gerry madden31/03/2017 13:23:55
331 forum posts
156 photos

I have just go a fractional HP motor 250V single phase. In its top mounted box it has a start and run capacitor. I assumed this could be connected directly to the mains supply but in browsing a Clark catalogue it suggest they motors should be connected via a DOL. Can anyone advise me here as to the purpose of DOL and why I might or might not need one ?

john fletcher 131/03/2017 13:45:36
893 forum posts

Clark are right. The idea of a DOL is as follows,should you be working on say your lathe and the there is a power OUT for whatever reason, and you could just be making some adjustment to the chuck and then the power is then restored you could be seriously injured. The DOL would protect you, as you would need to press the GREEN on button to restore the power. Also within the "box" there are overloads as well.John

Emgee31/03/2017 14:02:15
2610 forum posts
312 photos

For those who may be wondering, the DOL mentioned is a Direct Online Starter, this will as John states disconnect the motor connection when power is lost and also provide motor overload protection so it is important to set the overload device to the same as the full load current amps (FLC) stated on the motor plate.

Emgee

gerry madden31/03/2017 14:08:41
331 forum posts
156 photos

Thank you all for that clear guidance which I will follow. What a great forum this is !

Speedy Builder531/03/2017 14:59:17
2878 forum posts
248 photos

I have a Boxford lathe. My emergency STOP switch breaks on power out. Next is the on/off switch that breaks if any of the cupboard doors are opened (Screw cut gears, motor speed, backgear select etc), then I have a rotary switch for forward, off and reverse.
BobH

Neil Wyatt31/03/2017 16:05:58
avatar
19226 forum posts
749 photos
86 articles

If you search for NVR ('no voltage release' switch you might find something cheaper that does the same job.

Several of our advertisers sell a little unit combining a start and stop switch with an NVR and a hinged red emergency STOP button as fitted to many types of machine.

Neil

MW31/03/2017 16:22:21
avatar
2052 forum posts
56 photos

I don't want to hijack the original poster but is there a way to combine an emergency stop to a lathe controlled by an inverter/electronic pendant? I'm just saying because I don't have one and ideally I should.

The stop button is a little obscure for when my hand might be trappedindecision

Michael W

Keith Long31/03/2017 17:25:35
883 forum posts
11 photos

Gerry - a word of caution, the DOL that Clarke sell is NOT an NVR switch. It is mechanically locked on so that if the mains fails the contacts actually stay in the made position with the result that the motor WILL restart when the mains comes back on ie it's no different in function to an ordinary on/off switch apart from having the over-current device built in. If you want a starter that gives you the NVR protection, look in the Toolstation or Screwfix catalogues. Machine Mart's reason for stating that the motor must be connected through a DOL starter is to have it connected to the mains through an over current protection device, to save the motor being run at overload an burning out. Both Toolstation and Screwfix sell the over-current protection devices separately and you choose the one that suits your motor.

Les Jones 131/03/2017 17:54:43
2292 forum posts
159 photos

Mitchael-w,
You can probably connect an emergency stop button in series with the stop button on the pendant. This is assuming that the stop button in the pendant is an normally closed contact type. To be sure you would need to provide w wiring diagram of the pendant and how it is wired to the inverter. Also a copy of the page of the inverter manu manual that shows the control input connections. would be helpful.

Les.

MW31/03/2017 17:57:10
avatar
2052 forum posts
56 photos
Posted by Les Jones 1 on 31/03/2017 17:54:43:

Mitchael-w,
You can probably connect an emergency stop button in series with the stop button on the pendant. This is assuming that the stop button in the pendant is an normally closed contact type. To be sure you would need to provide w wiring diagram of the pendant and how it is wired to the inverter. Also a copy of the page of the inverter manu manual that shows the control input connections. would be helpful.

Les.

Thanks Les, it'll take a little time but i'll go and see what it looks like.

Michael W

Neil Wyatt31/03/2017 18:19:47
avatar
19226 forum posts
749 photos
86 articles

Michael, this link explains how I did just that.

www.model-engineer.co.uk/news/article/3-phase-conversion-and-other-alternative-methods-of-powering-a-mini-lathe/18752

Neil

MW31/03/2017 19:00:45
avatar
2052 forum posts
56 photos

Ah whoa, thank you!

I have a pendant, inverter and motor that's very similar to yours,

I bought a TEC motor which was 1/2HP, I did okay with it for a long time til i needed to turn a long length of EN3 BMS square bar for a T bolt (to fix a toolpost to) and ran table down the bed of my Clarke using the gear train, however, it stalled half way through the cut, as it wasn't able to handle both the spindle and the gear train at the same time (thankfully, it stopped, so it didn't kill the motor and i was able to re-use it on my mill when the original DC motor packed up).

