Thread: Peculiar electrical problem
24/09/2023 23:01:37

In discussions with Meggar, they recommended using the clamp meter around line and neutral together. A parallel path to earth through an extraneous conductive part (e.g. water pipe, gas pipe or structural steelwork) could reduce the current in the earthing conductor and give a misleading measurement of the difference between line and neutral currents. The clamp meter needs to cover the range 0-30mA.

24/09/2023 22:56:02
Posted by Chris Pearson 1 on 24/09/2023 20:58:47:
Posted by Robert Atkinson 2 on 24/09/2023 19:19:24:

You don't actually measure thr current in the CPC ("earth" conductor). This is becuse the leakage culd be finding a different path to ground. You do what an RCD does, measure the difference in current between the line and neutral. A clamp meterto do this has to go around the line and neutral.

You can put your clamp meter around line and neutral together, or CPC, but it doesn't make any difference.

You could even put two AVOs in the line and neutral and calculate the difference.

Thread: Fuse Rating for VFD
16/08/2023 17:04:21

Qualified is a term often used in manufacterer's instruction and is in my opinion, somewhat meanlingless regarding electricial installation work.

The Electricity at Work Regulations states that

"No person shall be engaged in any work activity where technical knowledge or experience is necessary to prevent danger or, where appropriate, injury, unless he possesses such knowledge or experience, or is under such degree of supervision as may be appropriate having regard to the nature of the work". In my opinion, this applies more to installation and testing work which needs to be carried out safely.

BS7671 Requirements for Electrical Installations requires:

"Good workmanship by one or more skilled or instructed persons and proper materials shall be used in the erection of the electrical installation. The installation of electrical equipment shall take account of manufacturers' instructions."

Neither document stipulates the neeed to be qualified or the level of a qualification, except for a curious mention in BS 7671 of a "qualified electrian" in a sample notice regarding the temporary connection of a caravan to a plot supply point, It could be argued that a qualification may be evidence that an installer is "skilled" or "competent" but I have seen plenty of examples of individuals who have paper qualifications but whom could not be trusted to produce a safe installation unless thery are closely supervised. In addition, an electrician who is deemed competent to carry out domestic installations may not be competent to install systems in an industrial location.

Thread: How to test dc motor or board?
01/08/2023 22:01:03

Could I suggest that your refer to the "live" conductor as the "line". The neutral is connected to the supply transformer as well as being earthed, so technically, it is also a live conductor.

Thread: Cutting Oil Fumes
17/06/2023 22:23:26
Posted by Justin Thyme on 17/06/2023 20:07:25:
Posted by SillyOldDuffer on 17/06/2023 19:04:03:

Ventilation is the best answer. The worst thing to do is breath fumes through a lit cigarette.

Dave

I used to smoke heavily when working with asbestos, (the monkey dung variety), I guess the asbestos would not have become more dangerous after passing through the red glow of the fag end - LOL

Edited By Justin Thyme on 17/06/2023 20:08:00

Probably true, but is smoking makes you more likely to suffer the effects of asbestos exposure

https://www.asbestos.com/asbestos/smoking/#:~:text=Smoking%20damages%20cilia%2C%20making%20it,scar%20tissue%20in%20your%20lungs

Thread: Workshop floor advice please
13/05/2023 15:14:42

My concern with a latex screed is that it is not regarded as a finish. Similarly, cement and sharp sand is usually the bed for another finish but it could also be painted.

The traditional screed was was usually 50-75mm thiich bonded to the subfloor by coating with cement grout before laying the screed.. PVA on the subfloor is a better alternative. A good plasterer could achieve a flat and even finish but shrinkage of the screed may mean that it does not bond fully to the subfloor. However, the compressive strength of the screed should to be sufficient to support the machinery as the subfloor will provide the bending strength.

I agree with Clive on this one. As you have 40mm to accommodate, I would use some 18mm battens and 22mm green chipboard with glued joints. Some polystyrene insulation between the battens would make it more comfortable for standing. If you have high point loads for machinery, you could cut a core hole at each point and fill it with a hardwood plug bearing on the subfloor. That would eliminate the deflection of the chipboard floor. Some floor paint would add a finish.

Thread: Surface plate
22/11/2022 19:35:32
Posted by Bazyle on 22/11/2022 19:25:33:

Really you can only use cast iron because of the way it can be scraped. I'm not sure how other materials would respond. You can grind glass and therefore probably porcelain. Generally tiles of various sorts are gong to be thin and hence flexible so you would want to laminate a few together first.

Another possibility is to find a kitchen fitter and see if they will give you the bits they cut out of granite worktops for the sink. These are still too thin to use as is.

I agree. Kitchen worktops are probably too thin to give you a relaible surface plate. I can measure slight curve in my granite worktop.

See Robin Renzetti's Youtube for lapping a granite surface plate.

Thread: Workshop going into storage - Rust Prevention?
21/11/2022 19:29:21
Posted by J Hancock on 21/11/2022 17:17:37:

Many, many years ago MEng did a test on this subject.

Three-in-one oil came out way ahead of all the other fluids used to provide protection against corrosion.

img_20220718_204736864.jpg

I tried this test a while ago. Five pieces of identical plate suspended beneath the eaves of my garage for a period of months, From the left:

No treatment

Muck Off

3 in 1

WD40

Waxoil (best).

I use white spirit to remove it

21/11/2022 17:15:15

I have had good results with Shell Ensis fluid or Waxoil from Halfords. Cutting tools well oilded in sealed plastic bags also seems to work. You may have difficultiy obtaining Ensis in small quantities

Thread: cable core colours for 3 phase motors
18/09/2022 21:12:51

BS 7671 requires that the cables comply with relevant standards which could be British Standards or equvalent. SY cable does not have a particular standard. However it is widely used in industry for final connections to machines where inverters (VFDs) are used to control motors. The reason is that the braid on ST cable is earthed and helps to minimise the noise caused by the VFD which could affect other equipment.

