Gerard O'Toole08/01/2020 09:46:23
159 forum posts
13 photos

I am a little confused about VFD's 3-phase motors and setting. Reading her on the forum and also on other websites is only adding to my confusion I am afraid. I should add that i have a mill working on a VFD but I am a little concerned about some of the settings. In particular I am confused about reference to dual voltage etc.

As I understand it, two measurements of voltage are often quoted , that for a single phase, eg. 230V and that value between any two phases which I understand, from various books etc. to be fixed at single phase voltage *√3 ( square root of 3) or 1.732 . So a single phase at 220V provides 380V between any two phases , 230V provides 400V and 240V will provide 415V between any two phases. These are the old European standard, the new EU standard and the UK standard respectively.

My VFD provides three phases at up to 240V. My understanding therefore is that as these phases are staggered at 120 degrees the same rule , i.e. if the single phase voltage is set at 240V then the between voltage is automatically 415V.

Perhaps my reasoning above is faulty. Please let me know, i have no experience or expertise in electrical matters and i might be misunderstanding the matter.

Now I see on this forum people say that you cannot power a 380V motor( or 400V or 415V) from a 240V VFD. But it seems to me that a 240V VFD exactly matches 415V across any two phases and should work correctly.

Now to my own setup. I was advised, based on the last paragraph, that i need to reduce the frequency proportionally to the voltage in order for the VFD to work. I.e. 400/240 = 1.71 so reduce the frequency 50Hz/1.71 = 29.2Hz. But this seems wrong to me as it is mixing up the single phase and between phase voltages.

I might add that I have made this adjustment, i.e. I have set the maximum frequency to 29Hz and the motor does work, although at a slower speed that it is designed for.

i wonder can someone please explain it all to me, preferable in simple terms I might understand.

Thanks for reading this far.

not done it yet08/01/2020 10:10:37
7517 forum posts
20 photos

The basics of a VFD is to vary the frequency - it’s in the name. The frequency determines the motor speed. If the motor is rated at 50Hz, it will run (at normal UK mains frequency) at its rated speed. Reducing the frequency simply changes the motor speed downwards.

Most VFDs also attempt to improve the torque at lower motor speeds as the power available would normally be related to the lower speed and torque is a function of rotational speed and power.

Set your frequency to whatever you require, within reason - remembering the design was for 50Hz. At lower speeds there will be less cooling which is likely to become more important when drawing the maximum power - the motor may overheat. At higher frequencies the motor will consume more power with its cooling fan and one must consider the physical constraints of the design - bearings, for instance, particularly the type of bearing. Ball and roller bearings will withstand higher speeds better than plain bearings.

Andrew Johnston08/01/2020 10:12:06
avatar
7061 forum posts
719 photos

The 240V output from the VFD is phase to phase, not phase to neutral.

You can run a 415V motor on a 240V output VFD, but the torque, and hence power, will be reduced in proportion. If the 415V motor is designed to run in star (most are) then by changing the arrangement to delta you can run from 240V without loss of power. Many motors have links in the connection box that make it easy to change from star to delta.

You don't need to change the frequency to make the VFD work. What your adviser may have been saying is that the output voltage needs to reduce as the frequency reduces. Otherwise you will overcurrent, and overheat, the motor. It's called a v/f curve, and is looked after by the VFD, not something the user needs to alter.

Andrew

daveb08/01/2020 10:20:37
631 forum posts
14 photos

Most of the low cost inverters output 220/240v 3 phase. A 415v 3 phase motor needs to have the windings connected in Delta to operate with these. If the windings are Star connected, they are effectively in series. There are 220v in/415v out inverters available but they are expensive, it is cheaper to reconfigure the motor windings.

John Olsen08/01/2020 10:20:53
1294 forum posts
108 photos
1 articles

Hi Gerard,

The usual VFD can only provide a maximum phase to phase voltage the same as the input AC Voltage. So it will run a delta connected 240 Volt motor at full power. The same motor if Star connected would run off the usual 415 V supply. This supply would provide 240 Volts between phase and neutral. Most motors come star connected for 415, and it is usual to have to restrap them to delta connected to run off a VFD, at least the type of VFD that is designed for 240V input. (There are VFD's that will take three phase input, these are not usually of much interest to amateurs since we usually don't have three phase power.)

