Alan .204 | 15/11/2013 21:34:43 |
304 forum posts 14 photos | Can you run say a 1hp motor through a 1.5hp inverter or even a 2hp inverter does it damage either one of these motor or inverter, hope this makes sense.
Al. |
John Rudd | 15/11/2013 21:56:14 |
1479 forum posts 1 photos | Yes, shouldn't be a problem....In fact I'm running my Chester Eagle 30 mill with a 1.1kw (1.5hp) motor and using a 1.5kw vfd bought from Ebay
|
jonathan heppel | 15/11/2013 22:02:14 |
99 forum posts | No problem, though it's wise to programme the motor's characteristics jnto the inverter. Most important is the max current to prevent motor overload. The advice used to be that the inverter should be one size smaller than the motor, but I think that advice is now obsolete. Ps it probably depends on the make of inverter. They're not all the same, but probably not different enough to matter greatly. Get the best you can afford. Edited By jonathan heppel on 15/11/2013 22:13:25 |
Alan .204 | 15/11/2013 22:19:36 |
304 forum posts 14 photos | Seen a 1hp inverter for sale at a good price but I would have preferred to fit a 1.5 hp motor that's the problem, my have to go for the smaller 1hp motor after all.
Thanks Al. |
_Paul_ | 15/11/2013 22:28:23 |
![]() 543 forum posts 31 photos | I have one Teco 2HP Inverter which has for years been powering various different machines all with different size motors ranging from 1/3 hp to 2 hp with no problems at all. Swapping machines/motors is done by using a 3 phase socket and plug system. Paul
|
jonathan heppel | 15/11/2013 22:30:42 |
99 forum posts | Still no problem. The reason for the manufacturer's advice to use a motor one size bigger had to do with the spiky nature of the output. By all means use the 1.5 Kw motor. |
Alan .204 | 15/11/2013 22:34:14 |
304 forum posts 14 photos | Just checking Jonathon do you mean it's OK to run a 1.5hp motor with a 1hp inverter it's just you put 1.5KW motor.
Al. |
jonathan heppel | 15/11/2013 22:42:18 |
99 forum posts | Paul, what you're doing is fine as long as there isn't an overload any time. A DOL starter has thermal protection. Your small motors don't, and fuses aren't recommended for the drive's sake. You may well be fine for ever, but it is a potentially dangerous set up. |
jonathan heppel | 15/11/2013 22:48:41 |
99 forum posts | Alan, yes sure. As I said earlier, it used to be the manufacturer's recommendation, and is still good practice, particularly with budget drives and older non-vfd rated motors. |
_Paul_ | 15/11/2013 22:52:11 |
![]() 543 forum posts 31 photos | Posted by jonathan heppel on 15/11/2013 22:42:18:
Paul, what you're doing is fine as long as there isn't an overload any time. A DOL starter has thermal protection. Your small motors don't, and fuses aren't recommended for the drive's sake. You may well be fine for ever, but it is a potentially dangerous set up. Whats dangerous about it then? |
jonathan heppel | 15/11/2013 23:09:56 |
99 forum posts | Your 2hp vfd thinks the1/3 hp motor is 2hp. If for example the rotor locked, the vfd would try to produce the current for a 2 hp motor, and fry it. Overloads or fuses between them could prevent it, but then you run the risk of blowing up the vfd- they really don't like having the load disconnected while running. It's not hugely dangerous, but a drives pro wouldn't do it. |
_Paul_ | 15/11/2013 23:46:15 |
![]() 543 forum posts 31 photos | How strange... the recommendation to use such a setup came from Dave the chap that owns Drives Direct probably one of the biggest retailers of VFD's in the UK. |
ronan walsh | 16/11/2013 01:49:09 |
546 forum posts 32 photos | The newer vfd's or inverters , have the ability to "assess", for want of a better word, the motor its connected to the first time it is connected and powered up. I bought a Yaskawa vfd to run a 5hp colchester lathe and it did this for me. The electronics are getting really sopfisticated now and can do things only dreamt of a decade ago. I still agree with what jonathan says though, match the vfd to the motor, if for no other reason than to save money, the bigger the inverter the bigger the bill. Why pay for engineering you are not going to use ? |
Muzzer | 16/11/2013 02:28:31 |
