Martin Connelly | 24/01/2021 09:01:26 |
![]() 2549 forum posts 235 photos | You are close to correct but not all the way there. Connect L1 and link to 1 and 3, connect and link L2 to 5 and 7, connect and link L3 to 9 and 11. Connect and link A to 2 and 4, connect and link B to 6 and 12, connect and link C to 8 and 10. Check this out on a bench first with a meter or continuity tester first to be sure it works as expected. Make up the link wires (6 off) to join the terminals 1-3, 5-7, 9-11, 2-4, 6-12, 8-10, In position one note what L1, L2 and L3 connect to, and check for continuity or not between the L1, L2 and L3 positions. I would expect them to connect to A (2), B(6), C(10) respectively and no continuity between them. In position two repeat as above, I would expect them to connect to A(2), C(8), B(12) respectively and once again no continuity between them. In position 0 I would expect no continuity between any terminals except where linked. Note this system is for use with a 3 phase supply that is not being fed by a VFD as stated above. They don't like switching the terminals when on. Martin C PS this is with the advantage of the table, up to then there was some guess work going on so it is important to have full information before going ahead with this sort of wiring. Edited By Martin Connelly on 24/01/2021 09:08:27 |
Les Jones 1 | 24/01/2021 10:13:58 |
2292 forum posts 159 photos | From the truth table Noel's instructions will only work in position 1. (Post 23/01/21 at 23:33) Edit. I see Martin has beat me to replying. His information will also work Les. Edited By Les Jones 1 on 24/01/2021 10:32:42 |
Martin Cargill | 24/01/2021 11:47:43 |
203 forum posts | Good to see that this has been cleared up
Just a word of warning regarding Alain Foote's solution. Connecting a switch in the way that has been suggested will certainly work BUT this leaves the motor connected to one live phase even with the switch on the off position. Thus its possible to receive an electric shock from the motor terminals even when its not running (assuming that the contactor is still energised)
I once realised that some 3 phase DeWalt saws are connected in a similar manner. Their motor control switchgear only controls two of the three phases. The third phase is connected to the motor all of the time, so if the saw is connected to the mains the motor is live.......
Martin |
Me. | 24/01/2021 14:36:36 |
147 forum posts 30 photos | Thakns again for all this info. Just to clear this in my mind - where you say "link" you mean add a link wire between the terminals. ? My machine has an On Off Button which controls a contactor which then send the power to the old switch - No VFD. Is there any chance of a small schematic diagram ?
Just to note I had already Rulled out the "one line directly to the motor" option as I don't really want the motor to be live all the time its switched on. |
Bazyle | 24/01/2021 14:37:04 |
![]() 6956 forum posts 229 photos | mmm probably very helpful thread for future fererence |
Les Jones 1 | 24/01/2021 14:48:18 |
2292 forum posts 159 photos | Reading through the thread again I notice you do have a contactor so here is a suggestion that would ensure the contactor dropped out when the switch passed through the middle off position. Connect L1 directly to A on the motor. Connect L2 to 6 and link 6 to 8. Connect L3 to 10 and link 10 to 12 Link 1 to 3 We will call this point X Link 2 to 4 We will call this point Y Break the feed to the contactor coil and connect the two ends of the break one to X and one to Y
Les. Edited By Les Jones 1 on 24/01/2021 14:56:22 |
Me. | 24/01/2021 15:16:33 |
147 forum posts 30 photos | I had thought of that option and I suppose it would be safer I suppose if I did it that way - For some reason my PC isn't allowing me to upload any photos - pictures so I can't draw out what I have got but its very basic wiring. 3 phase wires + Neurtal which goes into the coil of the contactor 1 phase wire goes into the coil of the contactor (hager - 240v coli) and into the switch - one "off" and one "on" wired in series. When I press the "on" button it energises the coil which brings in the contactor - which then feeds my (very) old existing lever switch. Up for forward and down for reverse. To stop the motor I bring the lever switch to the middle which kills the power to the motor and then I press the "off" button.
