Insulation tester - some guidance please

All Topics | Latest Posts

Search for:  in Thread Title in  
Sandgrounder20/12/2018 13:26:50
256 forum posts
6 photos
Posted by Emgee on 20/12/2018 10:31:12:

I believe the Megger linked to by Michael is not working correctly, the meter is indicating a reading when not being cranked, without operating the handle the needle will be at 1 end of the scale, don't remember which end but I used that type of instrument for a few years before digital meters were available.

Emgee

That's the normal position for the needle to be when not being used, my 500V model which is the same as shown works perfectly, a quote from the manual describing the how they work,

"there is no appreciable restoring force to make the pointer come to rest in any particular position"

martin kilroy 120/12/2018 13:56:23
4 forum posts

Measuring insulation resistance with high DC (relative to normal operating voltage) is pointless if all you are trying to ascertain is whether the equipment is safe to energize. Take a typical domestic 240V installation with MCB overcurrent protection and 30mA RCD earth fault protection. To operate the MCB the phase to neutral or earth insulation would need to have an resistance of just a few ohms and to operate the RCD an resistance of a few Kohms. Both these values are easily detectable with a multimeter and a deciscon on the safety of energizing can be made. Once the system is energized the safety of the system and its insulation is down to its design, maintenance and operation.

However if you are trying to ascertain the condition of the insulation then its resistance (measured with high DC voltage) may be helpful but interpreting the results will be difficult.

At higher system voltages (above 11kV) there is evidence that high DC test voltages cause damage to plastic insulated cables.

My view is use a decent multimeter to check your insulation.

Nick Clarke 320/12/2018 14:35:53
avatar
1607 forum posts
69 photos
Posted by Harry Wilkes on 19/12/2018 22:18:44:

Ah a megger 500v or a 1000v would break the will of any apprentice wink

H

A long time ago I used to drive for a firm that repaired fridges. One of the engineers used to get a kick out of asking an apprentice to hold a wire from a 'windy' megger which he then wound up and shocked the guy.

The apprentices learnt to keep away from him when he was in a 'joking' mood and recognised the megger as the source of his fun.

So what happens next - engineer buys a push button megger that they don't recognise and the cycle starts over!

Phil Whitley20/12/2018 14:49:45
avatar
1533 forum posts
147 photos

Michael Gilligan, yes, I noticed the lettering does seem odd on that megger, there was a mine version which was lower voltage (I have one) but they were black.I alsao have an older wooden one with "Royal Engineers" branded on it! Now we know there was also an aircraft, and a train model too! The needle position is random till the handle is wound, so could be anywhere on the scale. Sorry Simon Williams< I can't agree on robustnes, I have spent literally thousands on modern digital equipment, and have chucked it all out when it failed, and not replaced it, but I am still using an AVO8 and a megger from the early seventies! As to digital equipment being more accurate, don't believe it, check your specs and you will find that your test gear has a given accuracy at a fixed temperature only, because its electronics is sensitive to ambient changes, the AVOs and meggers use wirewound resistors which are unnafected by temperature, and anyway, the actual difference in claimed accuracy is so small as to be irrelevant, but the AVO will hold its accuracy over a much wider range of ambient temp. As to sensetivity, they all measure within the parameters of the selected scale. My problem with digital meters is that they are trying to measure values which are very often analogue! try watching a capacitor charge up with a digital meter, and looking for the little needle dips which indicate breakdowns at certain voltages, or going around tapping and rattling to find a loose connection or broken flex, ok, you can press hold and see a reading for a varying voltage, but on an analogue meter, you can watch it happen.

Ian Hewson20/12/2018 15:16:48
354 forum posts
33 photos

In the late 50s as an apprentice in the YEB meter test room it was a joke to get the lad to hold the wires of the 1000volt megger, but they could not understand why I could hold on as they wound.

So long as I held tightly I only got a tickle, laugh on them.

It was a different story with the later electronic version though, I could not hold that.