![]() 2904 forum posts 448 photos | If you don't tell the inverter that it's actually got a smaller motor connected and it tries to generate full torque or boost torque, it's going to put some serious amps into the machine that it wasn't designed for. This is likely to saturate the machine and certainly won't result in the required performance. And the various operating and protection schemes for the motor and inverter won't be set up correctly. Modern inverters do some wonderful things as noted but they need to know some key information about the motor. This often requires little more than entering the motor plate ratings but it's worth taking the time to do so and isn't usually difficult. So you don't have to choose matching motor and inverter but you should "match" them by correctly setting the inverter up. Obviously there's no harm running a large motor with a small inverter (the max limits are hard coded) but you simply won't be able to develop the rated torque and power due to the current limitation. Merry |
I.M. OUTAHERE | 16/11/2013 08:31:23 |
1468 forum posts 3 photos | I would have thought that 1.5KW unit to be a minimum for a 1 hp motor and i'm currently setting up a 3/4hp motor to run from a 3.3kw inverter . Other than motor voltage and frequency I have not noticed anything in the programming for maximum current but I would have to double check this , I did have an issue when first connecting this unit for its first run though - wired it up , double checked everything then hit the start - nothing but noise ! I also had some fun setting up the emergency stop /fwd jog/rev jog as these use 3 of the 4 input terminals as one was labelled incorrectly but I eventually sorted this and marked it down in the manual..
Other than that i'm very pleased with the unit . Ian
|
John Haine | 16/11/2013 08:37:01 |
5563 forum posts 322 photos | Ian, I suspect that the pots you used are log types intended to be used as volume controls. A VFD should use a linear type. |
I.M. OUTAHERE | 16/11/2013 09:17:47 |
1468 forum posts 3 photos | Hi John , I thought of that but the pot is marked LIN and a check with a meter would suggest this is correct . The pot on the VFD is the same , it only works in the first half of its travel so I am starting to think it may be an internal issue or something to do with the reference voltage that is set up for the pot . I am thinking about trying a logarithmic pot at 10k as it may counteract the effects i'm getting from a linear pot at the same value ? The reference voltage is 10v but there is also an output for 5v so I may also try this tomorrow although I suspect I will not achieve full rpm with this but ... Ian |
Ian P | 16/11/2013 09:32:47 |
![]() 2747 forum posts 123 photos | Ian (Slo...) My first thought was that a log pot had inadvertently been used. As its not then something else is clearly amiss. Is the fact you mentioned wrongly labelled terminals a clue? I have not heard of the manufacturer you mentioned, nor of a VFD that did not work out of the box (after making a few simple checks or changes). What is the documentation like? does it give proper wiring diagrams and input output details of each connection? I would assume the pot is wired across a reference supply and the wiper feeds an analogue input terminal. It sounds (just possibly) that the pot is wired incorrectly.
Ian P |
WALLACE | 16/11/2013 09:47:16 |
304 forum posts 17 photos | 1 hp is only 720 watts or so - 1.5kw is probably ample. The slow ramp up on inverters helps to keep the current low on heavy start up loads as well. The only thing to avoid is to not start cutting before it's reached maximum revs as I once broke a milling cutter by trying to take a cut at much too slow a speed. W. |
jonathan heppel | 16/11/2013 10:24:42 |
99 forum posts | There really isn't a need to over specify a quality inverter. The manufacturers know what they're doing. |
Please login to post a reply.
Want the latest issue of Model Engineer or Model Engineers' Workshop? Use our magazine locator links to find your nearest stockist!
Sign up to our newsletter and get a free digital issue.
You can unsubscribe at anytime. View our privacy policy at www.mortons.co.uk/privacy
You can contact us by phone, mail or email about the magazines including becoming a contributor, submitting reader's letters or making queries about articles. You can also get in touch about this website, advertising or other general issues.
Click THIS LINK for full contact details.
For subscription issues please see THIS LINK.