Andy Sproule | 17/11/2017 22:27:34 |
122 forum posts 35 photos | Hi got my rotary converter up and running 240 to 415.Tried it and ran my lathe the voltages were 419,396 and 389 would this be considered acceptable or is it too far out of balance? |
Brian Sweeting | 17/11/2017 22:47:38 |
453 forum posts 1 photos | Unless it has recently changed the accepted voltage tolerance in the UK is 415 -6% +10% which gives you 390 low and 456 high so you should be okay. How is the amperage though? Edited By Brian Sweeting on 17/11/2017 22:47:51 Edited By Brian Sweeting on 17/11/2017 22:49:40 |
not done it yet | 17/11/2017 23:05:20 |
7517 forum posts 20 photos | I don't think balance between phases and voltage tolerances are the same. Three phases all at +10% is not the same as two @ +10% and the other @-6%. Whether that would make any difference operationally, I don't know. But we always tried to even out the legs on three phase generators as much as possible. |