Ajohnw | 07/01/2017 22:58:26 |
3631 forum posts 160 photos | RCD's do not provide protection against electrocution Nick. They are there to prevent fires. The claim is that the bulk of fires in the UK are caused by faults in the electrical circuitry in houses. I have had a kick from the mains at work a couple of times. Wouldn't surprise me if the bulk of house fire of this nature were down to rubber insulated house wiring that has perished but statistics are statistics and don't always account for cause on things like this - just like the effect of so called safety cameras hidden around corners to catch people for minor speeding offences. Quick edit. I thought that a range of rcd trip currents were still available The low limit was either 5 or 10ma - can't remember which. Next step as I understand it is none at all and clear marking but it's hard to see why at this level. John - Edited By Ajohnw on 07/01/2017 23:05:09 |
Emgee | 07/01/2017 23:30:35 |
2610 forum posts 312 photos | Posted by Ajohnw on 07/01/2017 22:58:26:
RCD's do not provide protection against electrocution Nick. They are there to prevent fires. The claim is that the bulk of fires in the UK are caused by faults in the electrical circuitry in houses. JohnJohn, 30ma tripping current of the RCCB is so designed to prevent fibrillation and so prevent death by electric shock and is well documented . Prevention of fires by electrical faults can normally be achieved by the use of a 100ma RCCB. Emgee Edited By Emgee on 07/01/2017 23:36:19 |
Clive India | 08/01/2017 09:24:58 |
![]() 277 forum posts | Posted by Emgee on 07/01/2017 23:30:35:
Posted by Ajohnw on 07/01/2017 22:58:26:
RCDs do not provide protection against electrocution Nick. They are there to prevent fires. The claim is that the bulk of fires in the UK are caused by faults in the electrical circuitry in houses. John John, Yes, agree with Emgee. The downside is they breed over-confidence when working on live circuits. |
Michael Gilligan | 08/01/2017 09:38:53 |
![]() 23121 forum posts 1360 photos | Posted by Clive India on 08/01/2017 09:24:58:
... The downside is they breed over-confidence when working on live circuits. . There must be a 'Darwin' joke in there ^^^ MichaelG. |
Rick Kirkland 1 | 08/01/2017 09:49:29 |
![]() 175 forum posts | Unfortunately there is a load of inaccurate and somewhat dangerous crap being spouted in this thread by people who obviously know NOTHING about protective devices and their usage. I hope to God none of those spouting said crap have got the nerve to call themselves Electricians. There is also a lot of truthful fact being posted especially regarding the requirements of BS7671, 17th edition to Amd 3, 1st January 2015. THAT is the satandard to which I have to carry out my work. The sad part is I actually work with other Electricians, term used loosely who are unable or too idle to read the book and understand it. And before ANYBODY starts shouting about the onsite guide, that is ALL it is, , a guide. I look at certificates where the column asking for the " max Zs permitted under BS7671" is put down as one of the figures from a table in the onsite guide. TOTALLY WRONG. And in the Electricity at work act the legislation forbids working on live circuits unless absolutely impracticable to do so. It is NOT ok to work on live circuits thinking and RCD will protect you from stupidity. For Gods sake STOP messing with things you don't understand and get someone in who does. IT COULD SAVE YOUR LIFE. What price do you put on your life? ? Edited By Rick Kirkland 1 on 08/01/2017 09:51:16 |
Toby | 08/01/2017 09:51:10 |
117 forum posts 17 photos | John, you cannot use an earth spike for bonding you will get nowhere close to the resistance required. As to the size of the bonding, don't forget you need to consider faults external to the building as well as internal. And you cannot assume that just because today your water pipe is low resistance to the supply earth it will be so next year. I agree with the comments about RCDs breeding over-confidence, too many people think they prevent an electric, as in some how magically prevent more than 30mA going through. Whereas in practice all they do is limit the duration of the shock.