SY is a useful cable but should not be considered as an armoured cable as the braid in not as tough as the steel wires in an SWA cable.

Yes, the cores are all black and are numbered but coloured sleeve could be used to identify the cores as Brown, Black and Grey.

Special brass cable glands are available terminating the cable but, in many cases, I have seen plastic stuffing glands used. It is important that the braid is earthed at the origin of the cable and that the terminations are not put under strain if the cable is pulled.

Edited By Richard Taylor 17 on 18/09/2022 21:13:10

Thread: Motor terminal issue
04/09/2022 17:10:39

I would fit a Wago on the cooked conductor once you have cut back the worst of the damaged insulation. Hopefully that is still within the terminal box of the motor. If you need to go back further, you would have to dismantle the motor far enought to expose the good part of the conductor, In that case, you bay be ettor off with a butt splice crimp to save space.

04/09/2022 14:21:17

Could you use a Wago lever-type connector to extend the conductor? Easier to fit and you would not be trying to use a crimpt tool in a small space. As Wago connectors are constant pressure, they do not creep in a location where vibration can be a problem.

Thread: Quorn Workhead Conundrum.
30/08/2022 19:58:43

Do you know if the part was turned from a casting or round stock?. As I recall the workhead was not the easiest part to turn, particularly as the bore needs to be concentric with the pivot and the angled faces. Ideally the bore, pivot and angled face would have been turned in one setting of the part in on the lathe. Howerver the boss on the upper surface made it difficult to mount in the chuck of a small lathe.

In addition, there is little space between the boss and the bore to enable you to mount the piece between centres. A chunky purpose-made mandrel relieved on one side may be the solution to thet issue

One of the other challenges if you are starting from scratch is the undercut grooves. If you can salvage the part by fabricating a boss to fit, you could save some extra work, but it may be worth checking the concentricity before you start.

I hope this helps. I would be pleased to know how you get on.

Thread: water
12/08/2022 19:13:27

One already has..

https://en.wikipedia.org/wiki/Thames_Gateway_Water_Treatment_Works

Thread: CO2 - Dumb question
11/08/2022 20:48:32

Conserving the planet is not just about principles and science but also about economics. A design solution for insulation in a building is affected by the prevailing interest rates more than just the energy to be saved vs the energy costs of the manufacture and installation of the materials. High interest rates wil discourage investment in energy saving measures as the future returns must be subject to greater discount. Hence the accountants can have significant influence in investment decisions unless regulation forces the pace.

Thread: Bulb for a Vertex swan neck work light
26/07/2022 15:56:25

Bulbs grow and lamps glow

Halogens lamps may be preferable to LEDs because of the lack of the stroboscopic effect.

Thread: WD40 alternative - any good?
22/07/2022 17:19:21

I agree that Shell Ensis is very good for corrosion protection but it seems to be difficult to buy in small quantities. Waxoil is more readily available form retailers such as Halfords.

21/07/2022 11:35:43

I was interested to validate some of the claims regarding the corrosion protection provided by various products. I cleaned and coated four samples of mild steel sheet with Muckoff, 3-in-1, WD40 and Waxoil respectively. I supended the samples together with an untreated control sample on PVC insulated wire under the eaves of my workshop where they were exposed to outside conditions but not direct rainfall or sunlight.  img_20220718_204736864.jpg The samples after exposure - control, Muckoff, 3-in1, WD40 and Waxoil

The results suggest that most effective treatment was the Waxoil, so I use that product for long term protection of materials and surfaces which I would not normally touch.  It requires white spirit  to remove it.  For protection of tools, there is not a lot to choose between WD40 and 3-in-1.  Even the Waxoil treated sample showed some signs of corrosion, so it would benefit from an extra coat.

I have no commercial interest in any of these products.

Edited By Richard Taylor 17 on 21/07/2022 11:50:49

Thread: Fiber optic cable
13/06/2022 19:08:14

Beware of the dangers of fragments of optical fibre if using the material for anything other than commmunications. Fragments can stick to you skin and then be carried to your eyes or mouth. If your are working with optical fibre it is recommended that the work surface is dark in colout as the shards are more apparent.

Thread: Metallurgy of Copper
02/06/2022 22:52:30

I cannot agree that the olive needs to cut into the pipe. Once the copper pipe starts you yield under the force from the olive, you will never achieve a leak-free joint, however much you tighten it.

I certainly agree that the olive needs some lubrication. I alway use a smear of Boss White or similar. I know plumbers who swear by silicone sealant but that is not my preference.

Magazine Locator

Want the latest issue of Model Engineer or Model Engineers' Workshop? Use our magazine locator links to find your nearest stockist!

Find Model Engineer & Model Engineers' Workshop

Sign up to our Newsletter

Sign up to our newsletter and get a free digital issue.

You can unsubscribe at anytime. View our privacy policy at www.mortons.co.uk/privacy

Latest Forum Posts
Support Our Partners
cowells
Sarik
MERIDIENNE EXHIBITIONS LTD
Subscription Offer

Latest "For Sale" Ads
Latest "Wanted" Ads
Get In Touch!

Do you want to contact the Model Engineer and Model Engineers' Workshop team?

You can contact us by phone, mail or email about the magazines including becoming a contributor, submitting reader's letters or making queries about articles. You can also get in touch about this website, advertising or other general issues.

Click THIS LINK for full contact details.

For subscription issues please see THIS LINK.

Digital Back Issues

Social Media online

'Like' us on Facebook
Follow us on Facebook

Follow us on Twitter
 Twitter Logo

Pin us on Pinterest

 

Donate

donate