There are VFDs that will take a 240V supply and provide the correct output for a 415 V star connected motor, probably by using a voltage doubling rectifier. I have no experience with these, but they have been on the market for a while, so presumably work OK.

Incidently you can run a motor on a lower voltage than the plate rating when necessary. I have a shaper with a Delta connected 460 Volt motor. This makes it impossible to lower the voltage rating, since if I star connected it the required Voltage would go up, to over 600 Volts. But it actually runs fine from a VFD , even the the voltage is effectively half what it should be. This limits the maximum power to about half the nameplate rating too, but since it is a three horsepower motor, half that will shift metal quite fast enough for most purpose.

So normal 3 phase is 240 phase to neutral, 415 phase to phase, but the three phase from a VFD is 240V phase to phase, and there is no neutral. (The neutral from the incoming mains is not a neutral for the output side.)

John

Michael Gilligan08/01/2020 10:27:53
avatar
23121 forum posts
1360 photos
Posted by Gerard O'Toole on 08/01/2020 09:46:23:

[…]

Now to my own setup. I was advised, based on the last paragraph, that i need to reduce the frequency proportionally to the voltage in order for the VFD to work. I.e. 400/240 = 1.71 so reduce the frequency 50Hz/1.71 = 29.2Hz. But this seems wrong to me as it is mixing up the single phase and between phase voltages.

I might add that I have made this adjustment, i.e. I have set the maximum frequency to 29Hz and the motor does work, although at a slower speed that it is designed for.

i wonder can someone please explain it all to me, preferable in simple terms I might understand.

Thanks for reading this far.

.

You will find a good explanation of the 29Hz linked on this previous thread:

**LINK**

https://www.model-engineer.co.uk/forums/postings.asp?th=97755

MichaelG.

Gerard O'Toole08/01/2020 10:40:00
159 forum posts
13 photos

Thanks for all the replies.

My motor is wired delta.

The VFD ( Bosch) states that the output is 3x 240V. I take that to mean three phases at 240V. By definition the between phase voltage is therefore 415V if each phase is 240V.

I will try reading up more on the difference. The manual states that the usual setting for maximum frequency is 50Hz. My concern is that I am being advised to set this to 29Hz.

I might try measuring the voltages with a meter and see what readings I get.

Thanks to you all for taking the time to read and reply, much appreciated

SillyOldDuffer08/01/2020 10:42:14
10668 forum posts
2415 photos

Don't overthink it, is my advice! The motor is the place to start.

Your description of 3-phase is good, but how it's wired up can vary.

Inside a three-phase motor are three windings. They can be connected in two different ways, 'star' and 'delta':

stardelta1.jpg

When a motor is wired 'delta', each winding is connected directly across a phase. Wired 'star' two windings are wired across each phase, ie twice the resistance.

So a motor wired 'delta' runs off 230V 3-phase, while exactly the same motor wired 'star' needs 440V 3-phase.

Investigate your motor plate and perhaps the terminal box. Most, but not all 3-phase motors, bring the windings out to terminals. If so, the motor can be easily wired to run on either 440v or 230. It is possible to get high-voltage VFDs, but yours is probably the low voltage type intended for running a delta wired motor. Unfortunately not all motors bring the windings out, in which case it's necessary to dig around inside the motor to find and open the star point marked 'N'.

If you connect a motor in star (440v) to a delta inverter (220v), the motor may well run, but only at much reduced power. Reconfigure the motor to delta, and all should be well.

Using the VFD to change frequency provides speed control, rather than power. RPM is related to the number of poles in the motor and supply frequency. If the VFD is set to 50Hz, it will spin the motor at normal rpm. Increasing the frequency (don't go mad!) will over-speed it, while decreasing frequency will slow it down. Don't run the motor at slow speed for a long time because it might over-heat. (The motors fitted to machines designed for VFD control are usually fitted with a separate full-speed cooling fan. Older machines, designed to run at constant speed, may rely on an impeller directly attached to the motor to keep cool; impellers don't work at low speeds.) But, to get everything working just set the VFD to 50Hz and don't worry about "i need to reduce the frequency proportionally to the voltage in order for the VFD to work. I.e. 400/240 = 1.71 so reduce the frequency 50Hz/1.71 = 29.2Hz."

There are several chaps smarter and more experienced in 3-phase than me on the forum: worth waiting to see what they say!

