Neil Wyatt22/11/2020 16:46:07
avatar
19226 forum posts
749 photos
86 articles

I picked up a four-way plug strip earlier and there was a huge band and big white flash. It tripped the workshop ring breaker and the supply breaker in the house but not two RCDs in the path.

On dismantling the strip there was no obvious fault, but I could see where a small bit of metal must have got inside and shorted across the brass strips carrying live and neutral - no earth imbalance to trip the RCDs.

Whatever it was that cause the short vaporised, along with some of the brass and plastic.

I binned it, although it would probably have been OK, as at the far end to the problem was a crack and a hole about 6mm across (where the metal got in?)

I suppose what is striking is how bright it must have been to make such a flash visible through the casing, it must have been in the order of several tens of amps to trip the main breaker for the workshop spur instantly.

Neil

Frances IoM22/11/2020 16:57:53
1395 forum posts
30 photos
was the strip not fused - preferably with a 10A fuse as the usual cable used must be to Chinese standards.
Bazyle22/11/2020 16:58:18
avatar
6956 forum posts
229 photos

n opportune moment to mention a system we have going at the men's shed. A local group collects things like that lead and similar scrap and have a team of people with various mobility problems who strip out the metal. This makes it higher value scrap and gives the guys inolved some occupational therapy. See if you can find a similar group near you.

Steve Skelton 122/11/2020 17:00:41
152 forum posts
6 photos

Neil, potential fault currents can be in the order of thousands of amps depending on the impedence of the cables supplying it.

In an extension socket lead, I would imagine it is somewhere between 500 and 2000A depending on how close to the origin of the installation the socket was.

Steve

SillyOldDuffer22/11/2020 17:57:26
10668 forum posts
2415 photos

Spectacular flash when a ribbon of aluminium swarf found it's way into my mini-lathe's control box and shorted out across the motor feed.

As it didn't damage the board or blow a fuse I reckon half the light was chemical - the swarf caught fire and went off like a photoflash.

I wonder how many of us have blown the tip off a screwdriver with a 300V 16uF valve power supply capacitor? Happy days...

smiley

Dave

Nick Clarke 322/11/2020 18:58:49
avatar
1607 forum posts
69 photos
Posted by SillyOldDuffer on 22/11/2020 17:57:26:

Spectacular flash when a ribbon of aluminium swarf found it's way into my mini-lathe's control box and shorted out across the motor feed.

As it didn't damage the board or blow a fuse I reckon half the light was chemical - the swarf caught fire and went off like a photoflash.

I wonder how many of us have blown the tip off a screwdriver with a 300V 16uF valve power supply capacitor? Happy days...

smiley

Dave

In the days when you could smoke in pubs panatella cigars came in tins about 90mm dia and 150mm tall litho'ed a beige/pink colour. When empty these were prized for workshop storage but the print soon wore off.

I was handed one with shiny metal showing in several places and asked if I could get the lid off as it was stuck.

Electric shock and tin thrown across the room with much swearing. It had insulating tape around the rim to insulate the tin from the lid and a large fully charged electrolytic soldered between the two! He only held the tin, not the lid while I grabbed one in each hand.

I don't know what the guy charged it from, and you can't get the tins today, thank goodness!

Nigel Bennett23/11/2020 13:41:10
avatar
500 forum posts
31 photos

I had a near similar experience once when I casually picked up a 4-way adaptor and the outer plastic shell crumbled in my hand. How I didn't short two contacts I know not - but I checked all the others in the house immediately after. I literally crushed the adaptor into hundreds of pieces with my hands as I threw it away. It hadn't been out in the sun or anything - it was tucked away behind the PC.

Some Chinese rubbish we'd got from a cheapie shop somewhere.

If you are thinking of doing the crush test on one, do unplug it first...

Robert Atkinson 223/11/2020 14:14:36
avatar
1891 forum posts
37 photos

Another example of why VFDs shouls always be in an enclosure, swarf gets everywhere

Samsaranda23/11/2020 14:21:33
avatar
1688 forum posts
16 photos

A few years ago now I was installing a new kitchen and drilled into a wall on which to hang a cupboard unit, there was an almighty flash and a bang, our cat who had been watching from a distance shot off upstairs. It transpired that I had drilled into a hidden and unforeseen spur of the downstairs ring main, the masonry drill had gone dead centre between the live and neutral, this promptly vaporised it and on subsequent examination I found that the episode had blown the providers main fuse, at that time I think it was 100 amps. We had recently moved into the property and the distribution board was about the most basic you could get and had rewireable fuses, needless to say that board is long gone and replaced with a split load board with mcb’s and rcd. My workshop has a separate board fed via an rcd and has a mixture of cartridge fuses and mcb’s, replacing the cartridges with mcb’s as and when I can get the correct ones. You can never be too careful when electrical safety is concerned, had quite a few incidences involving electricity and so far survived them.
Dave W

