mark smith 20 | 03/08/2016 15:12:40 |
682 forum posts 337 photos | Posted by Emgee on 03/08/2016 12:37:43:
Mark Type C mcb, use ramp up speed to prevent mcb tripping. Cable shown is suitable but if you don;t use the proper glands that are listed be sure to take a tail of the protective braid into the earth terminal at source of supply and same at motor. The 1.5mm size will be OK with such low current and short lengths but you may have to go to 2.5mm to satisfy short circuit protection of the type C mcb. You may want to fit a Double Pole isolator in the feed from the consumer unit to provide complete isolation of the supply at the inverter. Emgee Bazyle, states Continuos Duty on the plate but your advice should be headed. Edited By Emgee on 03/08/2016 12:46:46 You mean an isolator like this, say the 20 amp one?? **LINK** |
mark smith 20 | 03/08/2016 15:40:37 |
682 forum posts 337 photos | Posted by Martin Connelly on 26/07/2016 13:33:13:
I'd use a rigid type terminal strip rather than the soft nylon type, they are more like the material usually found as terminal blocks in motors and may be more resilient with regard to fretting due to vibration. Martin
Hi Martin, so which of those on that link do i need, you mention 2 wires on one side and one on the other???? Heres my idiot understanding of the wiring is that right or completely wrong. Edited By mark smith 20 on 03/08/2016 15:41:54 Edited By mark smith 20 on 03/08/2016 15:42:46 |
mark smith 20 | 03/08/2016 18:50:46 |
682 forum posts 337 photos | Anyone?? |
mark smith 20 | 03/08/2016 20:04:32 |
682 forum posts 337 photos | Really need advice on this,am i on the right track? Can a 3 section block be used and the T4 T5 T6 wire be simply twisted together seperately from the block and one of those twist cap wire connectors used?? Thanks |
Andy Holdaway | 03/08/2016 20:39:37 |
![]() 167 forum posts 15 photos | Mark, your sketch is correct for a 230v 3 phase setup to run from a single to three phase inverter. If the motor runs the wrong way, swap any two of the wires from the inverter to the motor. Andy |
Emgee | 03/08/2016 21:52:59 |
2610 forum posts 312 photos | Mark, the isolator you linked to should be OK but don't forget to connect both ends of the cable metal braid for continuity of protection, either use earthing rings with connecting conductor or take the tails into the enclosure and connect at the earthing terminal with the cpc's (g/y earth cables) Emgee |
Andy Ash | 03/08/2016 22:29:52 |
159 forum posts 36 photos | From what you show it seems correct, but my meter probes won't reach your motor from here. Unfortunately I can't say you won't burn your house down! Good luck. Edited By Andy Ash on 03/08/2016 22:30:26 |
mark smith 20 | 04/08/2016 12:19:48 |
682 forum posts 337 photos | Andy thanks for the confirmation,ill blame you if i blow myself up!!! Emgee ,thanks for the info,ill try and follow the advice correctly. One question is the screw in the middle of the terminal box (middle of black area going into motor housing) on the motor the one to secure down a terminal block?? I assume the one to the side is the earth? |
mark smith 20 | 11/08/2016 10:23:38 |
682 forum posts 337 photos | Hi , Im wanting to test the motor and inverter off the machine as im no way ready as the machines in pieces being cleaned up. Would a 2hp motor and inverter run off a normal 13 amp plug just for testing purposes. The inverter says input current 17.8 amps but as there will be no load on the motor would i be ok ? Or will i need to have it wired into the consumer unit through the mccb before i can safely test it to just see that both motor and inverter are at least working? Thanks |
Martin Connelly | 11/08/2016 12:51:47 |
![]() 2549 forum posts 235 photos | The 17.8 amps may be inrush current when first switched on as capacitors are charged, these inverters have quite high capacity ones inside. The current draw when running will depend on the motor and load but should be proportional to the load the motor is taking. I would give it a go and see what happens. If it trips a circuit breaker then reset it and try again, if it is capacitors being charged then once they are full the inrush current will drop off. There is a possibility that the maximum current given is for an inverter with a motor matched to its maximum output and set up to run at startup. Most default to not running at startup but if you have one set up in a factory where power trips regularly you may want automatic restart when power is restored. Martin |
Please login to post a reply.
Want the latest issue of Model Engineer or Model Engineers' Workshop? Use our magazine locator links to find your nearest stockist!
Sign up to our newsletter and get a free digital issue.
You can unsubscribe at anytime. View our privacy policy at www.mortons.co.uk/privacy
You can contact us by phone, mail or email about the magazines including becoming a contributor, submitting reader's letters or making queries about articles. You can also get in touch about this website, advertising or other general issues.
Click THIS LINK for full contact details.
For subscription issues please see THIS LINK.