with careful use as above no damage should occur.

With regard settings in the unit you will have to accept common settings for both machines unless of course you re-program certain features at every change-over.

Emgee

Edited By Emgee on 20/02/2021 16:02:29

terry callaghan20/02/2021 16:10:37
237 forum posts
10 photos

Thanks for the information chaps.

Clive Foster20/02/2021 16:31:35
3630 forum posts
128 photos

If you share a VFD with two motors you won't be able to run a self tuning vector drive VFD. Which is a pity because such drives work much better than old style Voltage/Frequency types. Torque holds up much better as speed falls.

There is an intermediate type of vector drive where you simply program in the size, current(?) and rpm of the motor which could be managed if your two motors are the same. Not as good as self tuning but better than simple V/F.

Clive

SillyOldDuffer20/02/2021 16:44:47
10668 forum posts
2415 photos

I wouldn't recommend it but something like this might do.

I notice switches sold for 3-phase changeover all come with 'Authorised Personnel Only' guard features like locked doors and padlocks. I suppose absently mindedly switching over a live 3-phase service could be far more exciting than the operator expected! In Terry's case likely to damage the VFD and maybe spiking the motors too, so don't get it wrong!.

I doubt one would be be bought by accident because they're so expensive, but the automatic 3-phase changeover switches are the wrong way round for this purpose. Designed for failover applications, they switch one load between two sources, whereas Terry wants to connect one source to either of two loads.

Saving a bob or two is usually a good thing, but maybe sharing a VFD intended to power a single motor is a risky economy? Some of the better VFD's learn and adapt to whatever motor is connected, and switching one of them to a different motor might cause it to think it had detected a fault. But the real danger is the obvious one - too easy for the operator to switch over before the circuit is completely dead, i.e with both motors stopped and the VFD turned off. The money spent on the changeover switch and wiring might be better invested in another VFD, and imposing a switch means the lathe and mill can't be left idling ready for jobs to be swapped between them. (I do this occasionally.)

I apologise to Terry for spending his money so enthusiastically for reasons that may not apply in his workshop! And how much dosh is available makes a difference too...

Dave

Steviegtr20/02/2021 16:55:22
avatar
2668 forum posts
352 photos

I don't think the change over switch is a bad idea at all. As long as you expect the ramp up / down times. Min freq. Max freq etc etc can be the same then all is well.

Surely you would not expect the average operator to switch over while the inverter was running on the other machine.

If you thought it could happen then simply use the aux contacts to break the stop circuit. So then it would be idiot proof. Not that there are any on this forum anyway.

If both motors are the same hp & the same poles say 2 or 4, then all should be well.

Steve.

Clive Foster20/02/2021 17:02:36
3630 forum posts
128 photos

There are dual interlocked contactor sets intended for forward-reverse motor control which will not switch from one setting to the other without going through the stopped position first.

The one I have floating around to (eventually) use on a garage door opener cost about £25. It has external links to do the pole switching needed between forward and reverse connections so there seems no reason why it could not be configured to control a pair of motors rather than forward-reverse on one.

Clive

Tony Ray20/02/2021 18:21:18
238 forum posts
47 photos

I would challenge the statement that 230V input vfds are hard to find unless we are talking about used units. I buy mine new from inverter drive.com No affiliation just a satisfied customer a quick search on their site just now showed 130 odd models in 1.5 kW.

Martin Cargill20/02/2021 18:45:53
203 forum posts

All very good but have you considered how you will control the machines? The existing switchgear cant be utilised easily as it will have to interface with the VFD and it won't be swappable between the two machines.

I have a VFD in my workshop that can power various machines. However to do this I have the motors disconnected from the original control gear and each one is fitted with a cable fitted with a 3 phase plug. I then have a control pod with start, stop, emergency stop, speed control and reversing switch that has to be taken to each machine (when it's in use) and this has its own cable.

Its quite messy with having two cables to the machine in use. In addition you have to work out a safe method for holding the control pod so that it's accessible when the machine is in use (and you have to remember that the existing controls don't work!!!! unless you have removed them)

You have to watch to make sure that nobody ever plugs in your 3 phase socket into normal 3 phase mains as your motor will be wired for 240 volts 3 phase and not 415 volts 3 phase, and of course there will be no switchgear feeding the motor.......

Martin

David Jupp20/02/2021 18:45:56
978 forum posts
26 photos

Potentially, with an extra pole on the changeover switch you can tell the VFD which set of motor parameters to use to match the selected motor. Many VFD's can store at least 2 sets of parameters...

hush20/02/2021 18:46:09
19 forum posts

My Boxford lathe is three phase, and is driven by a single phase to three phase box. My miller was also three phase, and was driven from the same box. Fed up with swapping the plugs over. I called the makers of the box to ask about fitting an extra socket on the front panel, this idea was OK'd provided the job was done by a qualified "sparks". This work was done and both machines were connected. It worked very well as I was the only person using the machines.

old mart20/02/2021 19:42:26
4655 forum posts
304 photos

It can be done, but as already advised, the VFD must be isolated from the mains power before switching from one to the other. VFD's do not like switches between the VFD and the motor and if the VFD is off when the switchover is made it will not be adversly affected. The cables between the VFD, the switching and the motors should be screened.