Simon036223/11/2020 15:15:16
279 forum posts
91 photos

Many years ago I was trying to fault find a failing power connection which I traced back to the fused consumer unit. Checking using my newly acquired digital voltmeter across the switch revealed that apparently 220V existed but nothing was happening at the business end of the circuit. I then switched to the 10A setting and placed the meter in line which showed a few milliAmps were flowing. After digesting this a bit more I decided to check the volts again. Unfortunately I did this before returning the meter to a voltage configuration and promptly put a straight short across 220 V - the loud bang and flash left me stunned for a while, although fortunately neither I nor the house was harmed. The meter apparently was not reacting though since shorting the leads or connecting one directly into the other socket gave no visible readings. It turned out that both leads had gone open circuit, swiftly cured by a trip to Maplins.

Ever after, I have made a conscious effort to take a current reading and then return the leads to the voltage configuration.

I think the flash was my guardian angel briefly attending to me..... angel

Howard Lewis23/11/2020 15:41:30
7227 forum posts
21 photos

Whist spending a year of my Apprenticeship in the Electronics and Vibration Lab, At the end of the day, I went to pull the plug for the Mullard Valve Tester from the socket. The top came off and finger and thumb went neatly across the Live and Neutral pins. Much to the amusement of my colleagues! Fortunately the flloor was proof against 5 Kv, so the shock did minimal damage, except to my pride.

More recently, one New Years Eve afternoon, the motor on the Myford emitted a big flash and ceased operating. Fortunately, the local motor rewinders still had a couple of chaps working. They soon diagnosed a bit of Ali swarf in the centrifugal switch, cleaned up everything and it worked again. Since the job was so quick, it had not even been booked in, So a drink for their efforts, and return home to refit the motor.

The next job was to make a simple cover to keep motor separate from stray swarf!

Howard

Neil Wyatt23/11/2020 16:53:08
avatar
19226 forum posts
749 photos
86 articles
Posted by Frances IoM on 22/11/2020 16:57:53:
was the strip not fused - preferably with a 10A fuse as the usual cable used must be to Chinese standards.

I didn't bother testing the plug fuse, I assume it blew too. It wasn't a cheap unit, just had been in the workshop for a decade or more.

Neil

John Baguley23/11/2020 18:08:51
avatar
517 forum posts
57 photos

My cordless kettle did a similar thing last week. I switched it on to make a cuppa, there was an almighty bang and it leapt off the base! It tripped the 32 amp breaker but the 13amp fuse in the plug was still intact when I checked it. Needless to say, the kettle went in the bin as it was only a cheapy and I ordered a new kettle.

Before binning it I took it to bits and there was no obvious sign of any damage. When I checked the element though it was high resistance between live and neutral and high resistance live and neutral to earth. Presumably the element had failed and shorted out inside.

John

Harry Wilkes23/11/2020 18:59:30
avatar
1613 forum posts
72 photos

My biggest 'bang' was during my time in the steel works and it was a case of ' familiarity breeds competent' myself and a fellow sparky had just changed large DC compound motor normal procedure was to run the motor with the shunt field disconnected to check direction then the shunt field was connected and the series field shorted out. At the rear of the control panel the armature cables were red and the series field were both green so without checking I shorted out the two greens restored power I then signaled to the other sparky to try the motor when he did there was an almighty BANG filling the control room with dust. When the control room was clear we checked what the cause of the problem was I had shorted the armature connections due to the colors being reversed the 350 amp fuses had completely disintegrated so too the ceramic fuse carriers strangely the two fuse bases had survived !

H

David Davies 823/11/2020 21:44:55
avatar
202 forum posts
1 photos

Simon 0362 wrote:-

"Unfortunately I did this before returning the meter to a voltage configuration and promptly put a straight short across 220 V."

This mistake is easily made. For this reason, at work, the leads supplied with (Fluke) multimeters were removed and replaced with leads having fused prods before the instruments were issued to our electricians.

Because of the fused leads an instruction was also made that the electricians should test their meters on a known live circuit at the start of each shift thus proving that the fuses within the prods of the leads were healthy.

Dave

Martin Kyte23/11/2020 22:24:56
avatar
3445 forum posts
62 photos

Apparantly AVO 8's are indestructable. Apart from,that is, when connected accross the Southern Region in current mode.