Dave

Edited By SillyOldDuffer on 08/01/2020 10:45:21

Andrew Johnston08/01/2020 11:26:20
avatar
7061 forum posts
719 photos
Posted by Michael Gilligan on 08/01/2020 10:27:53:

You will find a good explanation of the 29Hz linked on this previous thread:

**LINK**

I've re-read it and am still none the wiser as to what he's trying to say. sad

Andrew

Michael Gilligan08/01/2020 11:28:22
avatar
23121 forum posts
1360 photos
Posted by Andrew Johnston on 08/01/2020 11:26:20:
Posted by Michael Gilligan on 08/01/2020 10:27:53:

You will find a good explanation of the 29Hz linked on this previous thread:

**LINK**

I've re-read it and am still none the wiser as to what he's trying to say. sad

Andrew

.

Then evidently it is not a good explanation.

MichaelG.

John Haine08/01/2020 12:58:55
5563 forum posts
322 photos

Talking nonsense IMHO.

Gerard O'Toole08/01/2020 13:06:01
159 forum posts
13 photos

Thanks everyone.

I did manage to measure the between voltage and it measured 220V not 380V

I wil leave everything alone , as the motor is working fine and I don't run the mill for long periods of time. The motor never gets hot, at most a comfortable warm after a good few hours.

The motor is definitely wired delta, I did that before fitting the VFD. ( Originally it could be switched from Star to Delta)

It is the original German motor fitted to a Deckel FP1 mill from 1950's I think.

thanks again for all thetrouble you have all taken to explain things to me

norm norton08/01/2020 14:20:39
202 forum posts
10 photos

I thought I had a limited understanding of this, but now I am confused.

If a residential road is fed with three separate phases of 240v, then each house takes a feed from one of those phases and has single phase 240v. If an industrial premise takes all three phases then (I assumed) it has an available feed of 415v (or 380v or whatever) 3 phase. Correct or wrong?

Or are there transformers on the old poles to drop 415v lines down to 240v domestic?

Now if you take one of the 250v phases, and put it through a VFD box, is the output actually three separate 250v sine waves each shifted by one-third of a cycle. If so, why is this phase adjusted supply not producing 415/380v 3 phase?

I need to see the actual AC diagrams perhaps of the two 3 phase scenarios I have described. I think Gerard was asking the same question.

Norm

Martin Connelly08/01/2020 14:41:47
avatar
2549 forum posts
235 photos

3 phase voltages csn be given as phase to phase or phase to neutral. UK mains is 230v phase to neutral and 398v phase to phase. The output of a vfd connected to 230v phase to neutral is 230v phase to phase. As there is not usually a neutral from the vfd they do not give the phase to neutral voltage but it would be 133v if it was measurable. If you really want to measure it connect it to a motor wired as star and measure the star point to phase voltage. It should be 133v. Voltages are approximate.

Martin C

Gerard O'Toole08/01/2020 14:42:25
159 forum posts
13 photos
Posted by norm norton on 08/01/2020 14:20:39:

I thought I had a limited understanding of this, but now I am confused.

If a residential road is fed with three separate phases of 240v, then each house takes a feed from one of those phases and has single phase 240v. If an industrial premise takes all three phases then (I assumed) it has an available feed of 415v (or 380v or whatever) 3 phase. Correct or wrong?

Or are there transformers on the old poles to drop 415v lines down to 240v domestic?

Now if you take one of the 250v phases, and put it through a VFD box, is the output actually three separate 250v sine waves each shifted by one-third of a cycle. If so, why is this phase adjusted supply not producing 415/380v 3 phase?

I need to see the actual AC diagrams perhaps of the two 3 phase scenarios I have described. I think Gerard was asking the same question.

Norm

Yes Norm

I was asking the same question you asked. I too understood 3 separate phases at 240 V but apparently not

gerard

Andrew Johnston08/01/2020 14:50:37
avatar
7061 forum posts
719 photos

In the UK electricity distribution is 3-phase and earth, no neutral. At the local sub-station transformer the primary is wired delta and the secondary is wired star. So the secondary has a 'neutral' point. This is grounded at the sub-station. The cable running down the road has three phases, the neutral (aka earth at the sub-station) and a protective earth. The sub-station transformer is arranged so that the voltage from any phase to 'neutral' is 240V, while the voltage phase to phase is 415V, ie, times the square root of 3. So a property on single phase will have an earth, neutral and live (from one of the three phases). An industrial property will have the three phases and earth. A neutral may also be supplied for any single phase loads. That's what I have at home; three phases (which are fused) a neutral (which isn't fused) and an earth. I run the house off one phase and the neutral whereas the workshop runs from 3-phase. The neutral also runs around the workshop, but none of my machine tools use it. They just take 3-phases and earth. Remember that all quoted voltages are rms aka root-mean-square.

