By continuing to use this site, you agree to our use of cookies. Find out more
Forum sponsored by:
Forum sponsored by Forum House Ad Zone

The 3 phase question

Seeking advice

All Topics | Latest Posts

Search for:  in Thread Title in  
Jon16/07/2012 19:00:26
1001 forum posts
49 photos

For ref OP has a 1.3kw dual speed motor, geared head! so would need 3ph 400V inverter plus extras. Or change to a dual voltage motor approx £150 with a 220V 3ph inverter and many hours of planning and rewiring. Likewise would have to do twice with the Tom Senior but easier, absolute minimum £600.

Your not with me Kwil, using my 4kw 3ph 440v inverter its impossible to do much with the machine assuming it started up. In other words putting a minor cut on more than 20 thou sees spindle slow dramatically, inverter continually ramping up trying to rectify. Put a little more cut on 40 thou and it wont rectify, spindle speed drops and would stay there or stop. The 4kw inverter is not man enough to power a 2.2kw motor. I have exactly same symptoms with a Transwave 5kw rotary convertor and sounds like relays/contactors clattering with serious groaning. Again this is with menial cuts in 6082.

Chalk and cheese a direct swap for a 7.5kw inverter of same make saw no slowing down putting a 3/8" cut on, 3/4" diameter reduction on power feed, thats the difference.

John Olsen16/07/2012 22:45:53
1294 forum posts
108 photos
1 articles

It seems to me Jon that there is something wrong with that particular inverter. 4kW is about 5hp, you should be able to get a decent cut with that before it starts to struggle. Are you sure it is not set up to current limit at too low a value? What should happen is that the setup will work fine and maintain speed until you reach the current limit. You don't need to oversize the inverter to allow for any starting surge, since there is none. The inverter soft starts the motor by ramping up the voltage and frequency. So this eliminates things like lights flickering and TV's going funny when you start a big motor

I've tried a bit of a strange one, a 0.75kW 230 Volt inverter running a 440 Volt 3 hp motor. So the motor is running at half the nominal voltage. It starts fine and runs well, although naturally you cannot get more than .75 kW, eg about 1 hp out of it, the inverter would current limit if you tried to get any more. It is on a big shaper, and the machine will take a good size cut without any signs of distress. Not an ideal way of working, but since the motor is a Delta connected 440V job it is kind of hard to run from single phase. I haven't found a local (NZ) source of inverters with 230 Volts in and 440 Volts out, although they do exist.

John

Steve Garnett16/07/2012 23:02:48
837 forum posts
27 photos
Posted by John Olsen on 16/07/2012 22:45:53:

I've tried a bit of a strange one, a 0.75kW 230 Volt inverter running a 440 Volt 3 hp motor. So the motor is running at half the nominal voltage. It starts fine and runs well, although naturally you cannot get more than .75 kW, eg about 1 hp out of it, the inverter would current limit if you tried to get any more. It is on a big shaper, and the machine will take a good size cut without any signs of distress. Not an ideal way of working, but since the motor is a Delta connected 440V job it is kind of hard to run from single phase. I haven't found a local (NZ) source of inverters with 230 Volts in and 440 Volts out, although they do exist.

My bro-in-law tried an interesting experiment, which he said worked quite well. He purchased a hefty auto-transformer for his single-phase 240v which gave him 415v, and fed this to a 415-415 3-phase inverter, to all three inputs. This works, because it's all converted to DC anyway; if you can feed enough current to the three inputs, it simply doesn't matter about the phase of it.

I'm absolutely not recommending this to the faint of heart though, and will disclaim any responsibility for it as an idea! Should work fine, although as far as I'm aware you can purchase a 240-415v inverter anyway for about the same price as his 415-415 and the autotransformer. So interesting, but almost certainly pointless, I'd guess.

John Haine17/07/2012 09:32:56
5563 forum posts
322 photos

Steve, an interesting idea. Actually, you don't even need to feed all the phase inputs, just one, though at high powers the input diodes might suffer.

Steve Garnett17/07/2012 10:06:22
837 forum posts
27 photos
Posted by John Haine on 17/07/2012 09:32:56:

Actually, you don't even need to feed all the phase inputs, just one, though at high powers the input diodes might suffer.

That's why he did it that way. The reason for this device was that it was intended for use with a Hardinge capstan lathe, and these are dual-speed star-wired. I pointed out that switching the motor speed from high to low under power wasn't going to be a very clever idea - it's a good way to blow an inverter apart in a fraction of a second; this sequence of operations needs to be prevented by a safety switch. Dunno what the current status of this project is, though - he's currently working on a less ambitious project completely rebuilding a flat.

Jon17/07/2012 14:22:29
1001 forum posts
49 photos
Posted by John Olsen on 16/07/2012 22:45:53:

It seems to me Jon that there is something wrong with that particular inverter. 4kW is about 5hp, you should be able to get a decent cut with that before it starts to struggle. Are you sure it is not set up to current limit at too low a value? What should happen is that the setup will work fine and maintain speed until you reach the current limit. You don't need to oversize the inverter to allow for any starting surge, since there is none. The inverter soft starts the motor by ramping up the voltage and frequency.

Its not just that smaller 4kw inverter its also a 4kw Transwave rotary convertor. Symptoms are both the same.

No soft start, its plug and play just the way 3ph 400V+ would be installed to premises.

Its not only powering the motor up but also have to bear in mind the additional load from belts/pulleys, gearbox and shear weight of chuck fitted at time. Even my current 7.5kw inverter with a small 5 1/4" chuck set on 2500rpm takes at least 10 to 15 secs, on 540 rpm its instant, bang.

I do have something not right some where this morning blew another 3ph coolant pump, its only been on 6 weeks. Since pump was running whilst attempting to start and stop lathe 70 times this morning, reckon it could be surge.

