john fletcher 125/09/2023 17:41:25
893 forum posts

Back again, many thanks chaps, plenty to read and ideas to act upon. I've print out the text and will give to my friend, I'll come back some time later to let you all know the result. John

Robert Atkinson 225/09/2023 17:55:43
avatar
1891 forum posts
37 photos
Posted by Chris Pearson 1 on 25/09/2023 12:03:24:
Posted by Master of none on 24/09/2023 23:01:37:

In discussions with Meggar, they recommended using the clamp meter around line and neutral together. A parallel path to earth through an extraneous conductive part (e.g. water pipe, gas pipe or structural steelwork) could reduce the current in the earthing conductor and give a misleading measurement of the difference between line and neutral currents. The clamp meter needs to cover the range 0-30mA.

Only: (1) if there are any extraneous CPs (which is seldom the case in modern homes); and (2) the device is attached to an ECP and the fault or leakage is to that.

It does not have to be leakage to a conductive (metal) part extraneous or otherwise. An old junnction box screwed to wood and exposed to water will cause leakage current. The RCD senses line / neutral differential current so that is what you need to measure when testing.
A mill bolted to a even slightly damp concrete floor would provide a parallel path to earth.

SillyOldDuffer25/09/2023 21:17:05
10668 forum posts
2415 photos
Posted by Chris Pearson 1 on 25/09/2023 16:57:16:
Posted by SillyOldDuffer on 25/09/2023 12:28:45:
Posted by Robert Atkinson 2 on 25/09/2023 07:47:01:

Wot I said....

Yes, but I'm glad of all the clarifications. My understanding wasn't good enough! I assumed current in the earth cable should be measured, now I know better.

Hang on - this is all getting a bit muddled.

If you think that there is high earth leakage, you need to measure or calculate it, which requires access to the conductors individually. I see no advantage in testing L & N together as opposed to the CPC. If the device is bonded and you test L & N together, you do not know which route any missing electrons are taking.

Always happy to be educated!

In this Fluke diagram showing how to measure AC current, it's explained you can't put the clamp over Live and Neutral:

This I understand to be because the AC current flows one way in the Line wire and in the opposite direction in Neutral. The two generate magnetic fields that cancel out, so the clamp meter reads zero. Highly misleading.

However Live leaking to earth is a different case. The current flowing in Live is not equal to the Neutral current, so the magnetic fields don't quite cancel. A sensitive clamp meter will measure the difference, which is equal to the earth leak current.

Chris has me worried though: if the clamp is put over LN and E and the leak is due to a suppressor, the clamp won't detect it because the 3 magnet fields balance. It will detect a leak due to faulty insulation and a damp floor, because then not all the leak current goes back along the earth wire. Is that right?

Can anyone design a circuit that would reliably show how much current a device was leaking under all conditions?

I don't believe the debate alters the advice given to John.

Dave

Chris Pearson 125/09/2023 21:36:28
189 forum posts
3 photos
Posted by Robert Atkinson 2 on 25/09/2023 17:55:43:
A mill bolted to an even slightly damp concrete floor would provide a parallel path to earth.

Yes, but a really good earth rod in damp soil might manage 20 Ohms and the same at the transformer. By contrast, the earth path through all the green and yellow might be, say 0.5 Ohm. So assuming that any earth leakage is to the bed or case of the machine, the vast majority (99%+) will go down the green and yellow.

The insulation of your junction box should be sound. Around one megaohm is about the minimum acceptable resistance, but a new machine in good order should achieve one gigaohm.

Chris Pearson 125/09/2023 21:42:51
189 forum posts
3 photos

Posted by SillyOldDuffer on 25/09/2023 21:17:00

Chris has me worried though: if the clamp is put over LN and E and the leak is due to a suppressor, the clamp won't detect it because the 3 magnet fields balance. It will detect a leak due to faulty insulation and a damp floor, because then not all the leak current goes back along the earth wire. Is that right?

Yes, I think so, but that is exactly what you want to avoid - you do not want the bed of your machine at anything above earth voltage. There is a big difference between faulty insulation and earth leakage. If the bits and bobs in your VFD are "leaking" they are supposed to return to earth via the CPC.

If there were no earth leakage at all, why have RCDs at 30 mA rather than say 10 mA. (Yes 10 MA ones are available.)

Martin Shaw 125/09/2023 23:58:17
185 forum posts
59 photos

Chris P asked

"I am afraid that it is not quite as simple as that.

What type of earthing do you have please: TN-S, TN-C-S, or TT?"