Not done by me I hast'n to add.

regards Martin

Nigel Graham 223/11/2020 22:27:31
3293 forum posts
112 photos

Among my illustrious c.v. details are Post Office Telephones - Trainee Technician (Apprentice) - failed. One afternoon when I was seconded to the team installing the telephone system in the newly-built local Council Offices, I was asked to plug in a 13A extension-lead in an adjoining room. As I did so there was sharp crack, accompanied by a sheet of flame from between two fingers, and a scream I think was probably me, but which brought the others rushing to my aid. One took me back to the depot, with a strip of skin hanging from one finger, to patch me up and cure the non-electrical shock with a mug of tea. I expect they had an accident-book but nowadays we'd be filling in forms while drinking the tea....

I spent some years working with piezo-electric devices, and the larger used big p-e ceramic stacks in parallel. Those had to be kept shorted because if left open-circuit, even just the tiny mechanical shocks from moving them about, or from the daily room-temperature changes, were enough for them to build up dangerously high static charges. They caught me out once or twice, but luckily only by small warning "bites".

Oven Man23/11/2020 22:52:42
avatar
204 forum posts
37 photos

Carbon fibre filaments can create some excitement among electrical gear. It took some little time to fathom out what was blowing fuses on the furnaces we had a Rolls-Royce for making carbon fibre back in the 70s. You can't see them coming and they don't leave much of a trace when they short out two phases. No burn marks, it all goes up as CO2.

Peter

John Baguley23/11/2020 22:53:15
avatar
517 forum posts
57 photos

You've just reminded me Nigel. I also worked for the GPO and then later BT. I was working in Belper telephone exchange installing another shelf of equipment on one of the old Strowger racks which involved fitting a new fuse mounting on the live busbars that ran down one side of the rack. It had to be done live to avoid interuptions to service. I had done this many times before but this time somehow managed to stick my 81's (pliers) straight across the busbars whilst wiring up the fuse mounting. This did cause an almighty flash and bang and took the main fuse out that fed that particular suite of equipment. Can't remember now but probably 250amp. Needless to say, my 81's were now missing a big chunk and two of my fingers got copper plated! Extremely painful and the pain lasted a couple of days. Fortunately, the chap I was working with managed to get a spare fuse in before anyone noticed the loss of service and the incident went unreported!

Apparently, a chap doing some painting in Derby exchange put his tin of paint on top of the main busbars feeding a whole floor of equipment and that had quite spectacular results!

John

Don Cox23/11/2020 23:34:59
63 forum posts

I too worked for Post Office telephones starting as a "Youth in Training." After a couple of enjoyable years charging about in a dark green Mini Van fixing customer's faults I was taken on as an exchange maintainer working on Strowger (clock work) equipment.

The contact array, which two motion selectors stepped over to make the forward connection, consisted of 11 contacts arranged in a semi-circle, stacked 20 high with plastic separators insulating adjacent contacts, these were known as "banks". Occasionally we would get a contact fault between contacts and since these banks were usually connected in multiples of 20 ( on two shelves of equipment) finding which bank unit was involved was quite a task. One of the old hands told me that these faults were usually caused by wayward bits of solder etc left behind during manufacture and that actually taking the trouble to locate the cause took up too much time and effort. The standard method to clear the fault was to apply the exchange 50 volt DC supply either side of the fault protected with the smallest fuse possible (0.25 Amps I think). Nine times out of ten this cleared the fault with no recurrence and didn't blow the fuse. The one in ten which persisted involve a lot more work, but that's another story. I have used this technique quite a few times to clear car electrical faults over the years too.

All Topics | Latest Posts

Please login to post a reply.

Magazine Locator

Want the latest issue of Model Engineer or Model Engineers' Workshop? Use our magazine locator links to find your nearest stockist!

Find Model Engineer & Model Engineers' Workshop

Sign up to our Newsletter

Sign up to our newsletter and get a free digital issue.

You can unsubscribe at anytime. View our privacy policy at www.mortons.co.uk/privacy

Latest Forum Posts
Support Our Partners
cowells
Sarik
MERIDIENNE EXHIBITIONS LTD
Subscription Offer

Latest "For Sale" Ads
Latest "Wanted" Ads
Get In Touch!

Do you want to contact the Model Engineer and Model Engineers' Workshop team?

You can contact us by phone, mail or email about the magazines including becoming a contributor, submitting reader's letters or making queries about articles. You can also get in touch about this website, advertising or other general issues.

Click THIS LINK for full contact details.

For subscription issues please see THIS LINK.

Digital Back Issues

Social Media online

'Like' us on Facebook
Follow us on Facebook

Follow us on Twitter
 Twitter Logo

Pin us on Pinterest

 

Donate

donate