chris j27/11/2012 12:22:37
338 forum posts
17 photos

Hi guys

I have decided to get a Jaguar Cub Inverter.

The Lathe is a 3ph version, and I have a 1ph supply.

Does anyone know if the coolant pump and/or worklight has a switchable transformer ?

Thanks Chris

Terryd27/11/2012 14:41:35
avatar
1946 forum posts
179 photos

Not sure,

Would Warco not know, they are usually very helpful?

Terry

mick H27/11/2012 14:47:54
795 forum posts
34 photos

Terry ........Is that an apprentice with you on your photo?

Mick

chris j27/11/2012 16:40:38
338 forum posts
17 photos
Posted by Terryd on 27/11/2012 14:41:35:

Not sure,

Would Warco not know, they are usually very helpful?

Terry

Could be Terry, but I thought I'd ask here while I wait for them to reply.

chris j28/11/2012 10:57:49
338 forum posts
17 photos
Posted by chris j on 27/11/2012 16:40:38:
Posted by Terryd on 27/11/2012 14:41:35:

Not sure,

Would Warco not know, they are usually very helpful?

Terry

Could be Terry, but I thought I'd ask here while I wait for them to reply.

Still no reply from warco ??

chris j02/12/2012 16:35:55
338 forum posts
17 photos
Posted by chris j on 28/11/2012 10:57:49:
Posted by chris j on 27/11/2012 16:40:38:
Posted by Terryd on 27/11/2012 14:41:35:

Not sure,

Would Warco not know, they are usually very helpful?

Terry

Could be Terry, but I thought I'd ask here while I wait for them to reply.

Still no reply from warco ??

Well I found Warco a little unhelpful tbh.

Rather than answer questions it would seem that selling me new boxes is their preference. Ah well.

Todays question is where does the neutral wire go ? Earth is easy and L1 to 3 are marked but whoever disconnected the lathe also undid the neutral wire between the main on/off switch and the fuse box and left it hanging - Grrr.

Any advice would be appreciated.

Brian O'Connor02/12/2012 17:30:08
74 forum posts
19 photos

Chris,

Presumably your motor is wired in delta configuration to work on 230/240v, in which case it doesn't need neutral (when connected in star configuration for 440v operation then it is usual to take the neutral to the star centre point).

In your case, connect the live, neutral and earth wires between the mains fuse box, On/Off switch and the Cub, but from the Cub to the motor all you need are the three phases and earth.

I have a Cub on my VMC so may be able to help if you have any more problems/questions.

Brian

chris j02/12/2012 17:39:43
338 forum posts
17 photos
Posted by Brian O'Connor on 02/12/2012 17:30:08:

Chris,

Presumably your motor is wired in delta configuration to work on 230/240v, in which case it doesn't need neutral (when connected in star configuration for 440v operation then it is usual to take the neutral to the star centre point).

In your case, connect the live, neutral and earth wires between the mains fuse box, On/Off switch and the Cub, but from the Cub to the motor all you need are the three phases and earth.

I have a Cub on my VMC so may be able to help if you have any more problems/questions.

Brian

Thanks Brian

The machine is wired 3ph. Not sure if it's star or delta.

The wiring between the fuse box and the motor is intact.

Between the rotary switch (on/off) is an Earth wire that goes to the fuse box (common earth point)

but there is a blue cable that is loose in the rotary and has been snipped off from somewhere in the fusebox as well.

chris j03/12/2012 10:02:23
338 forum posts
17 photos
It has been suggested that the neutral wire is not normally connected, can someone confirm maybe. ?
Thanks Chris
Andrew Johnston03/12/2012 10:29:59
avatar
7061 forum posts
719 photos

Correct. For a three phase motor connected in delta there is, by definition, no neutral point. For a motor connected in star the star point is effectively the neutral. However, if the system is balanced, ie, each phase has the same impedance, voltage and hence current, the current into, or out of, the star point is zero. So no need for a physical wire. Small three phase motors are generally considered to be balanced loads.

I've just wired up my Britan lathe to the three phase supply in the workshop and there is no neutral connection, just three phases and earth. The main drive motor clearly runs in both delta and star configurations, but still no need for a neutral.

Regards,

Andrew

chris j03/12/2012 10:33:53
338 forum posts
17 photos
Posted by Andrew Johnston on 03/12/2012 10:29:59:

Correct. For a three phase motor connected in delta there is, by definition, no neutral point. For a motor connected in star the star point is effectively the neutral. However, if the system is balanced, ie, each phase has the same impedance, voltage and hence current, the current into, or out of, the star point is zero. So no need for a physical wire. Small three phase motors are generally considered to be balanced loads.

I've just wired up my Britan lathe to the three phase supply in the workshop and there is no neutral connection, just three phases and earth. The main drive motor clearly runs in both delta and star configurations, but still no need for a neutral.

Regards,

Andrew

Brilliant, many thanks

Springbok03/12/2012 18:39:33
avatar
879 forum posts
34 photos

Bought a 3 phase system from Warco some years ago but they did not have a clue after that, found out the manufacturer and got it working.

Bob

chris j03/12/2012 18:46:23
338 forum posts
17 photos
Posted by Springbok on 03/12/2012 18:39:33:

Bought a 3 phase system from Warco some years ago but they did not have a clue after that, found out the manufacturer and got it working.

Bob

Sadly, my experience too.

I called Chester Machines for the answer. !!

Charlie,03/12/2012 22:29:10
76 forum posts
1 photos

Somone should put some curtiains in er, It sounds hollow, Every time somone speaks there is an echo,

All Topics | Latest Posts

Please login to post a reply.

Magazine Locator

Want the latest issue of Model Engineer or Model Engineers' Workshop? Use our magazine locator links to find your nearest stockist!

Find Model Engineer & Model Engineers' Workshop

Sign up to our Newsletter

Sign up to our newsletter and get a free digital issue.

You can unsubscribe at anytime. View our privacy policy at www.mortons.co.uk/privacy

Latest Forum Posts
Support Our Partners
cowells
Sarik
MERIDIENNE EXHIBITIONS LTD
Subscription Offer

Latest "For Sale" Ads
Latest "Wanted" Ads
Get In Touch!

Do you want to contact the Model Engineer and Model Engineers' Workshop team?

You can contact us by phone, mail or email about the magazines including becoming a contributor, submitting reader's letters or making queries about articles. You can also get in touch about this website, advertising or other general issues.

Click THIS LINK for full contact details.

For subscription issues please see THIS LINK.

Digital Back Issues

Social Media online

'Like' us on Facebook
Follow us on Facebook

Follow us on Twitter
 Twitter Logo

Pin us on Pinterest

 

Donate

donate