Harry Wilkes20/12/2018 15:42:20
avatar
1613 forum posts
72 photos
Posted by Nick Clarke 3 on 20/12/2018 14:35:53:
Posted by Harry Wilkes on 19/12/2018 22:18:44:

Ah a megger 500v or a 1000v would break the will of any apprentice wink

H

A long time ago I used to drive for a firm that repaired fridges. One of the engineers used to get a kick out of asking an apprentice to hold a wire from a 'windy' megger which he then wound up and shocked the guy.

The apprentices learnt to keep away from him when he was in a 'joking' mood and recognised the megger as the source of his fun.

So what happens next - engineer buys a push button megger that they don't recognise and the cycle starts over! wink

Harry Wilkes20/12/2018 15:48:21
avatar
1613 forum posts
72 photos
Posted by Ian Hewson on 20/12/2018 15:16:48:

In the late 50s as an apprentice in the YEB meter test room it was a joke to get the lad to hold the wires of the 1000volt megger, but they could not understand why I could hold on as they wound.

So long as I held tightly I only got a tickle, laugh on them.

It was a different story with the later electronic version though, I could not hold that.

The Forman at the very first place I worked could also hold the ends of the megger leads and his party trick to show us apprentices why he was the Forman was told hold one of the HT plug lead on a car in one hand and touch the end of the spark plug with the other hand whilst the engine was running smiley

H

Mike Poole20/12/2018 16:49:17
avatar
3676 forum posts
82 photos
Posted by Phil Whitley on 19/12/2018 21:16:29:

Mike Poole, an insulation tester is an essential tool when working on electric motors and electric heaters, which almost always fail "down to earth" They are used for final insulation tests on domestic installations, but that is about all. Absolutely essential tool for fault finding, but NOT on electronics!

Hi Phil, after over 40 years of electrical and electronic fault finding I stand by my comment on the need for an insulation tester, it spent most of its life in the equipment cupboard whereas my fluke multimeter spent most of its life in my pocket. As an apprentice motor failures were much more common but as with most things they have become much more reliable so that failure is now very rare, the last facilty I worked on probably has 10,000 motors installed and motor failure is very rare and determining failure rarely required an insulation tester or a bridge megger. As small motors are not economical to repair the precise nature of failure is not worth the time and effort to diagnose. I am not proposing that a multimeter does what an insulation tester is for, just that it is a more useful tool most of the time. My immersion heater didn’t need anything more than a multimeter to inform me the element was down to earth and open circuit but that was a particularly catastrophic mode of failure. Tracing the condensation in a socket box that was tripping the RCD very definitely did need an insulation tester, it’s always useful to have the right tool for the job but in my experience an insulation tester is rarely required but when it is it nothing else will do.

Mike

Michael Gilligan20/12/2018 17:01:34
avatar
23121 forum posts
1360 photos
Posted by Stuart Bridger on 20/12/2018 13:13:11:

Good Information here **LINK**

.

Thanks for that, Stuart yes

MichaelG.

Phil Whitley20/12/2018 20:18:58
avatar
1533 forum posts
147 photos

Yes Michael Giligan, good info, my wooden case model is the safety bridge megger, the second of the three pics. Mike Poole, not disagreeing with you, all you really need to tell a motor is gone is your nose! It may be that more modern installations than the ones I worked on in the sixties and seventies have better insulation, and fault to earth less, but a lot of what I did was in factories where the common denominator was wet! turkey and other food processing, and gravel pits, to mention a couple. earth leakages were very common. Today I have thank goodness retired from all that, and spend my time building, repairing and playing with machines and machine tools, much more rewarding, and a damn sight warmer and drier.

Edited By Phil Whitley on 20/12/2018 20:20:12

Simon Williams 320/12/2018 22:14:16
728 forum posts
90 photos

If I remember it right, the IEE Wiring reg's say the test source for testing insulation of low voltage equipment energised at 230 V AC must provide not less than 500 volts DC into a load of 1 megohm, other loads pro rata. Sorry gents but I don't think your windey Meggers do this.