|
Rick Kirkland 1 | 08/01/2017 09:59:46 |
![]() 175 forum posts | Here we go again. LISTEN UP! !! You do NOT earth to a water pipe. Bonding is in fact used to prevent electric shock due to the water pipe PROVIDING EARTH POTENTIAL ! Will you people stop posting inaccurate, dangerous ideas on here. I can see another thread coming up where a person asks, I've just bought a new 14inch swing by 40 inch between centres lathe, what kind of things can I make on it? And someone answers "you could make a large cast iron fruit bowl by sitting on the compound slide with the cutting tool taped to your arm, , I'm sure this will be ok as I've seen photos of massive industrial lathes with the operator sat in a chair on the saddle as the lathe does its work. Some of you lot are death waiting to happen. I really cannot believe what I'm reading here. |
Toby | 08/01/2017 10:03:41 |
117 forum posts 17 photos | Posted by Rick Kirkland 1 on 08/01/2017 09:49:29:
Unfortunately there is a load of inaccurate and somewhat dangerous crap being spouted in this thread by people who obviously know NOTHING about protective devices and their usage. ........... Come on Rick, don't hold back, tell us what you really think Seriously though, electrics is no different to anything else, for example hobbyists messing with dangerous metalworking machines that they have little experience of I think the great thing is people can post what they like on forums like this and there will hopefully be someone around to correct them if they mis-understand something. Like you say, there are plenty of "electricians" out there that don't really have a clue what the regs mean or why so it is hard to criticise a non electrician for occasionally getting it wrong. |
Toby | 08/01/2017 10:21:28 |
117 forum posts 17 photos | Posted by Rick Kirkland 1 on 08/01/2017 09:59:46:
Here we go again. LISTEN UP! !! You do NOT earth to a water pipe. Bonding is in fact used to prevent electric shock due to the water pipe PROVIDING EARTH POTENTIAL ! Will you people stop posting inaccurate, Ok, I cannot resist this- that is not quite accurate the external potential can be something other than earth Edit: btw, for those that want to read up on earthing and bonding I can recommend the IET guidance note 8 (earthing and bonding). A riveting read (ok, maybe not...) which gives a lot more info although I think doesn't go far enough in explaining why as apposed to just what....... Edited By Toby on 08/01/2017 10:24:34 |
Toby | 08/01/2017 10:34:13 |
117 forum posts 17 photos | btw. While I am correcting things, I need to give myself a good slap and correct myself! Yesterday I said...... Posted by Toby on 07/01/2017 17:30:49:
Bonding is a real can of worms! This is one area where it should be sorted even it was ok against the regs when installed. Hence the gas man giving everyone leaflets saying it must be done. In fact the 10mm2 min is actually for PME/TNC, for TNCS or TT it can sometimes be 6mm2.
That should of course have read " In fact the 10mm2 min is actually for PME/TNCS, for TNS or TT it can sometimes be 6mm2". |
Ajohnw | 08/01/2017 10:49:16 |
3631 forum posts 160 photos |
I'd strongly advise people not to stick one hand on a well bonded sink and then poke a finger on the other hand into something live. Sums it up pretty well really. That particular path is worst case. It also looks like there is no specific call for sink bonding in BS7671 or by the IET. This may be why.