Robert Atkinson 220/02/2021 21:02:19
avatar
1891 forum posts
37 photos

One thing that has not been mentioned is Start Stop controls. You really need to to switch at least the start switch (button) with the motor. You don't want to push the start on the mill and have the lathe start turning!
The Stop and E-Stop circuits for both machines can be wired in series (parallel if normally open) to the VFD so pushing stop on either machine will stop whichever is selected.

EMGEE sugessted a switch with auxillary contacts for the Stop circuit but this educes safety and does not address the start issue.

Personally I'd use a pair of electrically interlocked contactors and a 3 position (Lathe OFF MILL) rotary switch. An indicator light on each machine would be an added safety feature to let you know which is live .

Robert G8RPI.

Zan20/02/2021 23:59:22
356 forum posts
25 photos

StrangeG double post without the edit! See below

Edited By Zan on 21/02/2021 00:04:32

Zan21/02/2021 00:03:40
356 forum posts
25 photos

V d f thin on the ground? There’s thousands for sale Google it. Not worth the risk of disconnecting whithout. Switching the mains off and destroying the vdf Get one for each machine. I have one on each of my 5 machines they all have different perimeters set to suit the individual requirements. They are cheap( ish) compared with the uncertainty of remembering to change the settings n plugeps. What happens when one machine is running very slowly and you want to run another at the same time?

Emgee21/02/2021 00:18:01
2610 forum posts
312 photos
Posted by Robert Atkinson 2 on 20/02/2021 21:02:19:

One thing that has not been mentioned is Start Stop controls. You really need to to switch at least the start switch (button) with the motor. You don't want to push the start on the mill and have the lathe start turning!
The Stop and E-Stop circuits for both machines can be wired in series (parallel if normally open) to the VFD so pushing stop on either machine will stop whichever is selected.

EMGEE sugessted a switch with auxillary contacts for the Stop circuit but this educes safety and does not address the start issue.

Personally I'd use a pair of electrically interlocked contactors and a 3 position (Lathe OFF MILL) rotary switch. An indicator light on each machine would be an added safety feature to let you know which is live .Robert G8RPI.

I did not mention any starting arrangement as that question wasn't asked, however it would be sensible to have a portable pendant with start/stop/speed pot that could be moved between machines and fitted into a cradle provided on each machine as required.

Auxillary contacts are early break and late make which would ensure if the VFD was running the Stop circuit would be activated before the switch contacts opened, I fail to see how that reduces safety, it is no more than operating the Stop button on the VFD or Pendant control.

Nothing is gained by the additional use of mechanically and electrically interlocked contactors, it just adds complexity and cost to job in hand. With 1 supply into a changeover switch you can only provide power to 1 of the connected motors at any time.

The position of the pendant and the labelling on the changeover switch should be sufficient for Terry to know which machine the VFD is connected to without an indicator light.

Emgee

not done it yet21/02/2021 08:12:03
7517 forum posts
20 photos

The aggravation/cost of fitting all these interlocks or the risk of messing up a perfectly good VFD just does not seem worth it.

I would suggest buying a cheap VFD for the second drive. By all means replace with a mitsu’ when attainable and either keep the cheapie as a spare - or sell it on at less of a loss than messing up an expensive VFD...

All Topics | Latest Posts

Please login to post a reply.

Magazine Locator

Want the latest issue of Model Engineer or Model Engineers' Workshop? Use our magazine locator links to find your nearest stockist!

Find Model Engineer & Model Engineers' Workshop

Sign up to our Newsletter

Sign up to our newsletter and get a free digital issue.

You can unsubscribe at anytime. View our privacy policy at www.mortons.co.uk/privacy

Latest Forum Posts
Support Our Partners
cowells
Sarik
MERIDIENNE EXHIBITIONS LTD
Subscription Offer

Latest "For Sale" Ads
Latest "Wanted" Ads
Get In Touch!

Do you want to contact the Model Engineer and Model Engineers' Workshop team?

You can contact us by phone, mail or email about the magazines including becoming a contributor, submitting reader's letters or making queries about articles. You can also get in touch about this website, advertising or other general issues.

Click THIS LINK for full contact details.

For subscription issues please see THIS LINK.

Digital Back Issues

Social Media online

'Like' us on Facebook
Follow us on Facebook

Follow us on Twitter
 Twitter Logo

Pin us on Pinterest

 

Donate

donate