Martin Newbold | 21/08/2017 17:41:19 |
415 forum posts 240 photos | Does anyone one have an instruction sheet for GEC size D90S No LA303 1.5 KW , please? |
john fletcher 1 | 21/08/2017 18:00:02 |
893 forum posts | Is that a electric motor ? John |
Mike Poole | 21/08/2017 18:08:19 |
![]() 3676 forum posts 82 photos | I would be surprised if that turns up. Do you want to know anything in particular about this motor? Mike |
Martin Newbold | 21/08/2017 18:17:31 |
415 forum posts 240 photos | What am trying to find out is what is A B and C as in Data sheet for type A reversing switch for Dewhurst SDR52 switch are connecting to in motor but have no data sheet for motor.
|
Mike Poole | 21/08/2017 18:24:29 |
![]() 3676 forum posts 82 photos | Do you have a picture of your motor terminal block and the plate with the motor details? Mike |
Martin Newbold | 21/08/2017 18:34:14 |
415 forum posts 240 photos | Thanks Mike yes been having some problems retrieving it from my network printer the location of the memory cards seems to change weekly I am sure this is siple but just dont want to blow up a second motor, As you see it has V1 V2 and V2 have been told its connected in DELTA
Motor plate is below
Edited By Martin Newbold on 21/08/2017 18:43:04 |
Mike Poole | 21/08/2017 18:36:55 |
![]() 3676 forum posts 82 photos | The diagram you have posted is for a 3 phase motor wired in star, is the motor you have an unknown quantity or have you had it it in service? Some 3 phase motors have just 3 terminals and are usually wired in star for running on 415v 3 phase. One of the common options is for a six terminal block with links to wire the motor in star or delta, refer to the info plate to decide if you should be in star or delta. Mike |
not done it yet | 21/08/2017 18:40:51 |
7517 forum posts 20 photos | A, B and C are likely marked as U, V and W on your motor, if it is simply a 3 phase motor. The three phase connections should all be equivalent, so not important which connection goes to which terminal. Direction of motor can be reversed by changing over any pair of motor connections. Edit:OK, V1, V2 and V3 for yours. Unimportant difference. Edited By not done it yet on 21/08/2017 18:45:03 |
Mike Poole | 21/08/2017 18:50:08 |
![]() 3676 forum posts 82 photos | That is wired in star connection, the three studs that are not linked can be regarded as A,B,C so connect three wires as shown in the diagram, it will not matter what you call a b or c on the terminal block, you can swap any two of your three wires to change the direction if you have a preference which position the switch is in for forward. The rating plate says the motor is made for 415v in star so if you are running from 415v 3phase leave it as it is. Mike Edited for brain fade on star delta connection Edited By Mike Poole on 21/08/2017 18:58:24 |
Martin Newbold | 21/08/2017 18:59:58 |
415 forum posts 240 photos | I just looked at the connections again as gave you duff information in need 415 volt I have connected as default W2--------U2---------V2 U1 W1 V1
Edited By Martin Newbold on 21/08/2017 19:02:57 Edited By Martin Newbold on 21/08/2017 19:04:51 |
Brian Oldford | 21/08/2017 19:03:10 |
![]() 686 forum posts 18 photos | Unlike my Brooks motor this one is dead easy to reconfigure to delta if you want to use it with a VFD. |
Mike Poole | 21/08/2017 19:07:29 |
![]() 3676 forum posts 82 photos | The three terminals linked together make the star point and the plate says this connection is fo 380-415v, the delta connection is made by removing the links from the star connection and replacing them in a vertical connection as your picture shows them, there should be three separate links in the delta connection and the star connection only requires two so the spare is usually doubled up on one of the star links. Mike |
Martin Newbold | 21/08/2017 19:08:33 |
415 forum posts 240 photos | Brian is this configured in star . If i understand you correct I need toconnect a b & c to U1 W1 V1 does it matter in which order? Edited By Martin Newbold on 21/08/2017 19:13:07 |
Mike Poole | 21/08/2017 19:15:31 |
![]() 3676 forum posts 82 photos | If you call U1,W1,V1. A, B, C then you should be good to go. If your supply is 415v then leave the motor in star as shown in you picture, do not connect this motor in delta to run on 415v. As Brian says, if you wish to use this with a single phase input inverter then it is simple to change delta. Mike |
Mike Poole | 21/08/2017 19:18:03 |
![]() 3676 forum posts 82 photos | It will not matter which order you connect ABC and you can swap any two to change the direction if you want to. Mike |
Martin Newbold | 21/08/2017 19:37:33 |
415 forum posts 240 photos | Thanks for your help its seems to be working. So have left it alone till i get some more paint. |
not done it yet | 21/08/2017 20:04:12 |
7517 forum posts 20 photos | There seems to be some misunderstanding about VFDs and three phase motors here - I think. A 415 three phase motor can be run off a 230V input three phase inverter. These are different to a 230V output type of three phase inverter as the output will be 415V. Different price too! I have both. An expensive 415 output runs a motor wound star and likely difficult to convert to delta. The 230V output inverters are the cheaper and more common variety. Better to break the star point, rewire in delta and use the cheaper alternative, if possible. |
Martin Newbold | 22/08/2017 09:29:34 |
415 forum posts 240 photos | Hi 'not done it yet' I dont have a VFD As lost confidence with these devices and wanted something that would work , Its running of this MotoRun Phase converter through a Dewhurst Reversing switch currently. You need to check the engine plate for what the motor will run they are all differant. Its quite a challange. Having built a gear box I can alter speed here by changing pulleys and didnt think the VFD I had used gave power though out the range of speeds. Thanks
|
Please login to post a reply.
Want the latest issue of Model Engineer or Model Engineers' Workshop? Use our magazine locator links to find your nearest stockist!
Sign up to our newsletter and get a free digital issue.
You can unsubscribe at anytime. View our privacy policy at www.mortons.co.uk/privacy
You can contact us by phone, mail or email about the magazines including becoming a contributor, submitting reader's letters or making queries about articles. You can also get in touch about this website, advertising or other general issues.
Click THIS LINK for full contact details.
For subscription issues please see THIS LINK.