John - |
Steven Vine | 08/01/2017 11:01:28 |
340 forum posts 30 photos | Posted by Rick Kirkland 1 on 08/01/2017 09:49:29: Aw Rick. Is that too harsh? I think I've learned all I need to know about consumer units and electrical equipment from this thread. I am now even confident enough to go change my consumer unit, in case it goes up in flames due to the rubber wiring. I plan to go down the local pub and pick up some more information and 'hearsay' from the drinkers before I start. I'll probably thumb through the Screwfix catalog as well, as it contains a wealth of information for potential installers! And of course I will wear thick heavy gloves as I dismantle the consumer unit, in case the rats get me. LOL. (Ps, I'll probably do it live, as I am one of those with a different immunity to electric shocks). Steve Edited By Steven Vine on 08/01/2017 11:18:37 Edited By Steven Vine on 08/01/2017 11:31:02 |
Emgee | 08/01/2017 11:30:48 |
2610 forum posts 312 photos | Posted by Rick Kirkland 1 on 08/01/2017 09:49:29:
And before ANYBODY starts shouting about the onsite guide, that is ALL it is, , a guide. I look at certificates where the column asking for the " max Zs permitted under BS7671" is put down as one of the figures from a table in the onsite guide. TOTALLY WRONG. Edited By Rick Kirkland 1 on 08/01/2017 09:51:16 Hi Rick If the Zs table (A41.1to A41.6?) in the on-site guide is copied from and the same as that included in BS7671 why is it wrong to enter the Max Zs permitted for the cct by reference to a table of values ? provided of course the correct part of the table is selected for the type and rating of the protective device and maximum disconnection time for the cct. The cct measured Zs value will be written in the relevant column in the test readings to check compliance. Emgee |
Mark C | 08/01/2017 11:37:40 |
707 forum posts 1 photos | Just a point regarding the Darwin risk. If you do some stupid thing in your workshop and rip your hand off, you probably will learn a valuable lesson but it will most likely be limited to personal education. If you arse with electrics the collateral damage almost certainly will include OTHERS. This is the distinction between competent persons, they are the ones who know that they don't have the correct information and go find it rather than a quick look on wikipedia and some assumptions about what "they" think should be OK. Mark |
Toby | 08/01/2017 11:38:19 |
117 forum posts 17 photos | Posted by Ajohnw on 08/01/2017 10:49:16:
I'd strongly advise people not to stick one hand on a well bonded sink and then poke a finger on the other hand into something live. Sums it up pretty well really. That particular path is worst case. It also looks like there is no specific call for sink bonding in BS7671 or by the IET. This may be why.
John - John, you are going to have to explain what exactly you disagree with. Safe currents and voltages are always going to depend on circumstances and the subject. Just because RCDs don't work sometimes (no surprised to anyone I hope....) doesn't mean they don't serve a purpose. Ditto earthing and bonding. And why should the regs have something specific to kitchen sinks? The general rules on bonding cover them just fine. We could start a whole new discussion on when to bond and when not to but I don't think that would be appreciated As to live working, it is clear Rick was talking about domestic electrical work and he is right, there is no excuse for live working there except just lazyness. I know we are all tempted to bend the rules sometimes but that isn't really an excuse. I can tell you from experience that when the DNO fuse goes with a big bang and a flash you feel pretty embarrassed and stupid! On the other hand, if your job happens to be connecting up a new supply from the road to a house you would be well used to working live (in a hole in the road, half full of water.......) |
Rick Kirkland 1 | 08/01/2017 11:38:40 |
![]() 175 forum posts | I've just bought a brand new Atomic bomb. It has a detonator which is touch sensitive, like one of those bedside table lamps and a vibration detection detonator that goes off at the slightest movement. I need to get it into the corner of my workshop. Would it be ok to nudge it into the corner using a bulldozer with a rubber sheet covering the blade. Charlie down the pub said he didn't think it would be a problem and he could guide it with his hands as long as he was wearing leather gloves. What do you think as I'm new to nuclear devices and am not prepared to pay the people who are experts in the field and do this professionally . Ps. It's four feet wide, nine feet high and my doorway is a standard 6' x 2'6". What should I do about that? My wife seems unhappy about the whole project as too. |
Ajohnw | 08/01/2017 11:38:41 |
3631 forum posts 160 photos | Posted by Toby on 08/01/2017 10:21:28:
Posted by Rick Kirkland 1 on 08/01/2017 09:59:46:
Here we go again. LISTEN UP! !! You do NOT earth to a water pipe. Bonding is in fact used to prevent electric shock due to the water pipe PROVIDING EARTH POTENTIAL ! Will you people stop posting inaccurate, Ok, I cannot resist this- that is not quite accurate the external potential can be something other than earth Edit: btw, for those that want to read up on earthing and bonding I can recommend the IET guidance note 8 (earthing and bonding). A riveting read (ok, maybe not...) which gives a lot more info although I think doesn't go far enough in explaining why as apposed to just what....... Edited By Toby on 08/01/2017 10:24:34 I'd second that comment Toby. If they want to know why not just buy the IET guide. Maybe I am a control freak but maybe not. I like to know what should be done who ever does it. It can be useful. For instance the gas pipe bonding. The guide states something entirely different in my situation where the meter isn't in the house so if some one at some point wants to wreck the appearance of the place which seems likely I can point that out. I understand that the guide may mention things that the building regs don't and the advice is to follow them 'cause if something goes wrong an electrician might find themselves being sued. Toby has raised an interesting point as to why. For instance if some one has a metal waste pipe that contacts the earth it must be bonded.
