SillyOldDuffer | 26/03/2022 11:38:29 |
10668 forum posts 2415 photos | Posted by duncan webster on 26/03/2022 10:19:25:
... The motor manufacturers warned against running older 3 phase motors on vfd, something to do with insulation I think ...
Driving electric motors made before 1967 with a VFD is a bit risky. I know the forum likes to believe ancient British electric motors are far better than any modern foreign rubbish. But get real! Although old British motors were well-made they were limited by the technology of the time, and don't forget old age and damp storage does them no favours. Two reasons a VFD might damage an old motor:
1967 is the year after which the bearing problem was universally fixed and all motors were wound with modern enamel magnet wire. Does it matter? Maybe not. Weak insulation and tiny sparks inside the bearings are unlikely to cause an instant bleeding obvious failure. Bearing damage might never show up in a home-workshop and there's a reasonable chance even ancient insulation will be 'good enough' for a VFD. Problems are more likely to show up after many hours of operation than as an instant spectacular fail. I wouldn't go out of my way to fit an old electric motor, but if I had one to hand I'd dry it out carefully before using it. The worst that can happen is having to replace the old banger with a new one! Dave |
Robert Atkinson 2 | 26/03/2022 16:57:47 |
![]() 1891 forum posts 37 photos | A 415V Star connected motor running on a UK light industrial 3 phase supply will have 240 V between each supply terminal and ground and 415 V between phases. (the ratio between the voltages is the square root of the number of phases, sqrt3 or 1.732 for 3 phase). The supply transformer will be connected Star with the common point connected to ground and the neutral conductor. This allows both single and 3 phase loads. |
john fletcher 1 | 26/03/2022 17:34:59 |
893 forum posts | In the past 3 or 4 years some one on this forum published am excellent article, with good clear pictures on how he located the Star point and brought out 3 extra wires into his motor terminal box. I have done the conversion for my friends, all on older motors, and as yet to hear of a failure, they bought their inverters via ebay and again not heard of a failure, could be they are just lucky ! I have an insulation tester up 1000volts which I used to give the motors a test before use. Have a go, you have not much to lose, you need to look out for a lump in the windings area which needs to be carefully opened up, and three wires attached. I used three different coloured wires for identification purposes, fibre glass insulation tube and heat shrink and a small amount of resin is readily available via ebay. Best of luck and let us know how you get on. John |
Andrew Johnston | 27/03/2022 11:06:34 |
![]() 7061 forum posts 719 photos | Posted by choochoo_baloo on 25/03/2022 19:59:02:
...wouldn't a star connection actually run at one third* of the motor rated power... I was thinking in terms of mechanical output power: Power = torque x angular velocity Assuming both voltages are at 50Hz the angular velocity is constant. The voltage reduced by the square root of 3 leads to phase currents reduced by the same. To a first approximation the torque is proportional to the phase current. So the torque, and hence power, is reduced by the same factor, ie, the square root of 3. Andrew |
Please login to post a reply.
Want the latest issue of Model Engineer or Model Engineers' Workshop? Use our magazine locator links to find your nearest stockist!
Sign up to our newsletter and get a free digital issue.
You can unsubscribe at anytime. View our privacy policy at www.mortons.co.uk/privacy
You can contact us by phone, mail or email about the magazines including becoming a contributor, submitting reader's letters or making queries about articles. You can also get in touch about this website, advertising or other general issues.
Click THIS LINK for full contact details.
For subscription issues please see THIS LINK.