Duly ordered a single phase pump to get me out of the proverbial, jobs got to go out to Ozzy by next Tuesday.

KWIL17/07/2012 17:35:24
3681 forum posts
70 photos

All I can say is I have a 2.2kw 3ph motor on the Harrison M300 and a matching 3.9kva inverter. Absolutely no problems with control, running or lathe operations and use. The 2hp Bridgeport uses 2.8kva inverter with similarly no problems.

Jon17/07/2012 21:15:06
1001 forum posts
49 photos

Above is on an M300 but not dual voltage.

A mate has just sent me this link, it seems i may have underestimated the startup, it could be anything from 3 to 10 times the motor rating so 22.5kw (30hp)! Also why last lathe 1.125kw (1.5hp) 240v blew a 13A fuse 1 in every 3 startups with no load.

http://wiki.answers.com/Q/Why_is_the_starting_current_of_an_3phase_induction_motor_higher_than_its_rated_current

John Olsen17/07/2012 21:58:13
1294 forum posts
108 photos
1 articles

When you start a three phase motor by directly switching it on line, it will take a large starting surge. This is because the armature will act as a shorted secondary on a transformer. Larger motors usually have more sophisticated arrangements for starting to avoid this, eg they will have a wound rotor instead of a squirrel cage, and they will switch resistance into the rotor circuit for starting. Incidently like any transformer, when you switch it online there is a random chance of hitting a point in the cycle which will give larger surge, which is why things will randomly blow fuses.

However if you use it with a VFD there should be no starting surge. This is because the inverter will start out at low voltage and low frequency and ramp the motor up to speed. The time taken to do this is usually adjustable but should not be shortened too much. It may need to be longer with loads with a lot of inertia. You should never switch between the motor and an inverter, the control should always be from the inverter, and any isolation switching should be upstream from that.

You don't usually need to size an inverter much larger than the motor, although it does no harm and can be useful if you later want to use the VFD on a bigger machine. You can set things like the current limit to suit the smaller motor and tweak it again later.

Steve, the possible problem with feeding single phase to a three phase inverter is that the peak current through the diodes will increase, as will the ripple current through the capacitor. There will be some margin in the design, but there is no way to be sure unless it fails. So you takes your chances.....Parallelling all the diodes should help them, but does not help the capacitor.

John

KWIL18/07/2012 15:31:55
3681 forum posts
70 photos

Jon,

A 10 second start ramp time on the M300 is more than adequate, even with a very heavy 260mm 4 jaw chuck. Have you been controlling via the inverter as John Olsen points out or are you just dropping the lathe onto the inverter through it's own switch gear?

Jon18/07/2012 16:23:35
1001 forum posts
49 photos

As said before "No soft start, its plug and play just the way 3ph 400V+ would be installed to premises." Existing control panel untouched, inverter wired direct to main on/off rotary, retaining all functions.

An inverter is a means of changing DC to AC, misrepresented as a VFD.

At the time if i could have got the remotist of help from Direct Drives, the second inverter 4kw 400V would have been used as a VFD. Months passed lathe needed pronto as other Harrison was shot no time to figure the rewiring. Motor ran ok but never tried under load with 3 sec soft start which would have been tolerable.

Might get that 4kw inverter back if i can work out the lathe functions, should do but prob is where to wire in to the inverter, manual absolutely uselss blind you with science 100 odd pages but no ref to inputs. Or buy a Machine Mart motor and another cheap inverter 220v where you can get help.

I couldnt live with a 10sec soft start for higher revs, job could have been finished by then.

Currently using a 7.5kw 3ph 400V inverter 'Plug and play' meant for running whole workshops. Only problem i get is a live to neutral unbalance so trips the main RCCD at anything starting lathe up past 540rpm.

What sort of cuts can you put on power feed running at 220v 3ph?

Steve Garnett18/07/2012 17:25:36
837 forum posts
27 photos
Posted by John Olsen on 17/07/2012 21:58:13:

Steve, the possible problem with feeding single phase to a three phase inverter is that the peak current through the diodes will increase, as will the ripple current through the capacitor. There will be some margin in the design, but there is no way to be sure unless it fails. So you takes your chances.....Parallelling all the diodes should help them, but does not help the capacitor.

Whilst all that's true if you load the inverter heavily (and I'd suggested adding an additional capacitor anyway, as the particular inverter allows for it) it wasn't really an issue as this particular inverter was completely over-specced for the job - by about 50%.

Most halfway decent inverters allow for short-term overloads, often up to 200% or so. The diodes they use on the input side are pretty hefty anyway - they have to be!

All Topics | Latest Posts

Please login to post a reply.

Magazine Locator

Want the latest issue of Model Engineer or Model Engineers' Workshop? Use our magazine locator links to find your nearest stockist!

Find Model Engineer & Model Engineers' Workshop

Sign up to our Newsletter

Sign up to our newsletter and get a free digital issue.

You can unsubscribe at anytime. View our privacy policy at www.mortons.co.uk/privacy

Latest Forum Posts
Support Our Partners
cowells
Sarik
MERIDIENNE EXHIBITIONS LTD
Subscription Offer

Latest "For Sale" Ads
Latest "Wanted" Ads
Get In Touch!

Do you want to contact the Model Engineer and Model Engineers' Workshop team?

You can contact us by phone, mail or email about the magazines including becoming a contributor, submitting reader's letters or making queries about articles. You can also get in touch about this website, advertising or other general issues.

Click THIS LINK for full contact details.

For subscription issues please see THIS LINK.

Digital Back Issues

Social Media online

'Like' us on Facebook
Follow us on Facebook

Follow us on Twitter
 Twitter Logo

Pin us on Pinterest

 

Donate

donate