I was just getting my head around the Linking terminals now it looks like I'm gonna have to add more.... Ive not brought the rotary switch yet so if i need a 16 terminal switch then that's ok. |
john fletcher 1 | 24/01/2021 15:42:32 |
893 forum posts | I have been following this discussion with interest, so would some one tell the part number for this switch and where can I get the truth table or was it included with the package. John |
Martin Connelly | 24/01/2021 16:05:14 |
![]() 2549 forum posts 235 photos | This is the basic circuit that does not involve the contactor circuit. Martin C Edited By Martin Connelly on 24/01/2021 16:06:19 |
Me. | 24/01/2021 16:06:04 |
147 forum posts 30 photos | Hi John I just went on Ebay and inputted - 3 phase motor reversing switch. |
Me. | 24/01/2021 16:10:45 |
147 forum posts 30 photos | Wow Martin - Thanks- that is exactly what i needed - it is so much easier to understand when written down like that. I can't thank you enough - I wonder if you could do one with the other option with the It breaks the feed to the coil on the contactor as suggested by Les |
Martin Connelly | 24/01/2021 16:13:47 |
![]() 2549 forum posts 235 photos | This is the one where the top contacts are used to latch the contactor as described by Les. The contactor may have terminals just for this external latching with a link in place. Martin C |
Les Jones 1 | 24/01/2021 17:00:29 |
2292 forum posts 159 photos | It would be better if you can provide information on the existing so we can tell you where to break the feed to the contactor coil. all of the interlocks, the thermal overload contacts and the stop button will probably be in series with the coil. Also we don't know if the contactor coil is powered between phases, between a phase and neutral or from the secondary of a low voltage transformer. Your existing wiring diagram should provide that information. Les. |
Me. | 01/02/2021 15:54:36 |
147 forum posts 30 photos | Two pictures of the contactor and switches as fitted to my Mill. Brown Black and grey input from the mains at the top. the 3 pairs of yellow blue and red are the feed to the two motors. Which I am fitting the new rotary switches too. The brown leads go to two momentary switches the green one energizes the contactor and the red one turns it off. The blue wire sticking out at right angles is the neutral. Where do I need to break the leads to add my new switches as per Martins wiring diagram ( X - Y connection) Or do I need to replace the momentary switches for something else.
|
Les Jones 1 | 01/02/2021 17:34:52 |
2292 forum posts 159 photos | Here is a diagram of how I suggest adding the reversing switch.
Connect the reversing switch as in Martin's drawing posted at 16:13 on Jan 24th. Les. |
Me. | 02/02/2021 08:59:20 |
147 forum posts 30 photos | HI Les Many thanks again for your very easy to understand description and diagram. I will do as suggested. As I will have two rotary switches - one to control the main spindle motor and one to control the table feed, do I take a separate feed to each X point on each switch or do I add the switches in series. i.e "Brown (feed) - X-Y-X-Y - Stop". Steve |
larry phelan 1 | 02/02/2021 09:51:16 |
1346 forum posts 15 photos | Just as a matter of interest, why would you need to run the mill in reverse ? |
Les Jones 1 | 02/02/2021 10:36:50 |
2292 forum posts 159 photos | Hi Steve, Les. |
Me. | 02/02/2021 10:44:53 |
147 forum posts 30 photos | Thanks Les _ I can do that I have a spare contactor the same as the picture. Will I need two more on/off buttons as well ? My Idea was 1.Press the button to turn the contactor on 2.Switch the main motor on (rotary switch) 3.Switch Table feed on (rotary switch) 4.switch to the "0" position when finished cut 5.Press the off button to turn main power off. *i'm now in need to know the answer to Larry's Question - why does the main spindle motor need to run in reverse ???* It has the option too on the "old switch panel" but when would you ever need to make a cut with the spindle in reverse ??
|
Les Jones 1 | 02/02/2021 11:54:56 |
2292 forum posts 159 photos | You would need an extra stop button and start button. Les. Edited By Les Jones 1 on 02/02/2021 12:00:15 |
Please login to post a reply.
Want the latest issue of Model Engineer or Model Engineers' Workshop? Use our magazine locator links to find your nearest stockist!
Sign up to our newsletter and get a free digital issue.
You can unsubscribe at anytime. View our privacy policy at www.mortons.co.uk/privacy
You can contact us by phone, mail or email about the magazines including becoming a contributor, submitting reader's letters or making queries about articles. You can also get in touch about this website, advertising or other general issues.
Click THIS LINK for full contact details.
For subscription issues please see THIS LINK.