Coolant pump and VFD

All Topics | Latest Posts

Search for:  in Thread Title in  
Michael Horley07/06/2023 23:14:47
22 forum posts
2 photos

Good evening all. Can someone give me some advice on wiring up the coolant pump on my recently acquired Bantam Mk1 please?

I have a 3 phase motor running off a VFD but the coolant pump isn't connected, can I connect it up to the same terminals as the main motor? If so can I also wire in an on off switch?

Thanks in advance.

duncan webster07/06/2023 23:30:12
5307 forum posts
83 photos

You could run a coolant pump using a capacitor, called a Steinmetz circuit I think. Described in the little book on electric motors part of workshop practice series

Robert Atkinson 208/06/2023 07:58:48
avatar
1891 forum posts
37 photos

As long as the pump motor is much smaller than the main motor and the VFD is rated for more than the combines power of both yes you can connect the coolant pump in parallel with a switch. The main motor must be permanently connected to the VFD. If the pump motor is wired star (415 V) and the main motor has been changed to delta (240) I would initally leave the pump wired star and se if it produces enough flow for your use. Leaving it star will reduce the additional load on the VFD with the pump running. Make sure you use a 3 pole switch. While a 2 pole will work with normal 50Hz mains leavine one pole permanently connected to a VFD will cause an imbalance fo the high frequency PWM signal of the VFD. This can cause incorrect operation. damage to motor or drive and increased intereference.


Stienmetz is also an option see https://www.js-technik.de/en/faq/detail/groupid/4/id/75

Robert.

Andrew Tinsley08/06/2023 11:16:46
1817 forum posts
2 photos

Hello,

I had the same problem with an ML7 and a "Myford" 3 phase 415 volt suds pump. The pump was in star and was easily reconnected into delta configuration. I used a 2 microfarad capacitor to configure the motor into the Steinmetz set up

Worked a treat and i found that the 3 phase voltages were almost the same and were nearly 120 degrees in phase. The 2 microfarad capacitor was small enough to live inside the motor housing. So a very neat and practical way to run the suds pump off 240 Volt AC mains.

Andrew.

SillyOldDuffer08/06/2023 13:32:57
10668 forum posts
2415 photos
Posted by Andrew Tinsley on 08/06/2023 11:16:46:

Hello,

I had the same problem with an ML7 and a "Myford" 3 phase 415 volt suds pump. The pump was in star and was easily reconnected into delta configuration. I used a 2 microfarad capacitor to configure the motor into the Steinmetz set up

Worked a treat ...

Andrew.

Always worth putting figures on subjective statements like 'worked a treat'. When measured, Steinmetz connected motors perform significantly less well compared with running on a 3-phase supply:

  • At least 30% less power output
  • At least 70% less torque
  • 2-pole motors perform extra poorly, possibly turning not at all

When they work Steinmetz connected motors are a convenient compromise, not the best possible engineering solution. The most likely gotcha is low torque, so more likely to perform acceptably on Suds pumps and similar applications that don't need lots of turning power.

If Steinmetz connections worked well in all circumstances there would be no market for rotary converters and VFDs. More sophisticated approaches to 3-phase come with significant advantages, VFD's being extra tasty with speed control, torque boost, soft-start, and efficiency savings. But usually limited to one motor per VFD. On the other hand, if it works, simplifying a major rewire job by adding a small capacitor to an existing motor is fit for purpose and value for money. Just don't expect miracles!

Dave

Emgee08/06/2023 13:51:07
2610 forum posts
312 photos

The coolant pump on my Bantam is 400v 3 phase working voltage but it has been used occasionally for many hours during the last 20 years with the capacitor method of connection to a 240v AC supply.

Emgee

Andrew Tinsley08/06/2023 14:12:20
1817 forum posts
2 photos

Hello Dave,

Sounds as if you are in one of your "be careful moods" Absolutely no one is talking about large motors and the deficiency of the Steinmetz system re reduced torque and power! A suds pump motor is way overated for the job it does. Your warnings of grief are most certainly over the top. If emgeee can use such a motor connected WITHOUT the Steinmetz capacitor and without reconfiguring the voltage from 415 to 240 volts Then your Jerimiah predictions are totally invalid.

I certainly would not try to emulate emgee, but a correct value Steinmetz capacitor and rewiring to 240 V is a totally logical thing to do without any drawbacks.

If I were suggesting the Steinmetz system for a 5 HP lathe motor, then your comments would have validity. Please don't put people off from modding a suds pump in the same way.

Andrew.

duncan webster08/06/2023 17:19:37
5307 forum posts
83 photos

Steinmetz worked for me on Ferret grinder. The motor manufacturers recommended. Not running it off a vfd, something to do with old motors and insulation, but we're quite happy with my solution.

Mark Rand08/06/2023 17:27:43
1505 forum posts
56 photos

If you are using the VFD just to generate 50Hz three phase then JFDI* and feed the suds pumpfrom the VFD as well.

If you are using the VFD for variable speed purposes, then use a capacitor.

 

* Just Flipping Do It! cheeky

Edited By Mark Rand on 08/06/2023 17:28:53

Michael Horley08/06/2023 19:39:47
22 forum posts
2 photos

Thanks for all your comments, I have ordered a 2mfd capacitor so I will try that first.

