electrical fault puzzle

hobby shed lights

All Topics | Latest Posts

Search for:  in Thread Title in  
Diogenes19/09/2023 19:58:18
61 forum posts
6 photos

Where there's a rural ceiling cavity there's always a chance of mice.. ..the dribbly little blighters..

Chris Pearson 119/09/2023 20:21:25
189 forum posts
3 photos
Posted by Robert Atkinson 2 on 19/09/2023 19:45:12:

Yes he has " Consumer unit is a main 60ARCD with 4 MCB's the lighting circuit NIDCB06 "

So RCD on input and 6A MCB feeding four switched light circuits. My understanding is that the fault WAS if EITHER of the two internal light circuits were switched on the 6A MCB tripped.

I see what you mean - appropriate spacing might have helped. Given that the incomer is not tripping, that seems to rule out an (earth) fault.

Another possibility is excessive inrush current, which is tripping the type B MCB.

pgk pgk19/09/2023 20:41:06
2661 forum posts
294 photos

When I did the light conversion I removed all necessary gubbins.. wired direct to the tube holders.

One 6a MBC for the 2 pairs of 6ft led tubes and another MBC for the external security lights.

Chris Pearson 119/09/2023 20:53:32
189 forum posts
3 photos

I still think that you need to look at the inrush current. It may be marginal, and it may be temperature dependent.

This may help.

pgk pgk19/09/2023 21:38:09
2661 forum posts
294 photos

I bow to folk that understand this stuff. It'd be odd to start happening after 2,3 years of led use and with it happening on each single run of 2 6ft tubes. It's worked during previous heatwaves & Welsh rain

Robert Atkinson 219/09/2023 22:03:05
avatar
1891 forum posts
37 photos

The number of LED lamps fitted are highly unlikely to cause a 6A MCB to trip on inrush. It is also unlkiely to be intermiitent.
I don't think this is a problem that can be diagnosed remotely. The only thing I can think of based on the description is some kinf of intermittent fault in the 4 position switch or it's immediate wiring. I There is not much else that is common to both strings of lights. Damage by rodents or insect infestation is another possibility but unless the two strings share a common cable (3 core and earth is a possibility) or junction box it is still hard to see a common point of failure.

Robert.

Chris Pearson 119/09/2023 22:59:36
189 forum posts
3 photos
Posted by Robert Atkinson 2 on 19/09/2023 12:37:48:

That is very strange. Turning on either set of lights causing an over-current trip implies a common fault or fault load before the switch just under the trip point. Neither of these has an obvious cause. It would require knowledge of the exact wiring arrangement right down to the connection methods used.
What type and rating of lights?
What rating circuit breaker?
What brand of switches etc?

The next step as an electrician would be some measurements, insulation resistance and load current and a detailed inspection..

Well yes.

If we exclude an (earth) fault and inrush, what is left?

If the cables are T&E in plastic mini-trunking, how could they have been damaged? In any event, surely they can be inspected.

Ed Duffner20/09/2023 00:06:38
863 forum posts
104 photos
Posted by Chris Pearson 1 on 19/09/2023 22:59:36:

Well yes.

If we exclude an (earth) fault and inrush, what is left?

 

Some readings on the circuits would be useful, but I'm not sure nowadays if an insulation-resistance test can be performed whilst LED lights are connected. Needs an Electrician ideally to assess this.

Other things to check:

- With the incoming power off and everything made safe I would check that the MCB's are properly secured to the busbar in the consumer unit and the circuits are also tightly connected in the MCB's. Might be a loose connection and/or corrosion build-up.

- Swap the inside and security light circuits onto each other's MCB's. If the security lights then start to trip, it could be a faulty MCB.

- Check the connections to each of the light fittings are sound and make good where necessary. See over time if this has sorted the problem. There might be a dodgy connection on both runs of lights. Some of the push-in types of connectors aren't that great in my opinion, if these are what're used, but I doubt this is the issue. Worth checking anyway.

 

Ed.

Edited By Ed Duffner on 20/09/2023 00:08:22

All Topics | Latest Posts

Please login to post a reply.

Magazine Locator

Want the latest issue of Model Engineer or Model Engineers' Workshop? Use our magazine locator links to find your nearest stockist!

Find Model Engineer & Model Engineers' Workshop

Sign up to our Newsletter

Sign up to our newsletter and get a free digital issue.

You can unsubscribe at anytime. View our privacy policy at www.mortons.co.uk/privacy

Latest Forum Posts
Support Our Partners
cowells
Sarik
MERIDIENNE EXHIBITIONS LTD
Subscription Offer

Latest "For Sale" Ads
Latest "Wanted" Ads
Get In Touch!

Do you want to contact the Model Engineer and Model Engineers' Workshop team?

You can contact us by phone, mail or email about the magazines including becoming a contributor, submitting reader's letters or making queries about articles. You can also get in touch about this website, advertising or other general issues.

Click THIS LINK for full contact details.

For subscription issues please see THIS LINK.

Digital Back Issues

Social Media online

'Like' us on Facebook
Follow us on Facebook

Follow us on Twitter
 Twitter Logo

Pin us on Pinterest

 

Donate

donate