As to 100ma RCD's. I have no need. If I did I would take the trouble to find out the why's a wherefores of their use. The only reason I posted the link was to show that they were available. John - |
Russell Eberhardt | 08/01/2017 11:40:24 |
![]() 2785 forum posts 87 photos | This thread is getting silly! Russell. |
Rick Kirkland 1 | 08/01/2017 11:44:36 |
![]() 175 forum posts | Toby. . I'm giving up now. You on the other hand could go on for ever answering comebacks from people with just enough dangerous knowledge in their possession to keep making comebacks. This is one of the reasons I've not (and many others that have made themselves known to me) have not posted here for a couple of years.I'm in no way painting everyone with the same brush, but the term 'babies playing with loaded guns" springs to mind. |
Toby | 08/01/2017 11:55:43 |
117 forum posts 17 photos | Posted by Emgee on 08/01/2017 11:30:48:
Posted by Rick Kirkland 1 on 08/01/2017 09:49:29:
And before ANYBODY starts shouting about the onsite guide, that is ALL it is, , a guide. I look at certificates where the column asking for the " max Zs permitted under BS7671" is put down as one of the figures from a table in the onsite guide. TOTALLY WRONG. Edited By Rick Kirkland 1 on 08/01/2017 09:51:16 Hi Rick If the Zs table (A41.1to A41.6?) in the on-site guide is copied from and the same as that included in BS7671 why is it wrong to enter the Max Zs permitted for the cct by reference to a table of values ? provided of course the correct part of the table is selected for the type and rating of the protective device and maximum disconnection time for the cct. The cct measured Zs value will be written in the relevant column in the test readings to check compliance. Emgee I have to admit I am not clear what Rick means, the on site guide tables are not the same as BS7671 as the on-site has a 0.8 correction factor to take into account conductor temperature. I wonder if he is referring to Cmin, I don't have the latest copy of the guide to check if that is now included in the tables. Or maybe Rick is refering to circuits with RCDs where Zs can exceed this figures (but Zln should not....). Actually that is something that has always annoyed me, the certs (and hence what most people test) concentrates on Zs, completely ignoring that it still needs to work with a Line-Neutral fault. EDIT: but yes, Rick's post above mine and Russell before that are right, I am also going to shut up now Edited By Toby on 08/01/2017 12:00:05 |
Please login to post a reply.
Want the latest issue of Model Engineer or Model Engineers' Workshop? Use our magazine locator links to find your nearest stockist!
Sign up to our newsletter and get a free digital issue.
You can unsubscribe at anytime. View our privacy policy at www.mortons.co.uk/privacy
You can contact us by phone, mail or email about the magazines including becoming a contributor, submitting reader's letters or making queries about articles. You can also get in touch about this website, advertising or other general issues.
Click THIS LINK for full contact details.
For subscription issues please see THIS LINK.