Andrew Tinsley08/06/2023 21:22:46
1817 forum posts
2 photos

Hello Michael,

If you are going to supply 240V Ac to your pump, it may be better to rewire the motor to a star configuration rather than the 440 V delta which it is at the moment. Be careful in selecting a capacitor. The usual motor start capacitors are electrolytic and won't last long before they go bang in a Steinmetz circuit. The type you need are non electrolytic types and rated at 400 V DC or near. These are the types found in Motor run capacitor circuits. Or in fluorescent lamp units (or any power factor correction usage, where it is connected across the mains)'

The 2 microfarad capacitor that I used was selected after a little experimenting. I wanted the 3 phases to be near enough equal in voltage and at almost 120 degree phase difference. A 2 microfarad capacitor will work on your suds pump , but it may not give the optimum results of equal phase voltage and 120 degree phase separation. Not that it is all that important. It should give you an operational pump running on 240 V Ac.

Andrew.

Michael Horley08/06/2023 23:06:05
22 forum posts
2 photos

Thanks Andrew. I had already ordered the 2mfd capacitor after delving through the net looking for Steinmetz so your previous post confirmed I was in the right ball park!

I have just checked and it is a motor run type so hopefully it will work.

SillyOldDuffer09/06/2023 10:01:09
10668 forum posts
2415 photos
Posted by Andrew Tinsley on 08/06/2023 14:12:20:

Hello Dave,

Sounds as if you are in one of your "be careful moods" Absolutely no one is talking about large motors and the deficiency of the Steinmetz system re reduced torque and power! A suds pump motor is way overated for the job it does. Your warnings of grief are most certainly over the top. If emgeee can use such a motor connected WITHOUT the Steinmetz capacitor and without reconfiguring the voltage from 415 to 240 volts Then your Jerimiah predictions are totally invalid.

I certainly would not try to emulate emgee, but a correct value Steinmetz capacitor and rewiring to 240 V is a totally logical thing to do without any drawbacks.

If I were suggesting the Steinmetz system for a 5 HP lathe motor, then your comments would have validity. Please don't put people off from modding a suds pump in the same way.

Andrew.

I plead not guilty M'lud!

After providing numbers showing the actual limitations of Steinmetz , I finished my post with:

On the other hand, if it works, simplifying a major rewire job by adding a small capacitor to an existing motor is fit for purpose and value for money. Just don't expect miracles! Is that really a Jeremiad?

All engineering is conditional, and most of it can be expressed numerically. Bridges, ropes, aircraft and ships have weight limits. Car batteries only contain so many ampere-hours, internet connections have bandwidth and latency restrictions. Threads have to be cut accurately or they won't fit. It's useful to understand the underlying rules.

In engineering, guesswork, hearsay, optimism and random experience are all low value compared with knowledge. It's why the forum is wonderful: others know stuff I don't. When something doesn't work, we can establish why not and what to do about it. Sometimes the answer is a lemon.

Dave

duncan webster09/06/2023 10:13:29
5307 forum posts
83 photos
Posted by Andrew Tinsley on 08/06/2023 21:22:46:

Hello Michael,

If you are going to supply 240V Ac to your pump, it may be better to rewire the motor to a star configuration rather than the 440 V delta which it is at the moment. Be careful in selecting a capacitor. The usual motor start capacitors are electrolytic and won't last long before they go bang in a Steinmetz circuit. The type you need are non electrolytic types and rated at 400 V DC or near. These are the types found in Motor run capacitor circuits. Or in fluorescent lamp units (or any power factor correction usage, where it is connected across the mains)'

The 2 microfarad capacitor that I used was selected after a little experimenting. I wanted the 3 phases to be near enough equal in voltage and at almost 120 degree phase difference. A 2 microfarad capacitor will work on your suds pump , but it may not give the optimum results of equal phase voltage and 120 degree phase separation. Not that it is all that important. It should give you an operational pump running on 240 V Ac.

Andrew.

Andrew,

Are you sure you've got that the right way round? It conflicts with your earlier post, and I rewired my grinder to delta when I did it.

Andrew Tinsley09/06/2023 10:30:41
1817 forum posts
2 photos

Thanks Duncan,

Must be old age, the motor should be wired for 240 Volts i.e. delta connected. goodness knows what I was thinking of.

Andrew.

Michael Horley25/06/2023 22:38:39
22 forum posts
2 photos

Just to close this off, I used a 2mfd capacitor across two of the phases and 240v across one of those and the other phase. The pump works perfectly with a good strong flow.

Thanks everyone.

All Topics | Latest Posts

Please login to post a reply.

Magazine Locator

Want the latest issue of Model Engineer or Model Engineers' Workshop? Use our magazine locator links to find your nearest stockist!

Find Model Engineer & Model Engineers' Workshop

Sign up to our Newsletter

Sign up to our newsletter and get a free digital issue.

You can unsubscribe at anytime. View our privacy policy at www.mortons.co.uk/privacy

Latest Forum Posts
Support Our Partners
cowells
Sarik
MERIDIENNE EXHIBITIONS LTD
Subscription Offer

Latest "For Sale" Ads
Latest "Wanted" Ads
Get In Touch!

Do you want to contact the Model Engineer and Model Engineers' Workshop team?

You can contact us by phone, mail or email about the magazines including becoming a contributor, submitting reader's letters or making queries about articles. You can also get in touch about this website, advertising or other general issues.

Click THIS LINK for full contact details.

For subscription issues please see THIS LINK.

Digital Back Issues

Social Media online

'Like' us on Facebook
Follow us on Facebook

Follow us on Twitter
 Twitter Logo

Pin us on Pinterest

 

Donate

donate