I take Phil's point about liking analogue meters - I happen to prefer my digital, but it's horses for courses. However I can't let the assertion that a simple multimeter is sufficient to prove the equipment is safe to energise go unchallenged, the Regs say otherwise. By all means go looking for a fault with a DVM, but the testing to prove that it's safe to plug it in to the mains has to be done at an elevated voltage. Phil's right, all you often need to find there is a fault is a sense of smell!

The use of 5KV (flash testing) would only be warranted if the equipment was being re-designed or modified, or there was some reason to believe that a simple insulation test was insufficient. Or you've got a particularly difficult customer!

Mince Pies out for Santa + 4 days!

Phil Whitley21/12/2018 13:31:44
avatar
1533 forum posts
147 photos

That is what my windey megger produces Simon!

Robert Atkinson 223/12/2018 12:11:46
avatar
1891 forum posts
37 photos
Posted by Emgee on 20/12/2018 10:31:12:

I believe the Megger linked to by Michael is not working correctly, the meter is indicating a reading when not being cranked, without operating the handle the needle will be at 1 end of the scale, don't remember which end but I used that type of instrument for a few years before digital meters were available.

Emgee

This is not a fault. The meter movements in Meggers do not have a return spring and the pointer "floats" when the handle is not turned. The movment has two coils, a voltage coil that drives the pointer towards infinity and a current coil that drives it towards zero. It's a ratiometric instrument so the voltage does not have to be spot-on or zeroed like you do on an AVO.

Robert G8RPI.

not done it yet23/12/2018 12:36:10
7517 forum posts
20 photos
Posted by Harry Wilkes on 20/12/2018 15:48:21:
Posted by Ian Hewson on 20/12/2018 15:16:48:

In the late 50s as an apprentice in the YEB meter test room it was a joke to get the lad to hold the wires of the 1000volt megger, but they could not understand why I could hold on as they wound.

So long as I held tightly I only got a tickle, laugh on them.

It was a different story with the later electronic version though, I could not hold that.

The Forman at the very first place I worked could also hold the ends of the megger leads and his party trick to show us apprentices why he was the Forman was told hold one of the HT plug lead on a car in one hand and touch the end of the spark plug with the other hand whilst the engine was running smiley

H

1000 volts is chicken feed! We were often shocked by 6kV pulses. Now, the Van der Graff generator could easily make your hair stand on end.

We once had car seat covers that would cause a flash to earth across one’s shoe soles, after extracting oneself from the car, especially if one was wearing a synthetic shirt. Had to hold the car door, while getting out, to dissipate the static. They did not last long.

They don’t recommend playing with high voltages, these days, as it can reduce one’s favourable response in the case of ever needing to be defibrillated.

All Topics | Latest Posts

Please login to post a reply.

Magazine Locator

Want the latest issue of Model Engineer or Model Engineers' Workshop? Use our magazine locator links to find your nearest stockist!

Find Model Engineer & Model Engineers' Workshop

Sign up to our Newsletter

Sign up to our newsletter and get a free digital issue.

You can unsubscribe at anytime. View our privacy policy at www.mortons.co.uk/privacy

Latest Forum Posts
Support Our Partners
cowells
Sarik
MERIDIENNE EXHIBITIONS LTD
Subscription Offer

Latest "For Sale" Ads
Latest "Wanted" Ads
Get In Touch!

Do you want to contact the Model Engineer and Model Engineers' Workshop team?

You can contact us by phone, mail or email about the magazines including becoming a contributor, submitting reader's letters or making queries about articles. You can also get in touch about this website, advertising or other general issues.

Click THIS LINK for full contact details.

For subscription issues please see THIS LINK.

Digital Back Issues

Social Media online

'Like' us on Facebook
Follow us on Facebook

Follow us on Twitter
 Twitter Logo

Pin us on Pinterest

 

Donate

donate