So i upgraded to a 1HP motor, not wanting to go overkill but at the same time, solve the problem. I've operated this one ever since and it's been able to handle anything I've thrown at it.

I was going to say that i would've assumed that one needed to place the emergency in series with the single phase lead to the inverter, as this would be the source of power, breaking that part of the circuit cuts everything else instantly. I didn't think that it would be able to run this function through the inverter electronically?

Although i suppose breaking any part of the circuit to the control would create an incomplete path causing it to stop?

Michael W

 

Edited By Michael-w on 31/03/2017 19:04:01

not done it yet31/03/2017 19:09:44
7517 forum posts
20 photos

A good article on a real life fix (several times over). Off topic really, but my immediate thought was why he made a new counter shaft - I would have used the dead motor and added a pulley somehow.

MW31/03/2017 19:19:35
avatar
2052 forum posts
56 photos

img.jpg

That is what my inverter terminals look like, so it's a bit different to how they name the terminals on the jaguar.

Les Jones 131/03/2017 19:36:10
2292 forum posts
159 photos

Hi Mitchael-w,
We now need to know the functions that are configured on the multi function inputs S1 to S4 and S5/Y. We also need the schematic of the pendant so we know which switches / buttons are connected to each of the control inputs.

Les.

MW31/03/2017 19:36:36
avatar
2052 forum posts
56 photos

I've had a look through the manual of the IMO idrive 2 inverter, but i can't find any reference to a facility to emergency stop on it, i'm doubtful as to whether my particular model is able to do this unfortunately.

Guess that's what you pay for on an jaguar.

Michael W

MW31/03/2017 19:48:01
avatar
2052 forum posts
56 photos

Ok i'll see what i can do Les, however, i don't think i ever got a circuitry diagram nor can i find one online however, i can open the thing up and see if i can make sense of the spaghetti inside, this is the best thing i could find on "what does what" for the pendant in relation to the inverter.

img2.jpg

John Rudd31/03/2017 21:35:33
1479 forum posts
1 photos

I would never rely on the software of any piece of equipment when it comes to stopping it dead in an emergency....

In an industrial environment, an E stop is exactly that....it is hard wired doesnt rely on software code...why would you want to compromise on safety?

Remove the power......

I have three lathes and two mills, all of their E stops kill the power....

Is there a better solution?

Edited By John Rudd on 31/03/2017 21:38:20

MW31/03/2017 21:41:44
avatar
2052 forum posts
56 photos
Posted by John Rudd on 31/03/2017 21:35:33:

I would never rely on the software of any piece of equipment when it comes to stopping it dead in an emergency....

In an industrial environment, an E stop is exactly that....it is hard wired doesnt rely on software code...why would you want to compromise on safety?

Remove the power......

Edited By John Rudd on 31/03/2017 21:36:34

it isn't exactly software but more like an electronic input rather than a raw electrical one, I agree, my first instinct would be isolating the power supply, i'm going to upload some more pictures of my pendant, to weed out where all these wires are going to see if the electrical gurus can take a crack at it first. They might know something I don't!

I just took so long because my computer seemed to have a miniature fit over transferring the photos (curse you, windows app; TWINUI) For now i'm going to have to review everything thru paint.

Michael W

John Rudd31/03/2017 21:52:14
1479 forum posts
1 photos
Posted by Michael-w on 31/03/2017 21:41:44:

it isn't exactly software but more like an electronic input rather than a raw electrical one.....

Michael W

The control terminals of an inverter are the external interface that is controlled by software....thats my point...

Remove the power, the inverter/motor is dead....

All Topics | Latest Posts

Please login to post a reply.

Magazine Locator

Want the latest issue of Model Engineer or Model Engineers' Workshop? Use our magazine locator links to find your nearest stockist!

Find Model Engineer & Model Engineers' Workshop

Sign up to our Newsletter

Sign up to our newsletter and get a free digital issue.

You can unsubscribe at anytime. View our privacy policy at www.mortons.co.uk/privacy

Latest Forum Posts
Support Our Partners
cowells
Sarik
MERIDIENNE EXHIBITIONS LTD
Subscription Offer

Latest "For Sale" Ads
Latest "Wanted" Ads
Get In Touch!

Do you want to contact the Model Engineer and Model Engineers' Workshop team?

You can contact us by phone, mail or email about the magazines including becoming a contributor, submitting reader's letters or making queries about articles. You can also get in touch about this website, advertising or other general issues.

Click THIS LINK for full contact details.

For subscription issues please see THIS LINK.

Digital Back Issues

Social Media online

'Like' us on Facebook
Follow us on Facebook

Follow us on Twitter
 Twitter Logo

Pin us on Pinterest

 

Donate

donate