Like most properties of the age of mine in a town or city the earthing is TNS. Obviously TNCS could cause confusion dependent on where you measure the neutral current but ultimately phase current less neutral current should ideally be but rarely is 0A. If it isn't then there's a leakage to earth which is simple enough. Finding the path of that leakage may well be complex, although I would agree with Chris that you would expect the majority to flow in the CPC and main earthing conductor.

Regards

Martin

Edited By Martin Shaw 1 on 26/09/2023 00:02:08

Robert Atkinson 226/09/2023 08:42:44
avatar
1891 forum posts
37 photos

OK we anre now deviating away from the original issue of LEAKAGE currents of around 0.03 amps (30 milliamps mA) into Mains earthing systems that have to carry FAULT currents of hundreads of amps. The leakage currents form VFDs and similar devices are not due to faults. A resistance of 10,000 Ohms (10k) with 240V (UK mains) across it will cause a current of 0.024A to flow (Ohms law I = V/R). This close to the 30mA trip current of a domestic RCD. !0K is thousands of times higher resistance than a mains earth. Lets forget about earthing systems.

SOD. The Fluke picture is not helpful becuase it is addressing using a clamp meter for it's typical application of mesuring load current not leakage. I can design a vey simple means of detecting leakage current. A current transformer with two primary windings one carrying the current in the line the other tha current in the neutral. Oh wait that's a current clamp meter around live and neutral. It's also what is built into most electrical installation meters.

Chris P. I said a junction box screwed to wood and exposed to water (a fault condition) not a new, dry box.
The earthing system in use TT, TNC-S etc is irrelevent to this discussion.

As for finding where the leakage is that is not difficult given a sensitive clamp ammeter. First measure and note the leakage current by placing the live and neutral in the jaws of the clamp meter.
To deterine if the leakage is through the desigined "earth" protective conductor add the earth conductor to the L&N in the jaws. Any remaining current is leakage to a connection outside the designed earth system such as damaged insulation.
This process can be carried out at an individual piece of equipment, a particular section of an installation e.g. a ring and the whole installation. Thia allows the exact source of the leakage to be identified. However the fact you would be dealing with individual conductors means that the first layer of protection against shock e.g. equipment case, outer insulation has been removed exposing you to a higher risck of electric shock. This work should only be carried out by competent persons.

As an extension to the testing, it is also possible to tell how much of the leakage current is due to the filters in a VFD or similar. To do this you need a phase sensitive current sensor. As the filter leakage is due to capacitors the current is ninety degrees out of phase with that caused by "normal" resistive leakage.
Note that this intentional current nomally flows through the metal case of the filter as well as any earth wire. You should never earth a filter or VFD purely by bolting it to an earthed metal panel ther must also be a flexible cable connection. This is because if the filter or VFD was unbolted from the panel the leakage current would become a shock risk to anyone touching it.

I've designed this sort of equipment. An example is protection of the high current feeder between a generator and a circuit breaker panel without using fuses in the feeders. You just run the feeder conductor through a current transformer at the generator end and another at the load end. Connect the transformers secondaries in series anti-phase to a sensitive current relay. Load current flows through both transformers and cancel out. Any current due to a fault between the two transformers (to neutral or "earth" only flows through the generator transformer and is not cancelled causing the sensitive relay to operate and shut down the generator.

Robert.

Chris Pearson 126/09/2023 13:21:46
189 forum posts
3 photos
Posted by Martin Shaw 1 on 25/09/2023 23:58:17:

Like most properties of the age of mine in a town or city the earthing is TNS.

Then I think that you can quite reasonably conclude that your machines are sound.

However, with TN-C-S current in the earthing conductor may have nothing to do with leakage so if you find it, you cannot conclude that something is amiss.

(And don't forget that even with what looks like TN-S, there may be N-E links nearby.)

Mike Poole26/09/2023 13:34:11
avatar
3676 forum posts
82 photos

My mother’s bungalow had solid brick walls, the earth trip was operating so after unplugging everything the problem remained, dampness in a bedroom 13A socket was the problem, curiously it never happened again after a good drying out with a hair dryer. A high voltage insulation tester commonly referred to as a Meggar is the most useful tool for a fault of this nature.

Mike

Robert Atkinson 226/09/2023 15:54:38
avatar
1891 forum posts
37 photos
Posted by Chris Pearson 1 on 26/09/2023 13:21:46:
Posted by Martin Shaw 1 on 25/09/2023 23:58:17:

Like most properties of the age of mine in a town or city the earthing is TNS.

