An inverter for a 3 phase Myford plus 3 Phase suds pump

All Topics | Latest Posts

Search for:  in Thread Title in  
Andrew Tinsley09/10/2012 16:43:34
1817 forum posts
2 photos

Hello all, Thanks for the response to my query abourt a reliable inverter for my 3 phase powered Myford.

However I completely forgot about the small 3 phase powered suds pump (Standard Myford pump and resevoir). I was not looking at the inverter as a means of frequency conversion. So my query is can I run the suds pump motor from the same inverter powering the lathe motor?

Regards,

Andrew.

Speedy Builder509/10/2012 18:55:06
2878 forum posts
248 photos

You could run the pump off 240volt if the pump is dual voltage (440/240). Use the 240 volt legs.Put a capacitor across 2 of the legs, and live / netral from one end of the capacitor and the spare leg

I got this information from J.Olsen:-

I don't have a method for calculating a precise value for the capacitor, but a rough calculation suggests that something of the order of 33 microfarads would be about right for a starting point...it may be happy with a bit less or it may need a bit more. It must be rated for 240 volts AC continuous operation. Some motor start capacitors are not rated continuously since they have a switch in the motor.
Ok, last thing, remember to be careful, especially while you are trying things out!
KWIL09/10/2012 19:13:50
3681 forum posts
70 photos

There is no reason why you should not run the suds 3 phase pump in parallel with the spindle motor, the power demanded is low compared with the spindle motor and you only need the suds when you are running the machine anyway. I have this available on my lathe and mill.

Andrew Tinsley10/10/2012 10:28:05
1817 forum posts
2 photos

Thanks for the replies. I wasn't sure if there was some form of feedback to the inverter and trying to run two motors would confuse the feedback (if any?). Even if ther were feedback, I would assume that the demands of a small suds pump would not make much difference. However I wasn't sure so safer to ask!

Just another query, both 3 phase motors have 4 wires coming out of the flexible conduit. The 3 red phases and earth. So I assume the motors are connected in delta (i.e. no neutral connection). I have not yet checked at the motor connections themselves to see if they can be connected in star or delta. Assuming that the connections can only be made in delta (big if!). Can you use an inverter in delta, or do you have to be able to connect in star for inverter use? My 3 phase electrical theory was last use 40 years ago and is to say the least, a little rusty!

Regards,

Andrew.

Chris Hembry10/10/2012 10:53:33
52 forum posts
1 photos

Hesitated to reply on this one as it is not recommended to have switchgear between the motor and the inverter. However, if you always switch the suds on or off while the main motor is stopped you will have no problems whatsoever. The inverter will not see that there are two motors connected to it.

I have a M280 CNC where the coolant can be computer switched via a 3ph contactor. Switching on causes no problems but switching off occasionally causes the inverter to trip out and show an overcurrent error. I guess I could alter the parameters to allow the fault but since switching the coolant off usually precedes switching off the spindle, no real problem occurs.

You can use an inverter in star or delta but if the motor is not changed over it will be running on 240V per coil instead of 415V and you will thus lose a large amount of power.

Regards,

Chris

Martin Kyte10/10/2012 12:19:33
avatar
3445 forum posts
62 photos

You can connect 3phase motors in Star or Delta without bringing the star point out of the motor. The system is balanced and does not need a neutral connection.

You have the suds pump perminantly running and add a bypass to the pipework so that when fully open you get no sudsThis would act conveniently as a flow adjustment.

If you are using variable frequency drive to control lathe speed you will slow your suds down too.

Andrew Tinsley11/10/2012 11:14:12
1817 forum posts
2 photos

Thanks Chris and Martin,

Not all that au fait with inverters, but I assume that they rectify and then chop the DC volts to get a sine wave. I realise it is more complicated than that! However it will do for a start. If I am vaguely correct, then the 3 phase supply will be 240 volts per phase? So do I need the motor connected in star or delta. I seem to remember that a star configuration will be required if it is simply 240 volts per phase. However it is a long time ago since I did any 3 phase stuff. I don't even know where my old textbooks are!

Regards,

Andrew.

Chris Hembry11/10/2012 14:03:08
52 forum posts
1 photos

Martin,

You need to connect the motor in delta to give full power on 240V.

Between any two phases there will be only one winding so it will see the full 240V. In star you have two windings between any two phases so each will see half the supply voltage.

Regards,

Chris

Martin Kyte11/10/2012 14:55:34
avatar
3445 forum posts
62 photos

Yes I know Chris, my remark was about the Star point and not needing neutral connections which sometimes confuses people.

"You can connect 3phase motors in Star or Delta without bringing the star point out of the motor. The system is balanced and does not need a neutral connection."

However you are perfectly correct that the duel voltage motor needs connecting in Delta. I could be pedantic and say that each coil would see 1/root3 or 138.56Volts but I won't.

Regards Martin

Chris Hembry11/10/2012 16:57:39
52 forum posts
1 photos

Sorry Martin, reply was directed at Andrew.

Chris

john fletcher 111/10/2012 17:20:47
893 forum posts

Regarding Cap size for the colant pump its more likely 4 Micro farads. I have done this for my friends but cannot remeber the exact value. When the motor sound right and not getting hot then you have the best value, so its a bit hit and miss. Connect Caps in parallel to increase value, in series opposite.Ex fluorescent lights are good. Old 5 foots fluorescents were fitted with 7.5 micro farad. Ted

Andrew Tinsley13/10/2012 14:19:53
1817 forum posts
2 photos

Thanks Everyone for all your help. I now need to get stuck in and get my Myford on the road!

Regards,

Andrew.

All Topics | Latest Posts

Please login to post a reply.

Magazine Locator

Want the latest issue of Model Engineer or Model Engineers' Workshop? Use our magazine locator links to find your nearest stockist!

Find Model Engineer & Model Engineers' Workshop

Sign up to our Newsletter

Sign up to our newsletter and get a free digital issue.

You can unsubscribe at anytime. View our privacy policy at www.mortons.co.uk/privacy

Latest Forum Posts
Support Our Partners
cowells
Sarik
MERIDIENNE EXHIBITIONS LTD
Subscription Offer

Latest "For Sale" Ads
Latest "Wanted" Ads
Get In Touch!

Do you want to contact the Model Engineer and Model Engineers' Workshop team?

You can contact us by phone, mail or email about the magazines including becoming a contributor, submitting reader's letters or making queries about articles. You can also get in touch about this website, advertising or other general issues.

Click THIS LINK for full contact details.

For subscription issues please see THIS LINK.

Digital Back Issues

Social Media online

'Like' us on Facebook
Follow us on Facebook

Follow us on Twitter
 Twitter Logo

Pin us on Pinterest

 

Donate

donate