I feel the need to go and machine a large lump of steel! If no-one has explained why a 240V in VFD cannot normally produce a 415V output by the time get back then I'll explain.

Andrew

Andrew Johnston08/01/2020 14:54:08
avatar
7061 forum posts
719 photos

Should have mentioned that the reason the phase to phase voltages are higher is because the phases are time shifted with respect to each other by 120 degrees.

Andrew

norm norton08/01/2020 15:52:14
202 forum posts
10 photos

Ahh.. Thank you Martin and Andrew - got that.

So I (and perhaps two others in the world) have been misunderstanding the output from the workshop VFDs that we use. It is 240v phase-to-phase, and if there was a neutral it would be about 133v on each phase to neutral.

I guess the rules of physics say that one cannot phase shift 240v AC by 120 degrees and again by another 120 degrees, otherwise we would get 415v quite easily.

Norm

John Haine08/01/2020 15:58:09
5563 forum posts
322 photos

To save Andrew doing it. It a simple VFD the mains is full-wave rectified and charges a big capacitor up to 230 x sqrt2 = 325 V. It then has 3 high-voltage push-pull output stages run off this voltage to drive the 3 outputs. Each one is driven by a variable mark/space PWM signal at perhaps a few kHz. At 50:50 m/s the effective average output of one of these is 162.5 V, and it can be varied down to 0 V and up to 325 V. In effect this is +/- 162.5 V relative to an average of zero. If you vary the m/s ratio in a sinusoidal manner with time at 50 Hz you can generate what appears to a motor as a 50 Hz sine wave with a peak voltage of 162.5 V.

Now there are 3 output stages and they are driven to generate waveforms 120 degrees out of phase. If you connect a motor winding between two of these outputs it sees a voltage of 162.5 x sqrt(3) = 281 V peak or 199 V rms. This is not too much lower than the winding would see if it was connected between a line and neutral of a standard 3 phase supply so it will run with nearly the same current and power as normal.

You can also play games where the waveform is not sinusoidal but the peak is "flatter", which will increase the rms voltage and current to compensate for the lower peak voltage. There's nothing particularly sacrosanct about sine waves.

John Haine08/01/2020 16:03:06
5563 forum posts
322 photos
Posted by norm norton on 08/01/2020 15:52:14:

Ahh.. Thank you Martin and Andrew - got that.

So I (and perhaps two others in the world) have been misunderstanding the output from the workshop VFDs that we use. It is 240v phase-to-phase, and if there was a neutral it would be about 133v on each phase to neutral.

I guess the rules of physics say that one cannot phase shift 240v AC by 120 degrees and again by another 120 degrees, otherwise we would get 415v quite easily.

Norm

You can shift it using a resistor-capacitor circuit, but inefficiently (because of the resistors). To get high efficiency you need at least two power feeds with a phase difference. There's something for example called a Scott transformer that will generate two phases at 90 degrees given a 3 phase supply, or vice-versa.

All Topics | Latest Posts

Please login to post a reply.

Magazine Locator

Want the latest issue of Model Engineer or Model Engineers' Workshop? Use our magazine locator links to find your nearest stockist!

Find Model Engineer & Model Engineers' Workshop

Sign up to our Newsletter

Sign up to our newsletter and get a free digital issue.

You can unsubscribe at anytime. View our privacy policy at www.mortons.co.uk/privacy

Latest Forum Posts
Support Our Partners
cowells
Sarik
MERIDIENNE EXHIBITIONS LTD
Subscription Offer

Latest "For Sale" Ads
Latest "Wanted" Ads
Get In Touch!

Do you want to contact the Model Engineer and Model Engineers' Workshop team?

You can contact us by phone, mail or email about the magazines including becoming a contributor, submitting reader's letters or making queries about articles. You can also get in touch about this website, advertising or other general issues.

Click THIS LINK for full contact details.

For subscription issues please see THIS LINK.

Digital Back Issues

Social Media online

'Like' us on Facebook
Follow us on Facebook

Follow us on Twitter
 Twitter Logo

Pin us on Pinterest

 

Donate

donate