Then I think that you can quite reasonably conclude that your machines are sound.

However, with TN-C-S current in the earthing conductor may have nothing to do with leakage so if you find it, you cannot conclude that something is amiss.

(And don't forget that even with what looks like TN-S, there may be N-E links nearby.)

Hi Chris,

Can you please explain your reasoning behind the earthing system making a difference to machine leakage current? I think I'm missing something.

Any connection between neutral and earth downstream from an RCD will alost certainly cause it to trip.

Robert.

Chris Pearson 126/09/2023 17:31:22
189 forum posts
3 photos
Posted by Robert Atkinson 2 on 26/09/2023 15:54:38:
Posted by Chris Pearson 1 on 26/09/2023 13:21:46:
Posted by Martin Shaw 1 on 25/09/2023 23:58:17:

Like most properties of the age of mine in a town or city the earthing is TNS.

Then I think that you can quite reasonably conclude that your machines are sound.

However, with TN-C-S current in the earthing conductor may have nothing to do with leakage so if you find it, you cannot conclude that something is amiss.

(And don't forget that even with what looks like TN-S, there may be N-E links nearby.)

Hi Chris,

Can you please explain your reasoning behind the earthing system making a difference to machine leakage current? I think I'm missing something.

Any connection between neutral and earth downstream from an RCD will alost certainly cause it to trip.

Robert.

Robert, A couple of hundred Ohms of resistance in an TT earth path might make a milliamp or two of difference, but that is not my point.

If the supply is TN-C-S and there are any diverted neutral currents, they will swamp any earth leakage so you cannot necessarily measure it by looking at the current in the earthing conductor.

I was referring to the N-E link, which is normally in the service head, but there will almost certainly be other links nearby such as a neighbouring property or street lamps.

Some of my electrons appear to be going from N to E then through the bonding to the gas pipe then to at least one neighbour's gas pipe, along their bonding to the main earthing terminal and then back to the transformer via E or N, or a combination of the two.

Just now, I got a reading of 0.40 A with my clamp meter around L, N, and E together.

Robert Atkinson 226/09/2023 18:25:11
avatar
1891 forum posts
37 photos

N-E connections up-stream of the RCD or consumer unit are immaterial to RCD operation and leakage currents.

The whole point of measuring L-N differential current rather than earth conductor current is to capture all leakage.
400mA of leakage is a bit excessive. I'd want to investigate what is going on. what is the current in the protective conductor?
One thing is if you have metalwork with a low resistance to ground connected to the mains ground your system may be passing some mains return (neutral) current from your neighbors. If theter is a neutral fault in the street you could be badly affected.


Radio amateurs on TNC-S can suffer from this when their RF earth, often extensive and low resistance, is connected to mains earth via their radios. With a neutrla fault 100's of amps can flow.
The latest guidnace on NOT connecting pipework etc to TNC-S systems seems to be a way of avoiding this inhernet problem with TNC-S The only advantage of TNC-S is lower cost to the network providers.

Robert.

Chris Pearson 126/09/2023 18:43:11
189 forum posts
3 photos
Posted by Robert Atkinson 2 on 26/09/2023 18:25:11:

what is the current in the protective conductor?

Yesterday, I measured 3.0 A. It seems to fluctuate quite a bit. Generally, it seems to lie between 10% and 25% of the current in the Line.

All Topics | Latest Posts

Please login to post a reply.

Magazine Locator

Want the latest issue of Model Engineer or Model Engineers' Workshop? Use our magazine locator links to find your nearest stockist!

Find Model Engineer & Model Engineers' Workshop

Sign up to our Newsletter

Sign up to our newsletter and get a free digital issue.

You can unsubscribe at anytime. View our privacy policy at www.mortons.co.uk/privacy

Latest Forum Posts
Support Our Partners
cowells
Sarik
MERIDIENNE EXHIBITIONS LTD
Subscription Offer

Latest "For Sale" Ads
Latest "Wanted" Ads
Get In Touch!

Do you want to contact the Model Engineer and Model Engineers' Workshop team?

You can contact us by phone, mail or email about the magazines including becoming a contributor, submitting reader's letters or making queries about articles. You can also get in touch about this website, advertising or other general issues.

Click THIS LINK for full contact details.

For subscription issues please see THIS LINK.

Digital Back Issues

Social Media online

'Like' us on Facebook
Follow us on Facebook

Follow us on Twitter
 Twitter Logo

Pin us on Pinterest

 

Donate

donate